  1. What controllers are you dealing with? I have...

    What controllers are you dealing with? I have some and I'd be happy to share
  2. Replies
    7
    Views
    851

    Thanks for all the replies. I'm not onsite today...

    Thanks for all the replies. I'm not onsite today but if I remember correctly, the code was something like 2070. These are water source heat pumps.
  3. Replies
    7
    Views
    851

    Siemens FLN Network HP10 Controller

    Does anyone have a manual for a Siemens HP10 heat pump controller. I just replaced a dead Jace that was integrated to 94 of these but i was unable to get the database off of the Jace. I need to know...
  4. Replies
    9
    Views
    1,117

    I've got the following files: config.db...

    I've got the following files:

    config.db
    config.sms
    config.xml

    The db and xml files give me every point in the system. This system has hundreds of controllers, so it's taking a long time....
  5. Replies
    9
    Views
    1,117

    Thanks!

    Thanks!
  6. Replies
    9
    Views
    1,117

    Old Schnieder R2 Database

    Quick question for you gurus out there. Recently did a service call at a building with a bunch of TAC Lon stuff from 2004. The customer wants to rip it out. There is no access to the system and the...
  7. Replies
    35
    Views
    2,969

    The pic is slightly disturbing, but I can't look...

    The pic is slightly disturbing, but I can't look away! I don't know what hardware was used. It was installed by the customer's IT dept. I did use the secondary IP port on the Jace. I commissioned the...
  8. Replies
    35
    Views
    2,969

    Send it to me. This job went great! I've got 115...

    Send it to me. This job went great! I've got 115 EasyIO FT04's on a VLAN wifi network being brought into the Jace via BACnet IP.
  9. Thread: AAON ?

    by The Reaper
    Replies
    9
    Views
    1,352

    I just wired up a new Ebus stat today and asked...

    I just wired up a new Ebus stat today and asked tech support that exact question. My existing wire was 18/4. They said if the wire was shielded I was good to go
  10. Replies
    4
    Views
    1,197

    The customer wants this system gone. There is...

    The customer wants this system gone. There is nothing wrong with it, but he doesn't like the service provider and they are the only Delta dealer in the state. That being said, I am proposing putting...
  11. Replies
    4
    Views
    1,197

    Delta Controls Question

    I'm looking at replacing a Delta system and in the interest of saving some money, I am proposing taking control of all the central plant control and RTU control but leaving all the VAVs as is and...
  12. Replies
    10
    Views
    948

    Try something like this. It works just like an...

    Try something like this. It works just like an old pneumatic receiver controller. I've used this exact setup on many MZ units and it works great.
  13. Replies
    46
    Views
    2,171

    Great information! Thanks all

    Great information! Thanks all
  14. Thread: CGM in N2

    by The Reaper
    Replies
    20
    Views
    1,542

    Sorry to hear that! It took me 2 days of screwing...

    Sorry to hear that! It took me 2 days of screwing with it to make it work. The thing that really pissed me off is when I spoke with JCI, they said "you should never downgrade anything". I told them...
  15. Thread: CGM in N2

    by The Reaper
    Replies
    20
    Views
    1,542

    Sorry, I didn't see the first part of your...

    Sorry, I didn't see the first part of your question. I left the DC on the SA for about 30 seconds and I pulled it off, then hit the FC with the command.
  16. Thread: CGM in N2

    by The Reaper
    Replies
    20
    Views
    1,542

    My pleasure! It sounds like you are ready to...

    My pleasure! It sounds like you are ready to reload the main code back to 10.6. If you got the DAPP Ack message you are good to go. I don't think you can downgrade your MAP. If you're at the latest,...
  17. Thread: CGM in N2

    by The Reaper
    Replies
    20
    Views
    1,542

    After my controller was in test mode, I couldn't...

    After my controller was in test mode, I couldn't do anything with it. I got pissed and powered it down and went to lunch. When I came back, I powered it up and I was able to see it with my MAP,...
  18. Thread: CGM in N2

    by The Reaper
    Replies
    20
    Views
    1,542

    I don't think that matters. Is the SA flashing 2...

    I don't think that matters. Is the SA flashing 2 times rapidly? If so, it is in test mode and is ready to have the main code reloaded. I had to have the DC signal on my SA bus and my Hyperterminal...
  19. Thread: CGM in N2

    by The Reaper
    Replies
    20
    Views
    1,542

    My pleasure! It's on its way

    My pleasure! It's on its way
  20. Replies
    1
    Views
    299

    I have them. I tried to post them, but the...

    I have them. I tried to post them, but the website doesn't like the extensions. I'll email them
  21. Thread: CGM in N2

    by The Reaper
    Replies
    20
    Views
    1,542

    In my situation, I was running CCT 10.5 and I...

    In my situation, I was running CCT 10.5 and I installed a replacement controller for an old AHU102-0. The CGM came from the factory with the boot and main at 10.6. When I downloaded the controller,...
  22. Thread: CGM in N2

    by The Reaper
    Replies
    20
    Views
    1,542

    Did you downgrade the main code at all? If so,...

    Did you downgrade the main code at all? If so, this kills the SA Bus and does exactly what you described. There is a way to factory reset the controller. When you do this, your MAP needs to be at...
  23. Replies
    14
    Views
    1,569

    They are under the cover of the CGM. They are...

    They are under the cover of the CGM. They are just above the input terminal blocks. Last week, I upgraded a DX9100 that used a 4-20 pressure sensor that was powered off of the 15VDC onboard. I could...
  24. Replies
    14
    Views
    1,569

    Make sure you set the jumper correctly for the...

    Make sure you set the jumper correctly for the corresponding input if it's 4-20. Had that one bite me last week with a CGM.
  25. Why not just drop a label over the buttons with a...

    Why not just drop a label over the buttons with a colored background to hide them. I'm not aware of any other way.
  26. Thread: GX-9100

    by The Reaper
    Replies
    4
    Views
    1,125

    http://support.controls.johnsoncontrols.com/?cid=7...

    http://support.controls.johnsoncontrols.com/?cid=74&c=12&cpc=v7dS6AKprgyf54GU44uK3RC2#tab:homeTab:crumb:8:artId:34776:src:article

    I think this is your problem
  27. Replies
    5
    Views
    634

    Man! Sounds like you're almost as old as I am!...

    Man! Sounds like you're almost as old as I am! Used a bunch of those palm pilots. Right now I run a Windows 2000 VM with S2 convertor. Works great. Running a full PMI install on the same VM
  28. Replies
    5
    Views
    729

    Thanks man!

    Thanks man!
  29. Replies
    14
    Views
    1,457

    Found this on the JCI help site: Be careful...

    Found this on the JCI help site:

    Be careful when applying a max write time to points, especially controller hardware BOs and AOs. It has been found that if you have a point mapped with a max write...
  30. Replies
    5
    Views
    729

    Thanks for the quick reply! Unfortunately I can't...

    Thanks for the quick reply! Unfortunately I can't access the unit. The roof access is not finished yet. Is there a way I can change the IP settings through the IP connection. There was nothing in the...
  31. Replies
    14
    Views
    1,457

    How frequently does it happen? Can you disconnect...

    How frequently does it happen? Can you disconnect communications and see if it stops?
  32. Replies
    5
    Views
    729

    Trane RTU BACnet IP

    I have a site that has a Trane makeup air unit that is connected BACnet IP. I can access it through a browser but not through the Jace. The subnet on the Jace is 255.255.255.0 and the unit is...
  33. Replies
    14
    Views
    1,457

    Check your tuning policy. Make sure it's set to...

    Check your tuning policy. Make sure it's set to the default policy.
  34. Replies
    11
    Views
    1,372

    What a dope I am! I ended up not having a role...

    What a dope I am! I ended up not having a role assigned to my station to supervisor password! Thanks for all the replies!
  35. Replies
    11
    Views
    1,372

    I did a ping ans it pings fine. Then I did a scan...

    I did a ping ans it pings fine. Then I did a scan with nmap and it shows 4911 and 5011 open. I'm stumped! The user account info is good and the Super is online in the Jaces Niagara Network but still...
  36. Replies
    11
    Views
    1,372

    Will do. Thanks! I'll post results.

    Will do. Thanks! I'll post results.
  37. Replies
    3
    Views
    4,537

    Boiler Room Controls Before and After

    A recent boiler room controls upgrade. Ripped out 2 old JCI UNT111's and an NAE that was left dead on the wall. Rewired all high voltage to boilers and pumps .
  38. Replies
    11
    Views
    1,372

    I haven't tried a ping but the Supervisor is...

    I haven't tried a ping but the Supervisor is online consistently in the Jace's Niagara Network. I'll try when I'm back onsite.
  39. Replies
    11
    Views
    1,372

    Yes. No schedules show up to import. Also, I made...

    Yes. No schedules show up to import. Also, I made some various global points and I cannot see them either when I do a point discover. The Supervisor is on a VM.
  40. Replies
    11
    Views
    1,372

    Yes, the schedules are in the Supervisor. I can't...

    Yes, the schedules are in the Supervisor. I can't discover them in the Jaces.
  41. Replies
    11
    Views
    1,372

    Supervisor Scheduling

    I have 2 Jaces being brought into a Supervisor. All points pulled in fine but I can't discover any points or schedules from the Jace side to the Supervisor. I'm trying to map in my Supervisor...
  42. Replies
    4
    Views
    822

    I tried it with Chrome and Firefox

    I tried it with Chrome and Firefox
  43. Replies
    4
    Views
    822

    Thanks Digo!

    Thanks Digo!
  44. Replies
    4
    Views
    822

    N4 Supervisor Graphics Error

    I just put a new Supervisor online to 7 Jaces. They are all Honeywell 4.10. The Supervisor is on a VM provided by the customer's IT. When I try to make a browser connection, I get this error (see...
  45. Replies
    13
    Views
    899

    From memory, I seem to remember a few sites I...

    From memory, I seem to remember a few sites I took care of that shared points between NCM's. I believe it is possible to have a program in 1 NCM trigger points in another one.
  46. Replies
    13
    Views
    899

    Could the processes be buried inside another one?...

    Could the processes be buried inside another one? Can you send me the GPL folder? I have a PMI workstation on a VM.
  47. Replies
    2
    Views
    3,099

    N4 Supervisor Schedules

    I'm putting in a supervisor and pulling in 8 N4 Jaces. When I pull in the existing schedules, it looks like I cannot edit them, just view only. Is there a way that I can modify Jace schedules from...
  48. That was it! My password was 11 characters....

    That was it! My password was 11 characters. Thanks!
  49. Thanks guys. I did try multiple browsers and...

    Thanks guys. I did try multiple browsers and machines. Waiting for CC tech support to respond.
  50. Contemporary Controls BASRT-B BACnet IP/mstp Router

    I went to set up this router today and ran across an issue that's got me stumped. Direct connection with laptop and ethernet cable, I log in with the default creds and it says I need to change the...