    ... but my friend has done this for 30 yrs

    Got a call, no cool, brand new install. My office said you should call the company that installed it so they could fix it under warranty. Turns out that some "friend" installed this ac 3 months ago and they don't want him back.

    This guy didn't have a clue, he had been troubleshooting this for 4 weeks and couldn't figure it out. Before you look at the pictures, you need to know what he did.

    I put my gauges on the condenser, 0 superheat, 40 subcool.

    "you have a problem with the metering device or airflow issues".

    This idiot was using the +30 -30 method to check refrigerant.

    The home owner said it cant be that easy, " he has been doing this for 30 yrs, and he has spent 3-4 weeks on this" "it has to be something else".


    OK, take a look






    .
    .
    .
    .

    check out the TXV



    .





    Ok, it gets better, the coil is sitting on one piece of S-lock.
    LOOK AT THE BYPASS AIR!!!!!!!!!!!!!!!!!!

    .






    Take a look at the 24v wire to the txv area, the guy put a freeze sensor on the suction line outside the plenum. So when it froze, it cut the 24v to the cond. for a few min. 3 ton of cooling through an old permatron 16x20 filter.









    He fixed the humidifier leak at no extra charge






    Installed a Tuy w/ a 14i heat pump, Iaq stat,, it was a tight fit, but our installers did a nice job.



  2. #2
    Join Date
    Dec 2005
    Location
    Indiana
    Posts
    309
    Post Likes
    Thread Starter
    One more thing to mention, after a proper Man J was done, we installed a 2 ton in place of the 3 ton....

  3. #3
    Join Date
    Dec 2002
    Location
    Rochester, MN
    Posts
    5,307
    Post Likes
    Nice fix....

    Why didn't you keep the new A/C and coil? or the customer wanted to upgrade into the Heat Pump? Customer sure spent a lot of money in the last few months, or did you guys "buy" the A/C to save some money?

  4. #4
    Join Date
    Dec 2005
    Location
    Indiana
    Posts
    309
    Post Likes
    Thread Starter
    For one, the system had air in it, It had been opened up numerous times. I don't know if this hillbilly used nitrogen, He smashed the crap out of the evap, the original ac died, burnout, and he reused the orig lineset .... And it was one ton oversized. Where I live, heat pump is the way to go with a fossil fuel backup.

  5. #5
    Join Date
    Feb 2001
    Location
    Arizona
    Posts
    5,492
    Post Likes


    That right there looks like D.S.C. in Phoenix did that install!

    They would either HANG the sensing bulb or zip tie it and throw the metal strap away!!!!! They obviously had NO CLUE!

    So what is this 30/-30 thing you speak of? You mean the old "30 degree over ambient" head pressure charging method LOL!!!!

    ZERO SUPERHEAT thru that TXV, how is that possibe, even with the stacked up 40 deg subcool? Or was the system so mismatched that it couldn't boil off enough refer?

  6. #6
    Join Date
    Feb 2006
    Location
    Anderson/Noblesville, IN
    Posts
    397
    Post Likes
    Thats one heck of a friend. So Freefall where at in Indiana are your from?

  7. #7
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Post Likes
    its annoying when i see drains ran level along a floor .. i dont care that it drains due to the weight of the water .. there will be standing water in there in an off cycle & we all know what happens then

  8. #8
    Join Date
    Oct 2006
    Location
    In a freezer or in an attic somewhere
    Posts
    550
    Post Likes

    Cool

    That trane install looks as pretty as the wallpaper beside it. lol

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •