    Neutral or not to Neutral?

    Here's a good one for all you electrical buffs who would like a brain teaser...
    Would like to know everyone s thoughts on switching the neutral when installing or using a generator through a manual transfer switch Do you need to switch the neutral in order to isolate it from sending transient voltage back to the utility company? I say no only because the ground comes into contact with the neutral so all stray voltage will take the least path and leave through the ground...What are your thought guys?

  2. #2
    Join Date
    Feb 2013
    Location
    Phoenix, AZ
    Posts
    184
    Post Likes
    If the neutral conductor from the genset is grounded at the genset (separately-derived system), the neutral must be switched such that it is grounded either through the genset OR the bonding jumper, never both. If the neutral from the genset is floating (non separately-derived), then the neutral need not be switched.

    Note that having a genset with grounded neutral connected to a service with the normal bonded neutral can create a very dangerous situation during certain fault conditions and should never be done.

    Here's a good treatment of the subject:

    http://www.cat.com/cda/files/99865/7/LEXX0604-01.pdf

  3. #3
    Join Date
    Apr 2012
    Location
    ny
    Posts
    8
    Post Likes
    Thread Starter
    OK...now would it be safe to say if I have continuity between the neutral and ground than I don't have to switch the neutral?

  4. #4
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by lx2077bob View Post
    OK...now would it be safe to say if I have continuity between the neutral and ground than I don't have to switch the neutral?

    Okay, which neutral and which ground are you asking about now?

    Did you read the articles that I mentioned when you posed this question up in the other section?
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  5. #5
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by lx2077bob View Post
    Here's a good one for all you electrical buffs who would like a brain teaser...
    Would like to know everyone s thoughts on switching the neutral when installing or using a generator through a manual transfer switch Do you need to switch the neutral in order to isolate it from sending transient voltage back to the utility company? I say no only because the ground comes into contact with the neutral so all stray voltage will take the least path and leave through the ground...What are your thought guys?

    My suggestion is to install it according to code.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •