Search:

Type: Posts; User: apprentice3

Page 1 of 20 1 2 3 4

Search: Search took 0.03 seconds.

  1. Replies
    2
    Views
    231

    The WCI devices communicate BACnet Zigbee back to...

    The WCI devices communicate BACnet Zigbee back to the Tracer SC's WCI. I believe the hardwired communication protocol from the WCI to the SC is some form of IMC communication (proprietary to Trane)....
  2. Replies
    57
    Views
    17,495

    I have a copy of it that I can send you. I am...

    I have a copy of it that I can send you. I am not sure of the exact date that Trane stopped producing these controllers, but I will say that you stopped seeing them installed around 2008. The MP580...
  3. HydroTherm S-8 Control Panel Manual Needed

    I have a job site that has a old 1993 HydroTherm S-8 control panel that is used to stage multiple boilers. I was wondering whether anyone has a manual for one of these? I can't seem to find one...
  4. Replies
    9
    Views
    2,365

    I have successfully integrated a new Trane...

    I have successfully integrated a new Trane Centaurus Prime gateway into the NAE sitting under a Johnson Controls Metasys system. I was on site performing some testing today and I noticed that...
  5. Replies
    11
    Views
    2,971

    Remind me of the Cylon software you're using? Is...

    Remind me of the Cylon software you're using? Is it called Command Centre? If so, it isn't something that was used in America and I am not very familiar with it. If you're working in Unitron...
  6. Replies
    9
    Views
    2,365

    Thank you for this information! Is MCT built...

    Thank you for this information! Is MCT built into SCT? Or is it a totally separate application?
  7. Replies
    9
    Views
    2,365

    I believe the customer has SCT running on the ADS...

    I believe the customer has SCT running on the ADS server. I will look into using that tool later this week. Thank you for your reply!
  8. Replies
    9
    Views
    2,365

    Metasys Integration/ Device Templates

    I have been tasked with integrating a Trane RTU Gateway into a NAE on a older Johnson Controls Metasys system. I have worked around Metasys for awhile, but have never had to add multiple devices and...
  9. Thank you everybody for all of the feedback. I...

    Thank you everybody for all of the feedback.

    I will say that drawing provided by the mechanical engineer isn't 100% accurate. There was really no work performed on the condenser side of the...
  10. Since we're talking about bypass valves. I was...

    Since we're talking about bypass valves. I was wondering if anyone has seen a bypass valve installed like the one on the drawing below? On every single job that I have been a part of the bypass...
  11. The chillers are Daikin WME (magnetic bearing). ...

    The chillers are Daikin WME (magnetic bearing). The chiller struggles with getting the lift pressure up after the transition.
  12. I am already doing that for a set amount of time....

    I am already doing that for a set amount of time. The customer doesn't want the chilled water temperature to get too high when transitioning, so I have some limitations. I will keep pushing them to...
  13. The piping on this system is very large, so it...

    The piping on this system is very large, so it isn't cheap to get the bypass valves installed. That is the reason why they are asking me to do things that aren't normal. Trust me, I have mentioned...
  14. Cooling Tower Sump Heater Control Question

    I have a customer who isn't wanting to spend the money to install a bypass valve on their condenser water loop/ cooling tower right now. The system in question has a plate and frame heat exchanger...
  15. Reliable MACH-ProAir MPA 33 VAV Controller Question

    We have a customer who has Reliable Controls. They have been having a ongoing issue on a application with pneumatic VAV boxes. They're using the Reliable Controls MPA 33 VAV controller to send a...
  16. Thank you for your reply! Very helpful...

    Thank you for your reply! Very helpful information!

    I can look into the Lonworks option. Just to make sure that I have all of my bases covered, I want to make sure that I have the right hardware...
  17. Tracer Summit Intellipak and Non-Trane BACnet Device

    I have a customer with a Tracer Summit system that communicates to some Trane Intellipak RTUs (TCI) and some Trane VAV boxes (UCM) over Comm4. This particular customer wants to replace their RTUs...
  18. Replies
    0
    Views
    2,527

    TAC Vista Email Server Settings

    I have a customer with a TAC Vista system that used to email them alerts/ alarms, but doesn't seem to be working any longer. I started to look into the issue and I found the "Alarm Receivers" for...
  19. Replies
    4
    Views
    1,243

    That is what I was afraid of. Thank you for your...

    That is what I was afraid of. Thank you for your feedback!


    Sent from my iPhone using Tapatalk
  20. Replies
    4
    Views
    1,243

    Trane ZN517 Dehumidification Sequence

    I have a job site that has some Trane ZN517 controllers installed on some fan coil units (hot water and chilled water). I reviewed the manual for this controller and it indicates that a humidity...
  21. Replies
    9
    Views
    629

    You can utilize polygons and setup mouseovers by...

