    Trane troubles

    Any service facts for:
    YCH181E3LBBB
    114510138D

    I have 24 volts between c&g, but no indoor blower coming on. LED on steady indicating no problems. Before I condemn the board i want to verify that nothing else but the board could be causing the blower to not operate.
    Last edited by ncboston; 02-17-2012 at 05:25 PM. Reason: Sorry. Meant to start new thread.

  2. #2
    Join Date
    Sep 2011
    Location
    Augusta, ME
    Posts
    135
    Post Likes
    U got voltage at blower motor

  3. #3
    Join Date
    Mar 2008
    Location
    NC
    Posts
    1,511
    Post Likes
    Thread Starter
    No 24 volts at contactor. Wondering if board is bad and k6 relay not closing or if the board might not be passing lv for a different reason. But to answer your question, there is high voltage present at the contactor.
    I'm pretty sure it's a bad board, but I want to make sure nothing else could be telling the board to not pass 24 volts to the contactor.

  4. #4
    Join Date
    Mar 2008
    Location
    NC
    Posts
    1,511
    Post Likes
    Thread Starter
    To the mods,
    thanks for moving.

  5. #5
    Join Date
    Mar 2009
    Location
    central illinois
    Posts
    540
    Post Likes
    make sure phase is right,they have monitors on them.
    work to live not live to work.

  6. #6
    Join Date
    Mar 2008
    Location
    NC
    Posts
    1,511
    Post Likes
    Thread Starter
    The kicker is, this thing was running. I opened the disconnect, replaced filters, closed disconnect, and no blower. No wires moved, nothing.

  7. #7
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,302
    Post Likes
    Quote Originally Posted by ncboston View Post
    The kicker is, this thing was running. I opened the disconnect, replaced filters, closed disconnect, and no blower. No wires moved, nothing.
    Sabotage, you broke it !!

  8. #8
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,302
    Post Likes
    Tied into a Trane EMS by chance?

  9. #9
    Join Date
    Mar 2008
    Location
    NC
    Posts
    1,511
    Post Likes
    Thread Starter
    Quote Originally Posted by Chris_Worthington View Post
    Sabotage, you broke it !!
    I'm in trouble now.

  10. #10
    Join Date
    Feb 2011
    Location
    Sacramento, CA
    Posts
    46
    Post Likes
    I ran into this type of problem just 3 weeks ago on a Trane unit. Does the unit have an economizer?

  11. #11
    Join Date
    Sep 2004
    Posts
    13,934
    Post Likes
    smoke detector???????????

  12. #12
    Join Date
    Mar 2008
    Location
    NC
    Posts
    1,511
    Post Likes
    Thread Starter
    Quote Originally Posted by Jerry Jessup View Post
    I ran into this type of problem just 3 weeks ago on a Trane unit. Does the unit have an economizer?
    Yes.

  13. #13
    Join Date
    Mar 2008
    Location
    NC
    Posts
    1,511
    Post Likes
    Thread Starter
    Quote Originally Posted by supertek65 View Post
    smoke detector???????????
    No fire alarm system or smoke detector tied in.

    24 volts enters rtrm board, but does not bring on IDB.
    I'm thinking either board is bad, or something that the board looks at is bad.

  14. #14
    Join Date
    Sep 2004
    Posts
    13,934
    Post Likes
    is this a model that you can put your meter across a couple terminals and determine which mode the unit is in and if there are any alarms?
    the only things that would usually keep a blower off is smoke, freeze or un occupied setting?

  15. #15
    Join Date
    Mar 2008
    Location
    NC
    Posts
    1,511
    Post Likes
    Thread Starter
    no. I have 24 volts across g & c coming into the rtrm board.

  16. #16
    Join Date
    Sep 2004
    Posts
    13,934
    Post Likes
    looks like you have it figured out already?
    I will read some IOM stuff and look through the reliatel book!

  17. #17
    Join Date
    Feb 2011
    Location
    Sacramento, CA
    Posts
    46
    Post Likes
    The Trane unit I was working on had the same symptom. I also thought it was the main control board at first, but after some reading I found that I had a faulty economizer board. I purchased a new economizer board and unit quickly come online.

  18. #18
    Join Date
    Feb 2011
    Location
    Sacramento, CA
    Posts
    46
    Post Likes
    One way to test is to turn off the unit, unplug the economizer board plug from the main control board and then turn the units disconnect back on. If the blower comes on then replace the economizer board. The board costed us $$$$
    Last edited by Chris_Worthington; 02-18-2012 at 07:14 AM. Reason: Pricing Removed

  19. #19
    Join Date
    Jan 2012
    Location
    Central New Jersey USA
    Posts
    90
    Post Likes
    The boards usualy have triacs (electronic switches) for the output relays. Can you remove the output wires at the RTM going to the fan output and see if you have 24 volts. If you have 24 volts at the board and lose the 24 volt when you put the wires back on, the triac is bad and you have to replace the board. Can this unit be viewed with Rover software and do you have Rover? As someone said earlier, the economizer or the connections may have a problem. If you still have the bypass plug for the economizer, you can try plugging that in and see if the fan starts.

    Good luck

  20. #20
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,270
    Post Likes
    If the unit runs in TEST (including blower) the main board is good.

    In that case, it will be the econ board.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •