  1. Charged at 6000 microns? The fact that you can't...

    Charged at 6000 microns? The fact that you can't pull down doesn't raise any questions or concerns. That leak needs to get fixed.
  2. Replies
    22
    Views
    4,857

    I tried pumping it down and it wouldn't pump...

    I tried pumping it down and it wouldn't pump down. I also did that ac analyzer it says compressor was bad not pumping. Thanks guys, I'll replace the compressor as soon as it arrives. Thanks again.
  3. Replies
    22
    Views
    4,857

    No I haven't, that's a great idea Thanks!!!

    No I haven't, that's a great idea Thanks!!!
  4. Replies
    22
    Views
    4,857

    75/RA, 64SA. The load on the system wasn't big...

    75/RA, 64SA. The load on the system wasn't big enough to cause my suction to be that high. It's TXV System, Txv was maintaining good sh. The compressor does make rattle type of noise on start up.
  5. Replies
    22
    Views
    4,857

    It's a scroll compressor, line temps on the...

    It's a scroll compressor, line temps on the reversing are within 2-4 degrees. DT 163.
  6. Replies
    22
    Views
    4,857

    I believe it's the compressor. My start and run...

    I believe it's the compressor. My start and run windings are drawing the same amount of amps I've never seen that on a single phase compressor. There is usually a small amount of current going...
  7. Replies
    22
    Views
    4,857

    Condenser was filthy and my head pressure was...

    Condenser was filthy and my head pressure was super low. I cleaned the condenser and nothing changed.
  8. Replies
    22
    Views
    4,857

    R410A

    R410A
  9. Replies
    22
    Views
    4,857

    Inefficient Compressor

    Working on a split system heat pump
    OA 90 HP 325, SP 175, SH 10, SC 7
    Compressor amps common 6.2A, start 5.1, run 5.1. Nameplate rating 14A. Is compressor inefficient? Anything helps.
  10. Thread: New house

    by Temp_Drop
    Replies
    18
    Views
    5,907

    That look really Sharp. Nice job!

    That look really Sharp. Nice job!
  11. Replies
    4
    Views
    2,408

    We just stated at this location all these motors...

    We just stated at this location all these motors have been overgreased. We installed sealed bearings.
  12. Replies
    4
    Views
    2,408

    Not sure I just know it's a cone style bearing...

    Not sure I just know it's a cone style bearing heater.
  13. Replies
    4
    Views
    2,408

    Bearing replacement

    Got to help out with bearing replacement on 40HP Motor.
    715601715611715621715631715641715651
  14. Replies
    20
    Views
    64,051

    I think the rating of compressor tonnage and hp...

    I think the rating of compressor tonnage and hp changes with application is due to 1hp=746w electrical energy not cooling energy. The compressor hp would also change with different operating...
  15. Replies
    17
    Views
    3,099

    Got it figured that's what you meant. Thanks.

    Got it figured that's what you meant. Thanks.
  16. Replies
    17
    Views
    3,099

    What do you mean by manually control the...

    What do you mean by manually control the loading/unloading of compressor?
  17. Replies
    17
    Views
    3,099

    It uses dry coolers. I know the coils are filthy...

    It uses dry coolers. I know the coils are filthy or undersized, the guy onsite says they need to turn the sprinklers on when it gets around 85 +. They try to keep the site at 68 but in my opinion...
  18. Replies
    17
    Views
    3,099

    Yeah I dial the sheave to get me fla than switch...

    Yeah I dial the sheave to get me fla than switch to fixed sheave. The control ignores the low suction for 30-60 seconds(pump down). It doesn't happen right away and I haven't been able to catch it in...
  19. Replies
    17
    Views
    3,099

    :oops:

    :oops:
  20. Replies
    17
    Views
    3,099

    Humidity setting is 45% the space temp setting is...

    Humidity setting is 45% the space temp setting is 68. I had to lower the setpoint and watch it run for a while. There isn't a lot of load in bldg yet. They plan on adding more equipment but haven't...
  21. Replies
    17
    Views
    3,099

    Thanks I'll do that.

    Thanks I'll do that.
  22. Replies
    17
    Views
    3,099

    Liebert VH363??

    Liebert MN:VH363GUAAEI is tripping on low suction alarm, refrigerant charge is good pulled it out weighed it back system was a 1lb low. Pressure tested found no leaks. Evacuated and weighed charge...
  23. You should get the copeland x-ref app. It will...

    You should get the copeland x-ref app. It will give you specs on said compressor.
  24. Thread: Dry coolers

    by Temp_Drop
    Replies
    4
    Views
    1,296

    Ok thanks. I didn't know they had glycol with...

    Ok thanks. I didn't know they had glycol with different ratings, this unit is not piped to a cooling tower or anything at all. Its just piped from the Liebert to dry cooler.
  25. Replies
    3
    Views
    1,724

    Did you on inside of unit sometimes there's a...

    Did you on inside of unit sometimes there's a name plate under the control section of unit.
  26. Replies
    11
    Views
    2,652

    Is the coil clean, you have to clean it from the...

    Is the coil clean, you have to clean it from the back by removing the fan shroud. Does condenser fan motor have the right rotation, possible restriction of metering device? Once you start operating...
  27. Thread: Dry coolers

    by Temp_Drop
    Replies
    4
    Views
    1,296

    Yeah this one is being used to cool a Liebert....

    Yeah this one is being used to cool a Liebert. Yesterday it tripped on hp switch both circuits. Dry cooler was plugged with cottonwood, cleaned the strainers they were dirty but not as bad coil on...
  28. Thread: Dry coolers

    by Temp_Drop
    Replies
    4
    Views
    1,296

    Dry coolers

    hey just wanted to ask about dry coolers. Do they work well in ambient temps at or above 95 degrees?
  29. Thread: Dry coolers

    by Temp_Drop
    Replies
    3
    Views
    2,069

    Dry coolers

    hey just wanted ask if dry coolers work well in a hot weather 95 degree and above ambient temps.
  30. Replies
    2
    Views
    2,528

    rheem gas pack

    Does anyone have any technical info on RHEEM RRGF-131075CKR.
  31. Replies
    2
    Views
    1,540

    Thanks that clears that up.

    Thanks that clears that up.
  32. Replies
    2
    Views
    1,540

    dirty voltage?

    Can someone explain dirty voltage and how it affects the system? I am apprentice I would like to know what it looks like in my multimeter any input helps.
  33. Replies
    26
    Views
    7,380

    I check caps as part as every pm I do. Like you...

    I check caps as part as every pm I do. Like you said it also makes the next call billable if the capacitor fails, more than that it's good service to let your customer know what you found performing...
  34. Replies
    26
    Views
    7,380

    I use the uf setting on my meter. Today I...

    I use the uf setting on my meter. Today I performed a PM on 2 Gas Pack units a very old Bryant and a York, as part of maintenance I check run caps the one for IFM was rated 15uf +-.06% it was 11uf...
  35. Replies
    7
    Views
    1,178

    Got it I'll wait till I have posted 15 post with...

    Got it I'll wait till I have posted 15 post with technical info. I will also get my paperwork in pdf format.
    Thanks.
  36. Replies
    7
    Views
    1,178

    That's exactly what am trying to do, how do you...

    That's exactly what am trying to do, how do you apply for pro membership? While I was going to school I would search for answers to questions and this website would always come up. I know the...
  37. Replies
    7
    Views
    1,178

    Thanks.

    Thanks.
  38. Replies
    7
    Views
    1,178

    Pacific Northwest

    Good Afternoon everyone glad to be a part of such informative site. Today I got the opportunity to replace a compressor on ductless mini-split as well as the indoor fan motor. The indoor fan motor...
  39. Sticky: I just got off work, today I assisted one of our...

    I just got off work, today I assisted one of our journeyman replace the blower wheel on Liebert unit. It was rough for a minute there was barely enough room to get blower wheel through the ceiling...
  40. Sticky: I have been hired as a apprentice with a hvac...

    I have been hired as a apprentice with a hvac company in pacific northwest.
  41. Sticky: I just graduated from a 2yr program in HVAC/R one...

    I just graduated from a 2yr program in HVAC/R one of my instructors told me this is a forum with lots of technical information.
Results 1 to 41 of 62
Page 1 of 2 1 2