    Dude here....

    I have a domestic hot water recirc pump 8GPM @ 17psi (40ft.w.c.)

    I was thinking of using a flow switch to monitor the flow for a DDC system.

    However, the flow switch imposes a pressure drop of approx. 3 psi.

    I am a little worried of putting in a piping element that will inhibit the desired flow...

    Any opinions?

  2. #2
    Join Date
    Aug 2000
    Location
    Under my tree
    Posts
    5,133
    Post Likes
    Use a pressure differential switch to prove flow.

  3. #3
    Join Date
    Feb 2003
    Location
    Wichita Ks
    Posts
    1,603
    Post Likes
    another option would be an electronic flow switch. the diff pressure switch would be all right if the city water pressure did not bounce up and down much causing false alarms. another way is a current sensor on the motor.