  1. Replies
    250
    Views
    50,635

    I would also appreciate the signed modules as...

    I would also appreciate the signed modules as well. Thank you in advanced


    Sent from my iPhone using Tapatalk
  2. Replies
    3
    Views
    1,410

    You need to perform a backup and after loading...

    You need to perform a backup and after loading firmware, restore the backup.


    Sent from my iPhone using Tapatalk
  3. Replies
    9
    Views
    3,544

    This Siemens system is 100% proprietary. The...

    This Siemens system is 100% proprietary. The field panels will need to be replaced as there is not a driver that will talk to these P2 devices effectively. Most of the P1 devices can be integrated...
  4. Replies
    5
    Views
    1,718

    Mp580 and mp581 are fully programmable. ...

    Mp580 and mp581 are fully programmable.


    Sent from my iPhone using Tapatalk
  5. Replies
    5
    Views
    1,718

    You’ll have to reach out to your local Trane...

    You’ll have to reach out to your local Trane office. Most likely that will not sell to you, but good luck.


    Sent from my iPhone using Tapatalk
  6. You won’t have any issues writing to these point....

    You won’t have any issues writing to these point.


    Sent from my iPhone using Tapatalk
  7. Replies
    7
    Views
    3,087

    Preheat Face Bypass in large AHU

    I’m doing a controls upgrade on a large AHU. Most of the control has previously been converted from pneumatic to DDC, except for the 1/3 2/3 steam preheat valves and the actuator for the preheat face...
  8. Replies
    11
    Views
    3,324

    There is a p1 driver for Niagara. If all you have...

    There is a p1 driver for Niagara. If all you have is common TEC application such as 2020 it is pretty seemless. If there are other FLN controllers such as DPUs, MPUs and UC controllers you’ll have...
  9. Replies
    7
    Views
    2,847

    Correct, I’m referring to a separate P2 driver...

    Correct, I’m referring to a separate P2 driver that plugs into the rj11 hmi port of the Siemens device. I will verify the vendor


    Sent from my iPhone using Tapatalk
  10. Replies
    7
    Views
    2,847

    Siemens pxc00-pe96.a to Bacnet IP

    The Apogee 600 TEC driver can not be used to pull in the PXC.

    As mentioned earlier the two ways to accomplish this are the P2 driver or using the Insight server to export via BACnet.

    The...
  11. Replies
    0
    Views
    1,767

    Controllers for sale

    JCI DX9100(s) n2 with expansion modules
    JCI FX16(s) n2 with expansion modules
    Siemens PXC(s) p2
    Siemens MEC p2
    Make offer.


    Sent from my iPhone using Tapatalk
  12. Not sure this answers your question. But this...

    Not sure this answers your question. But this would show you at which priority a point is written to by another device. In your facets add “priorityArray” as a boolean equal true.


    Sent from my...
  13. Replies
    3
    Views
    2,299

    Verify that you do not have the BACnet discovery...

    Verify that you do not have the BACnet discovery enabled in Siemens system profile. If this is enabled it will try to discover all the devices, and will put a lot of “who is” traffic on the network. ...
  14. Replies
    1
    Views
    1,178

    Trane Tracer TU is needed to configure the uc600....

    Trane Tracer TU is needed to configure the uc600.


    Sent from my iPhone using Tapatalk
  15. Replies
    3
    Views
    1,225

    I think you that you are stuck without Tracer TU....

    I think you that you are stuck without Tracer TU.


    Sent from my iPhone using Tapatalk
  16. How bout just opening a web browser. If it's...

    How bout just opening a web browser. If it's remote set it up in your router with an external ip.


    Sent from my iPhone using Tapatalk
  17. Replies
    3
    Views
    1,008

    If you are a service customer than you can most...

    If you are a service customer than you can most likely purchase Tracer TU from you local rep, it's at least worth a call if your not. There is also yearly licensing fee.


    Sent from my iPhone...
  18. Replies
    12
    Views
    1,471

    The USB connection on the BCI is used to connect...

    The USB connection on the BCI is used to connect that tool.


    Sent from my iPhone using Tapatalk
  19. Replies
    12
    Views
    8,763

    Pre-apogee is a term that refers to the firmware....

    Pre-apogee is a term that refers to the firmware. It is pre-apogee


    Sent from my iPhone using Tapatalk
  20. Replies
    12
    Views
    8,763

    First device is a PXC, second is a pre-apogee MEC...

    First device is a PXC, second is a pre-apogee MEC and third is an MBC with a power open Processer (apogee).
    All devices are communicating P2 proprietary RS485 communications. MBC and MEC are...
  21. Replies
    12
    Views
    1,471

    This is set in Tracer TU. Should be automatic for...

    This is set in Tracer TU. Should be automatic for the start up tech, but unfortunately a BAS technician is rarely a part of this process if he's not involved in the project.


    Sent from my iPhone...
  22. Replies
    6
    Views
    1,211

    We'll need a lot more info, pneumatic, ddc?? ...

    We'll need a lot more info, pneumatic, ddc?? Control system?


    Sent from my iPhone using Tapatalk
  23. Replies
    3
    Views
    2,524

    Do you have the ai-fi connected through an SC? ...

    Do you have the ai-fi connected through an SC?


    Sent from my iPhone using Tapatalk
  24. Replies
    5
    Views
    2,296

    UC210 can be application specific as well as...

    UC210 can be application specific as well as custom configurable. Do you have a specific application your looking for?


    Sent from my iPhone using Tapatalk
  25. Replies
    7
    Views
    3,870

    The price Siemens will give you would be for them...

    The price Siemens will give you would be for them to install. I've installed this myself but Siemens said that I wouldn't be able to do it. That's before they'll found out I'd worked for Siemens for...
  26. Replies
    7
    Views
    3,870

    It's extremely marked up. All points are not...

    It's extremely marked up. All points are not exposed. You need to creat an export table in the insight software.


    Sent from my iPhone using Tapatalk
  27. Replies
    9
    Views
    3,000

    That is a Trane uc210 Sent from my iPhone...

    That is a Trane uc210


    Sent from my iPhone using Tapatalk
  28. Is the set point dial enabled? Also is CTL STPT...

    Is the set point dial enabled? Also is CTL STPT overridden? I only assume with the info you have that the set point dial is disabled. And you CTL STPT equals your DAY HTG STPT.
  29. Replies
    6
    Views
    2,547

    There is an FLN driver, but will only communicate...

    There is an FLN driver, but will only communicate to generic tecs. Custom applications and any extended io such as dpu, mpu and bims will not be discovered. Does the current insight server have the...
  30. Replies
    3
    Views
    3,047

    The SystControl is what you want, you'll be able...

    The SystControl is what you want, you'll be able to see all your indoor units as well as the outdoor unit.


    Sent from my iPhone using Tapatalk
  31. Replies
    9
    Views
    2,303

    The driver is very limited. Sent from my...

    The driver is very limited.


    Sent from my iPhone using Tapatalk
  32. Replies
    9
    Views
    2,303

    You will not ba able to see many devices when...

    You will not ba able to see many devices when using a p1 driver. Expansion modules such as pxms and bims, UCs DPMs and certain TEC applications.


    Sent from my iPhone using Tapatalk
  33. Replies
    6
    Views
    1,345

    I got water drops in my otterbox and phone...

    I got water drops in my otterbox and phone started going crazy. Giving a 1.5 year old a bath will do that.

    Sent from my SM-G900V using Tapatalk
  34. Replies
    6
    Views
    1,345

    Sent from my SM-G900V using Tapatalk

    Sent from my SM-G900V using Tapatalk
  35. Replies
    6
    Views
    1,345

    V'''v:v:v:v:vv::v:::v:'vv''vçccccccccccccccccccccc...

    V'''v:v:v:v:vv::v:::v:'vv''vçcccccccccccccccccccccvvvv:::::vvv::::::::::::::vvvvvv vvv

    Sent from my SM-G900V using Tapatalk
  36. You only need to hook up to one panel on a single...

    You only need to hook up to one panel on a single P2 network. Huge downside to that is the more points you have in point monitor the slower this solution will be. Your expectation shouldn't be to...
  37. No, you can not hook up the trunk interface to...

    No, you can not hook up the trunk interface to the jace, your only options are to use the csi driver thu the mmi port or if the insight server has a bacnet license, you can export the points via...
  38. Just found out on a lochenvar integration I'm...

    Just found out on a lochenvar integration I'm currently doing, lochenvar is now installing bacnet cards in the boiler and will no longer need the protonode. I'll be disovering these Friday to...
  39. Replies
    2
    Views
    913

    Are you designing this system yourself? Is...

    Are you designing this system yourself? Is Siemens your only option? Where are you located?

    Sent from my SM-G900V using Tapatalk
  40. The instance number applies to mstp as well. ...

    The instance number applies to mstp as well.

    Sent from my SM-G900V using Tapatalk
  41. Lochenvar has a field server that is pre...

    Lochenvar has a field server that is pre configured modbus to BACnet, used them several times with ease.

    Sent from my SM-G900V using Tapatalk
  42. Replies
    2
    Views
    1,021

    Wcis is the program you will need to connect to a...

    Wcis is the program you will need to connect to a tec. The max line driver only supports standard applications, it will not discover an dpu. Mpu or uc controller or special tec applications such as...
  43. There is a background object that is not defined....

    There is a background object that is not defined. They can drive you crazy, especially if there is a lot of lot of associations. Good luck.
  44. Replies
    5
    Views
    1,427

    It probably needs to be replaced. Are you writing...

    It probably needs to be replaced. Are you writing to any of the subpoints excessively?
  45. Replies
    9
    Views
    3,799

    Firmware upgrade can only be for through com...

    Firmware upgrade can only be for through com tools which is a not distrusted. Calling your local branch is your only option to upgrade.
  46. Replies
    11
    Views
    6,253

    Try network 9

    Try network 9
  47. Replies
    11
    Views
    6,253

    Have you discovered the devices thru the Web...

    Have you discovered the devices thru the Web browser, and verified all your devices were pulled in. There you should see your instance numbers.
  48. Replies
    6
    Views
    2,009

    Do datamate or wcis have a terminal emulator? I...

    Do datamate or wcis have a terminal emulator? I think they may, I'm used to using hyperterminal, dont remember what the keystrokes are to enable ethernet, you'll also need administration...
  49. Replies
    6
    Views
    2,009

    The 2.8 panels are made ether net thru...

    The 2.8 panels are made ether net thru hyperterminal. The earlier controllers will need to be flashed by Siemens
  50. Replies
    3
    Views
    1,351

    Validation of sensors for pharma

    I'm doing a pharmaceutical job where, I am using Vaisala current temp and humidity sensors. The customer has a third party validation company that wants to split and repeat my current signal to use...