  1. #21
    Join Date
    Sep 2013
    Location
    Wi
    Posts
    1,026
    Post Likes
    Thread Starter
    I'm back Cooler has no high side access but I was adding refrg. To see what happens it was becoming obvious the tube was plugged when it let go now there's way to much refrig.so took some out and it worked fine for a while then did it again so I evacuated well and added a filter drier so far so good.

  2. #22
    Join Date
    Jun 2013
    Location
    Austin, TX
    Posts
    639
    Post Likes
    Quote Originally Posted by ICanHas View Post
    What this guy said. When I read MP39, I guessed R12 system with MO. If it was a POE system with 134a I would've suspected it that as more likely.

    Very good SUPCO article on capillary clogging here:
    http://www.supco.com/images/pdfs/Man...g%20Manual.pdf
    Good article but use nitrogen, not air for testing cap tubes. Even if the air is super dry, the oxygen in it can oxidize the oil.

  3. #23
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,814
    Post Likes
    Quote Originally Posted by itsiceman View Post
    On a system with restricted cap tube after your compressor starts you will typically see a spike in head as the evap is cleared then the head will drop as the refrigerant stacks up in the condenser and there is less gas coming through the suction side. When you are low on charge you generaly do not see the same head spike. I agree with the others with vacuum on the low side will not always indicate a low charge. These would be the guys that over charge a restricted cap tube to get the suction up when total charge is not weighed in vs topping off.
    x2..

    also if you equalized both sides with your gauges then if it was a restriction you would get the "static" u were looking for correct?

    I had a reach in cooler and I was down to "low or restriction"...so i shut it off, pressures very very slowly equalized, i let them equalize thru my gauges and the static actually appeared normal given set conditions. I started her up. Head jumped way up...275 but then suction started dropping..30, 20, 10, 2. and then head came down with it so I'd say this is another good indicator

  4. #24
    Join Date
    Oct 2008
    Location
    Ohio
    Posts
    302
    Post Likes
    This is the type of system you can actually use your subcooling reading to tell you something.

  5. #25
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,814
    Post Likes
    Quote Originally Posted by Jared Fetter View Post
    This is the type of system you can actually use your subcooling reading to tell you something.
    subcooling..?? Whats that?

  6. #26
    Join Date
    Jan 2010
    Posts
    45,372
    Post Likes
    Quote Originally Posted by UmmScott View Post
    subcooling..?? Whats that?
    what they cool subs with ?

  7. #27
    Join Date
    Sep 2013
    Location
    Florida
    Posts
    423
    Post Likes
    I like my subs hot! No subcooling for me!

  8. #28
    Join Date
    Aug 2009
    Location
    Maine
    Posts
    8,146
    Post Likes
    Think he meant submarines ?
    Quote Originally Posted by Moonray View Post
    I like my subs hot! No subcooling for me!

  9. #29
    Join Date
    Sep 2013
    Location
    Florida
    Posts
    423
    Post Likes
    Quote Originally Posted by lytning View Post
    Think he meant submarines ?
    Oops! My bad!

  10. #30
    Join Date
    Jan 2010
    Posts
    45,372
    Post Likes
    Hey ! 110 - 220 whatever works

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •