    I was working on a walk in freezer today that had two bad condensor fan motors which I replaced...
    I started up the unit and was waiting for the evap fans to kick on ( waited about 30 minutes )
    Felt the evap. getting cold but the fans didn't kick on.
    I jumped out the Defrost Termination control and the fans started... so i went and picked up a new defrost termination control>
    When I got back the freezer was running @ 30 degrees> i put in the new control and started it up> same problem. fans did not start...

    really weird senerio.. I need some opinions. would really be helpful. thx!

  2. #2
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,573
    Post Likes
    It's doing exactly what it's supposed to do. 30 minutes seems excessive. Sounds like you may have additional problems. I woud be checking the charge, and the metering device as well as compressor efficiency. Why were the motors bad? and did you clean the coil while you had them out?
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  3. #3
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,136
    Post Likes
    Was the coil frozen up from running without the fans? Did the compressor slug itself to death and bust its valves? What are your pressures and your evaporator superheat?

  4. #4
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    9,679
    Post Likes
    Probably the defrost termination and fan delay switch. As 2sac stated, it is either doing what it is suppose to be doing and not closing to energize fans until evap coil temp drops low enough, or it is faulty and sticking and not energizing the fans. Time to investigate just a bit more.

  5. #5
    Join Date
    Sep 2010
    Location
    Western, MO
    Posts
    988
    Post Likes
    If the evap fans aren't running the DTT is the first thing I check. I had a tech order fan motors without checking to see how it got it's power and neutral.

    jim
    Common sense isn't very common anymore.

  6. #6
    Join Date
    Oct 2011
    Posts
    3
    Post Likes
    Thread Starter
    They had a power outage yesterday. Ive never seen two die at once tho. Charge is good.. little high head washed n blew out coil. Running at 285 n 32. Ill have to check out mire tmrw thx for the help

  7. #7
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,573
    Post Likes
    Betcha got a ZP charge on the powerhead. Should be good tomorrow.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  8. #8
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    Hot box and high ambient?
    May take a bit to pull down enough to make fan Circut. Should pull down at a steady clip though. If coil temp is not dropping steady your problem is elsewhere, as pointed out earlier. Charge, TXV, headmaster, comp valves, etc.

  9. #9
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    Had a freezer that gave me fits.

    Defrost heater was switched on the neutral leg. Intermittant grounded would bring the heater on with defrost stat open-sometimes. Usually after I left.

    Acted the same way. Charge right, but slow pulldown.

    Took forever to finally catch the defrost heater on while trying to cool.

  10. #10
    Join Date
    Jan 2008
    Location
    michigan
    Posts
    1,187
    Post Likes
    I had a problem once, similar in nature, on a three door display freezer. Changed the fan delay switch and unit took off. Next day get a call, not working again. Arrive on site, it is working fine. Check charge, SH etc., all good. Put unit in defrost, comes out of defrost and all works fine. Hmmmm. Did that multiple times. Even emptied out the contents, let box warm up and tried it again, all good. Next day, same problem. Only this time when I arrive, fans aren't running. Start checking power and discovered no power to fan delay switch. Turns out that the wire that ran from the terminal strip, throught the box, and to the FD switch had a "break" in it somewhere, and would send power most times but occassionally would "break". Replaced that wire and all was good. Drove me nuts.

  11. Likes trippintl0 liked this post.
  12. #11
    Join Date
    Jul 2019
    Posts
    1
    Post Likes
    Can a defrost termination mark ground and cause a short circuit?

  13. #12
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,573
    Post Likes
    Yes
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  14. #13
    Join Date
    Feb 2009
    Location
    Louisiana
    Posts
    10
    Post Likes

    That sign makes sense. I get sick of seeing those bums begging.

    If they can bum 4 or 5 hours they can work too.

  15. #14
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    But that's Al Bundy surely he can't be a bum.

  16. #15
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,136
    Post Likes
    Yeah, I know that guy. He works at a shoe store in the mall. His job is to help fat women stuff their feet into shoes all day.

    At least he used to. Now I think he sells closets and has married a hot Puerto Rican chick.

