    Water flow and Delta T

    Had a pump guy in on a job yesterday. He was saying that if you have too much water flow through a chiller you delta T will be closer. Is that true?

  2. #2
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    If by closer you mean decrease, the answer is yes. There is a very basic principle here that you may want to take the time to learn.

    The tonnage of a chiller can be determined by the following formula: Tons = GPM X DELTA T / 24. For example, if you have a 100 T. chiller that is designed to produce a delta T of 10*F then the flow would have to be 240 GPM. 100 = 240 x 10 / 24. Using the formula, one can see if the GPM is increased then the delta T has to decrease to get the correct answer. The 24 is a constant and the tonnage isn't going to increase if the flow increases.

  3. #3
    Join Date
    Jan 2013
    Location
    Dyersburg, TN
    Posts
    283
    Post Likes
    Thread Starter
    The machine that i have is a 30 ton designed to do 10* t at 100% at 65.3 GPM. I am get a 9.7 delta T at 50 %. So does that mean i am flowing to much water? I have a pressure drop of 14.56 ft head the design is 12.6 ft head

  4. #4
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,617
    Post Likes
    Quote Originally Posted by jeremyr325 View Post
    The machine that i have is a 30 ton designed to do 10* t at 100% at 65.3 GPM. I am get a 9.7 delta T at 50 %. So does that mean i am flowing to much water? I have a pressure drop of 14.56 ft head the design is 12.6 ft head
    at 65.3 gpm and 10F, you have a DESIGN LOAD of 27.21 tons. if you push more evaporator water through the barrel, then your chiller has to work harder to remove the same heat load at the same conditions because the water flows through the barrel faster and has less time to give up its heat. if you are getting a 9.7F drop at 15 tons, then you aren't flowing the same water as designed or something has changed from design. at 14.56 feet of head versus 12.6 feet of head, you are flowing about 8% more water. keep in mind that we are assuming that your design is water and that you have water in it now. other fluids (glycol, etc) change things dramatically.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

  5. #5
    Join Date
    Oct 2010
    Posts
    923
    Post Likes
    Check out bell and gossets system sizer app for smart phones,it can take design chiller barrell drops and calculate flow based on actual readings and also give tonnage

  6. #6
    Join Date
    Apr 2011
    Location
    Southern Indiana
    Posts
    215
    Post Likes
    Quote Originally Posted by KnewYork View Post
    If by closer you mean decrease, the answer is yes. There is a very basic principle here that you may want to take the time to learn.

    The tonnage of a chiller can be determined by the following formula: Tons = GPM X DELTA T / 24. For example, if you have a 100 T. chiller that is designed to produce a delta T of 10*F then the flow would have to be 240 GPM. 100 = 240 x 10 / 24. Using the formula, one can see if the GPM is increased then the delta T has to decrease to get the correct answer. The 24 is a constant and the tonnage isn't going to increase if the flow increases.
    Where did you get the 240?

  7. #7
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    903
    Post Likes
    Quote Originally Posted by SanchezHVAC View Post
    Where did you get the 240?
    Look at the math that was used. Multiples of 10 were used for the example, so he came up with 240 gpm.
    If you know the gpm then you can figure tonnage. To find the gpm you will need the original spec. for the chiller.


    Sent from my iPad using Tapatalk

  8. #8
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    2,964
    Post Likes
    You can calculate the chiller Cv. That is done by dividing the design GPM by the square root of the design delta p. To obtain flow multiply the Cv times the square root of the measured delta p.

    Another way is to get flow is to multiply the design GPM times the square root of the measured delta p divided by the design
    delta p.
    No man can be both ignorant and free.
    Thomas Jefferson

  9. #9
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    903
    Post Likes
    Click image for larger version. 

Name:	914E0834-079A-4B85-A2EB-A052EE2C33F7.jpg 
Views:	43 
Size:	84.9 KB 
ID:	808214I hope that picture came thru clear.


    Sent from my iPhone using Tapatalk

  10. #10
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    903
    Post Likes
    Click image for larger version. 

Name:	896AFB44-4488-4651-8FE4-3BC1AC5902E1.jpg 
Views:	42 
Size:	118.7 KB 
ID:	808216Dang it fat fingers!


    Sent from my iPhone using Tapatalk

  11. #11
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    903
    Post Likes
    God lord this is the picture . Ignore the others.Click image for larger version. 

Name:	IMG_1983.jpg 
Views:	44 
Size:	253.0 KB 
ID:	808217


    Sent from my iPhone using Tapatalk

  12. #12
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    903
    Post Likes
    Don’t forget only use one gage to take your readings. That takes gage inaccuracy out so you don’t chase your tail.


    Sent from my iPhone using Tapatalk

  13. #13
    Join Date
    Apr 2011
    Location
    Southern Indiana
    Posts
    215
    Post Likes
    Quote Originally Posted by Chev5372 View Post
    Don’t forget only use one gage to take your readings. That takes gage inaccuracy out so you don’t chase your tail.


    Sent from my iPhone using Tapatalk
    Thanks a lot! Especially the pics. How do you upload pics on here?