As the guy from Maine says "You can't get there from here!" Exec 4 never supported BACnet.
Type: Posts; User: Doug-e-fresh
As the guy from Maine says "You can't get there from here!" Exec 4 never supported BACnet.
I have seen this done with unitary equipment like VAV's and Air Handlers. Example: if you selected to change from a parallel to a series PIU through a dropdown box either on the graphic itself or in...
All of the Mitsubishi compressors are variable speed. From the residential Mr Slim to the largest commercial unit. I can't speak for Sanyo.
A JACE will not commision over LonIP.
I had a Transit Connect at my last job. I do not recommend them. We had several in the company and about 30% had transmission problems at 20,000 miles. Probably because they had more weight than what...
You really need the Lutron guy there with you. They have to program their panel to expose bacnet. I spent several hours trying to bring in a Lutron panel only to discover they had not set up their...
Based the info from DIGO, yes having the router installed will make a difference. Install the router as it was on the original system. From Spec Data:
Communications:
The W7751G uses a...
1. Have you commisioned the devices in LON? Sometime just discovering does not do the trick.
2. Discover some points and then do a bind.
Another Question, when you discovered the devices what is...
According to Honeywell's website they are FT-10
http://customer.honeywell.com/honeywell/ProductInfo.aspx/W7751G1003
Try installing the lonhoneywell jar file on your JACE and then rediscover the LON trunk and see if it matches any of the existing LMNL profiles. The fact that you are reading weird values means...
If it's a TNI, yes it is legacy CMnet. At least 15 to 20 years old. Probably part of legacy migration to WebCTRL.
Most JACE's ride through power blips like that just fine. They all have an on board battery. If the battery is more than 2 to 3 years old it may need to be replaced. Check the diagnostics in the Jace...
Your programming issue lies between the chair and the keyboard.
Look under the network tree. The driver will be FB-15 under the CM number for the TNI card. On all legacy controllers used FB-15 for the drivers.
How many System 3 units do you have and what is the Vintage? Very old System 3s may not be able to take an IntelliSlot. Also is the SiteLink a "one part" (IGM ports on the bottom) or "two part" (two...
SiteLinks do not support SNMP directly. In the past the best you could get was SNMP alarms via SiteScan Web for abnormal conditions. No operational data. In order to get SNMP data from Liebert units...
You may want to look at this site as well to make sure. I just did one and I was able to see everything but to prevent local setpoint control and scheduling the documentation is essential....
Unless it is specified in the original contract, no that software is not routinely provided.
:ditto:
I would add one more item, make sure all the JACEs are "open" so that any Tridium dealer can access it.
If you like Carrier you would LOVE AutomatedLogic's WebCTRL. WebCTRL is like i-VU on steriods.
The reason the units continue to run is because they are LON based. On LON units, to occupy a unit the...
Do you have an issue finding these guys in Rover? Make sure DSN A is showing up in Rover. If you can't find the controllers in Rover than you either have a bunch of bad controllers or more likely a...
Have the chillers ever talked with Alerton? Or were they part of Tracer Summit?
As of July 2011,( my last Spyder job I did before changing jobs) Rapidbalance did work with standard apps. You need to get the latest and greatest from the Honeywell buildings website for both the...
Are you using the LMNL object from Tridium or did you discover the controller as a dynamic device? I have found out that depending on the vintage of the Trane device, the Tridium object is wrong and...
Most of the time the stop is included in the box with the actuator. If not than that kit would be right.
Try doing a "Clear Ram and Reset" on both BCU's. Also want to acknowlege and delete all the alarms if there are a bunch of them. BCUs are not very good memory managers and sometimes you need to free...
Are the two workstations the same version and rev? Also what is the version and rev? I had site like that and the latest service pack took care of it.
Try this:
http://eikonforeducators.automatedlogic.com/eikon.nsf/605a21551bf892ac852573a80071d6ba/3029d4e39e29c5f5852574e9006b852e?OpenDocument
You won't see any Comm4 Voyagers on Rover. Those triangle shape boards are to change from Comm3 to Comm4 and Vice Versa. Make sure they are in the Comm4 position or you won't see it in on the JACE.
Try learning the LCI as a dynamic device and learn NV. You will have to null out the reference and save. Then you can learn the NV. I have had to do that to a few Trane LON devices when the LMNL did...
Did you use a null modem adaptor?
I generally agree with krac, the BCU does a LOT of control in the building. If integration is what you want why reinvent the wheel and have to recreate all that programming in a JACE? Aside from the...
Works the same in the SCC profile. The damper modulates to maintain zone temp. At least the last six I have worked on.
My experience has been that the OA dampers do close when unoccupied. The SNVT is used to set the Min OA Damper position used for ventilation requirements. On units that have economizer operation, the...
See if this helps.
http://specifyhoneywell.com/customer/Honeywell/UI/UserControls/ProductCatalog/Search/getliterature.axdXXLiteratureIDYY95-7668.pdf
It should explain alot.
Your assuming he has Rover and knows how to use it. If ControlY0urMind has Rover, he will need to upload all of the programs out of the contoller. The last time I upgraded a controller to the latest...
Was the MP already on another LON system and you are trying to learn the bindings? If the MP was bound to another device that is not in your database,(i.e. BCU) the quick learn will fail. If not try...
Look at this. The company is in England but they are using iPhones so it should work on iPads as well. Met the owner at the Niagara Summit a couple of years ago.
http://www.tyrrellsystems.com
What area of the world are you located? Look on the AutomatedLogic website and see if there are any dealers / factory offices in your area. If there is you probably don't have a snowballs chance in...
What is driving the touch screen? What behind it sending the data to and from the RTUs and Unit heaters. I have used Touch Screens (HMIs) and programmed a few. All of them had to be connected to...
Good luck with that. If they can't help you find someone that can do Tridium R2. If your customer has a WebSupervisor, all the programming can be done from it.
It sounds like you turned an old Intellipak into a new Intellipak with a brain transplant.
A very good point. If you can commission the LON devices from the controller without a third party program it will make adding and or replacing LON devices much easier.
Try this
http://hvac-talk.com/vbb/showthread.php?t=718181
It has a PDF copy of the IOM
After you get them all up on LON then you must decide how fancy you want your interface (front end). Web based? You could use a I-lon Smartserver or a JACE. Single seat? Why?:.02:
One question. Are you doing this Pro Bono or as an exercise to see if it can be done? If not, you are not doing your customer any favors. What is the cost of a NAE4510 if it crapped out and had to be...
There is a free download of a Bacnet sniffer program from Cimetrics. It is a Demo version and shuts it self down in I think 29 mouse clicks but it is very useful in finding the information you are...
Before you run off to the jobsite you might want to check if you can log in without the computer connected to your corporate network.
I had the same issue with some Intellipacks. I would try to commision them and they would fail. It was an issue with the LMNL file in AX. What I had to do was bring the device in as a dynamic device...
Your Modstat shows you running ARC156, so changing the Baud rate on the board won't do anything. Also if you could change the Baud rate you would have to do every module on the network as well.
I...