    If at First You Don't Succeed, Skydiving Is Not for You.

  17. #16
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by ammoniadog View Post
    Yeah, I know that guy. He works at a shoe store in the mall. His job is to help fat women stuff their feet into shoes all day.

    At least he used to. Now I think he sells closets and has married a hot Puerto Rican chick.

    And his daughter was the talk of the high school....
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  18. #17
    Join Date
    Jul 2019
    Location
    Central Massachusetts
    Posts
    27
    Post Likes
    I ran into a KolPak unit recently that 5 different companies worked on. The symptom was similar, except that the coil was freezing up solid- randomly! The others had replaced the thermostat, the terminator/delay, the defrost limit, timer, contactor...You'd have thought that ONE of them would-a noticed that most of the heating element was not actually touching the coil! You know- there's a 'groove' in the coil that the element sits in and it transfers the heat to the coil?, Yah that!! LOL Simple enough to take a ¼" nut driver and tap it back in....jeeeeeez!
    ► As to the fans, you DID say that you changed the --condenser fan motors--, which have almost nothing to do with the --evaporator fans--. If the Evap fans do not start within 10 minutes of the defrost terminating, start by checking the (usually 3 wire) defrost thermostat. If it's below 35°f, the fans should run. If it's cold enough, Bypass it to test. Fans start= bad stat. Fans no= something else, possibly a problem with the fan delay in the defrost timer. (Most units rely only on the stat for this function)

  19. #18
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Quote Originally Posted by MilfordsMrFixIt View Post
    Fans no= something else, possibly a problem with the fan delay in the defrost timer. (Most units rely only on the stat for this function)
    Where is this " fan delay in the defrost timer " you speak of ?

  20. #19
    Join Date
    Jul 2019
    Location
    Central Massachusetts
    Posts
    27
    Post Likes

    To clarify the Timer with fan delay question;

    Well, there are a number of timers that control the fan delay. Usually formatted in 'time initiate and time terminate' mode. There is a terminal "F" for this purpose, however most clocks just use it to isolate the fan output to prevent feedback issues.
    • This Grasselin control delays the "F" contact by a fixed 5 minutes. We found that out when the fans just would not come on. Of note, there are 5 relays on the board while most have just 2 or 3. Impatience on that one...LOL We rewired it to a standard DTFD as the fans were coming on just a little too soon causing fog in the freezer- alarming the users! One called the fire department reporting a 'Freon™ leak'! So we had to come up with a solution. (note the currently empty "F" terminal)
    • The ICM 550 on the other hand just turns the fans on as soon as the defrost terminates. Note there are 3 relays, the small one signals the termination cycle.
    • The electronic Paragon 9145 clock (love it) seems to be just a changeover as well. Great timer if you need to keep the times for defrost at exact times of day, or if you need to run short defrosts during the day, IE 15 minutes, and you can schedule a 90 minute at 4 am. The DTFD will still stop the defrost if it finished early.
    ◘There are a few models out there that delay the fans, few, but some.
    ▬ We have a customer that had a drive-in frozen warehouse that had 8 separate sets of condensing units and evaporators. that were all controlled by a single timer... and a boat load of relays and contactors! What a cluster---- that was. Initially I Converted them to individual timers. Imagine the inrush when 80 HP of condensing units all started at the same time!!! Their power demand went down enough for the accountant to notice!!
    --As of now, I installed an Arduino Uno that's programmed to defrost one at a time for a max of 30 minutes, then hard delay the fans for 6 minutes and 30 seconds with a standard DTFD stat backing it up. So, at the top of each hour, a different unit defrosts, giving a defrost every 8 hours to each unit in succession. This keeps energy usage in line and also the temperatur regulation, which is controlled separately. It's been running with the Uno for 10 years now trouble free, there's a spare at the site pre-programmed if it's needed.
    Attached Images Attached Images    

  21. #20
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,457
    Post Likes
    ICM using a Grasslin timer?

    What is this world coming to?
    I do a triple evac with nitro to remove non condensables.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •