Does the mobile site look like this? Or am I trying to use "full site" or desktop or whatever on my phone.
Per email from tapatalk today....Vertical Scope is made the decision to no longer make the h-talk forum available on tapatalk. So there is is. It sucks becsuse tapatalk is a far more user friendly...
100 psi flooded control.
That won't work when the ambiant temperature drops.
You'll need to do the 1.5 or 2 ton txv and #2 nozzle, and headmaster change.
Or better yet, change to an EEV and...
I've seen em on ebay methinks.
Sent from my SM-S901U using Tapatalk
I wonder if the piping is too small for the EEVs.
Compared to a TXV, EEV can/will open further initially, requiring more LL volume as it's controlling and maintaining say 8°SH on a high load...
Where did you find this "pro upgrade"?
Sent from my SM-S901U using Tapatalk
So does the correction factor get set once? Every once in a while?
Every job?
Does the hood come with a correction factor after you've sent it in for calibrating?
Sent from my SM-S901U...
I saw somebody do it once. On the three or 400 cfms per Outlet I don't remember the difference it made less than 3 CFM/per, which is meaningless. Particularly as the Flowhood can sometimes read up...
Yup. That's the way I'd go, even more, 20 or more likely. Lowers the capacity but decrease coil dewpoint too. Defrost may become an issue.
Keep an eye on DT.
Sent from my SM-S901U using Tapatalk
700 in the coil.
If the case runs about a 20 TD then that would be 17°, that'll be close to a 4 setting I think.
It's been a long time since I used one but what I used to do is wrap them around a...
Are you talking about a compression tank? The kind without a bladder that has a sloped pipe and a special air troll or similar fitting?
Sent from my SM-S901U using Tapatalk
@VTP99. What's happening for the cows that wanna be cool? Or is it people who want cool cows?
Sent from my SM-S901U using Tapatalk
Very likely that equipment is not rated for 40°f return air temperature. Typically I'd say 55 should be the very lowest, and 60 is much safer.
This is due to condensation forming in the heat...
Definatly some issues with this system.
You should go out with a senior tech and get full log data.
Also, if youre correct about no oil has been added, it sounds like the CC is not full of oil,...
What is your vacuum hose setup?
Sent from my SM-S901U using Tapatalk
We have a few chillers that cycle off at 41-45° ambiant due to full sizing. Chiller is mostly off from November to mid March. Otherwise they run full time. They are rtaa, rtac, and cgam, and...
Is this at your house?
Sent from my SM-S901U using Tapatalk
And grass clippings! Generates some weird looks lol.
Sent from my SM-S901U using Tapatalk
Do they have flow simultaneously WITHOUT the boiler circ on?
Do they flow simultaneously without the boiler circ on and the "ok" zone partially throttled?
I'm asking these things because...
Yes that's right Terry. Thats why I want him to play around with the zones only. Leave the boiler pump out of it and test the zones in various scenarios. Shoot, it's an interesting situation. It...
There are alot of funky piping jobs out there that work.
I see no reason the one there won't work. Doesn't mean it will work well, but it should still work.
What happens if you shut off...
I think this thread should be in AOP commercial. Not sure how much information we can divulge tho, until you get Pro status.
I will say though, that I think you have everything you need...
That's what is so weird about it[emoji846]
Sent from my SM-S901U using Tapatalk
Yup. Homerun me thinks.
Sent from my SM-S901U using Tapatalk
Is that pic showing that the p-switch OPENS on a RISE, and the DT never completes a circuit?....but can switch on a DROP in temperature?
Is that a HP switch shown?
How does t1-t2 ever close...
Long term hi head pressure would cause wrist pin wear. Due to the excessive pressure not allowing sufficient lubrication gap.
Sent from my SM-S901U using Tapatalk
Should probably be around 14 psi at setpoint.
I'm with pecsmg. Set your SH at 10 at the evap when your box is within 5°f of setpoint for starters. See how it shakes out from there.
Also,...
Merry Christmas all!
Sent from my SM-S901U using Tapatalk
Using that pressure probe....is that as good or better than using the Dwyer 460?
It would be on the report, which would be nice.
Sent from my SM-S901U using Tapatalk
What happens if you jump the p-switch?
Sent from my SM-S901U using Tapatalk
Yep the brand doesn't matter at all. It's the installation that's everything. And the service in the area.
You want to make sure that your lights are stretched out to at least 70% of their...
I just called about my 300. It also starts at 20.9 and subsequently goes to 2.6 after a combustion test. Power off and back on brings it to 20.9
They said to re-zero it. If it gets worse...
Hi Steve. I bid on one recently on ebay. I'd been high bidder at 41 for many hours then seconds before the auction ended someone went to 65. Oh well. I thought maybe someone here may have one, may...
I need one for one job for a rental. And I'd like to have it to use any time. (So don't want to borrow one)
Wondering if someone has a used one they'd like to sell?
Thanks!
Sent from my...
Possibly still missed soot burning off, giving you high C0.
Sent from my SM-S901U using Tapatalk
Hey TERY! Why's yr name spelt rong all a sudden?[emoji846]
Sent from my SM-S901U using Tapatalk
Coule thoughts:
Maybe the low side was isolated by compressor discharge check valve and eev?
It sounds like the bosses pump/rig is leaky.
If the fieldpiece got to 180 in 15 minutes on a...
Seems a bit suspicious that it's pulling 1.8. Just seems really high compared to the labeled pressure.
Sent from my SM-S901U using Tapatalk
Definatly not enough gas.
Find out what the gas company has to the meter and if you're allowed to up the main reg pressure. It may need a different spring and maybe orifice if you need to go to...
Get them to fire correctly first. That way you can at least trust they'll produce heat.
You need to know:
Boiler minimum/maximum input gas pressure. Does the gas pressure drop when boilers fire...
If it has its own circulator, is rotation correct? You can get flow, but weak flow with incorrect rotation.
Sent from my SM-S901U using Tapatalk
How the heck can one install that in 1.5 hours?
I'm not an installer, (but do wish I had more of those skills) but pretty sure it would take me 1.5 hours to simply read the manual lol.
Are...
You'll see check valves between the receiver and the "head master" at times. Basically anti migration and keeps the pressure that's in the reciever... in the reciever. Especially on a heated...
Isn't the circ by the zone panel backwards then?
Sent from my SM-S901U using Tapatalk
In that case, isn't the circ by the zone panel backwards?
Sent from my SM-S901U using Tapatalk
Why does Lochinvar have the relief on the boiler inlet?
Sent from my SM-S901U using Tapatalk
Lots of brownouts in this area. Just removes vfd power until vfd goes blank. Then reapply and happy fan.
They may have an auto reset option, but I don't know if/where tho.
Sent from my...
They are probably sized for low return water temp. Eg large delta T.
Allows the HE boiler to operate in the condensing area. For example, a 40-60 delta tee with 130- 150 inlet same btu output...
I have a few Carrier (Carlisle 15-25 ton semis) 35-60 ton RTUs converted to 407c. One, I added 1 qt POE. The others are straight mineral.
The maintenance man checks oil every few days for 3...