    You can utilize polygons and setup mouseovers by adding/ configuring the properties of the polygons. A polygon will allow you to plot points over your floorplan irregularly until you complete the...
  22. Replies
    12
    Views
    1,159

    I was sent the files to convert the RTU Open from...

    I was sent the files to convert the RTU Open from VAV to CV (opposite of what you have going on). We reviewed all of the options with the general contractor, engineer, and Carrier. In our case, we...
  23. BCI-I Intellipak Intermittent - Diagnostic - Invalid Unit Configuration

    I have a building that has (2) Trane Intellipak RTUs that were installed about 3 years ago that will randomly send "Diagnostic - Invalid Unit Configuration" down to the Tracer SC+/ Synchrony system. ...
  24. Replies
    12
    Views
    1,159

    If you can send over the files that may be...

    If you can send over the files that may be helpful. Based on Balibe's response it sounds like there is quite a bit of work involved with this conversion (outside of the programming requirements). ...
  25. Replies
    12
    Views
    1,159

    Thank you for this information. These are some...

    Thank you for this information. These are some of the things that I fear. We have been working with Carrier on this. I just received word from Carrier that they are going to provide us with...
  26. Replies
    12
    Views
    1,159

    This residential zone damper system is designed...

    This residential zone damper system is designed to operate at .5" w.c. They ordered this RTU with a high static fan rated at 1.5" w.c. These residential zone dampers have cheap low torque actuators...
  27. Replies
    12
    Views
    1,159

    It isn’t a VAV system. It is a low pressure...

    It isn’t a VAV system. It is a low pressure Honeywell residential zone damper system with standard thermostatic control. Right now the unit can’t take in commands from a system like this. The...
  28. Replies
    12
    Views
    1,159

    Carrier RTU-OPEN Board Applications

    I have been brought into a project gone wrong and I had a few questions in regards to some Carrier RTUs with a RTU Open Boards.

    There were some existing RTUs with standard thermostatic control...
  29. Replies
    10
    Views
    1,018

    Thank you for the information. This is very...

    Thank you for the information. This is very helpful!
  30. Replies
    10
    Views
    1,018

    This ended up working out for us on certain...

    This ended up working out for us on certain units. Is there a way to do this on the PremierLink RTUs? Can a centralized SNAP program be stored in one of the controllers and we simply reference it...
  31. Replies
    1
    Views
    513

    Outdoor Rated Smoke Control Damper?

    I have a customer who has (4) large pressurization fans for their smoke management system. The fans are used for the stairwells and hoist ways for some elevators. The installing contractor didn't...
  32. Replies
    7
    Views
    522

    Thank you for all of the replies! This site does...

    Thank you for all of the replies! This site does have Lonmaker installed and I reviewed all of the different Visio files that show all of the SNVTs/ references and nothing shows how they're getting...
  33. Replies
    7
    Views
    522

    TAC Vista Network Points

    I have a site with a TAC Vista system. I am trying to track down a outside air temperature reference and I am having a hard time figuring out what all it goes to and in some cases where it is coming...
  34. Replies
    7
    Views
    1,119

    What kind of i-VAV controllers are you dealing...

    What kind of i-VAV controllers are you dealing with? Are they TSC iVAV controllers or TLC iVAV controllers? This is very important to know because a TSC iVAV controller isn't BACnet visible. In...
  35. Replies
    7
    Views
    1,119

    I have a lot of experience with Teletrol...

    I have a lot of experience with Teletrol eBuilding systems. I have integrated certain portions of Teletrol eBuilding into a Tridium N4 system before. What all are you trying to do? Are there...
  36. Replies
    15
    Views
    1,058

    No unfortunately not. You will need Tracer TU to...

    No unfortunately not. You will need Tracer TU to get TGE to edit graphics.


    Sent from my iPhone using Tapatalk
  37. Replies
    12
    Views
    1,582

    Oh okay. I will look into that with the startup...

    Oh okay. I will look into that with the startup technician.
  38. Replies
    12
    Views
    1,582

    We only have one bypass valve output but we have...

    We only have one bypass valve output but we have two chillers. Which chiller takes priority control over the bypass valve/ cooling tower VFD speed? It makes sense to ramp the chillers together, but...
  39. Replies
    12
    Views
    1,582

    Daikin WME Chiller Controls

    I am working on a project with two Daikin WME Magnitude chillers with a common condenser header, a single bypass valve, and two cooling towers with VFDs. The Daikin startup technician, the Daikin...
  40. Thanks for the information. Yeah, I have more...

    Thanks for the information. Yeah, I have more experience with the BCU as well. Setting up LON devices under Tracer SC is still pretty new to me. I have replaced devices like VV550 controllers and...
  41. I believe the protonode has a way for me to input...

    I believe the protonode has a way for me to input the DSN through its field server interface. I do wonder how to determine what domain the SC is looking for. Does the Rover tool in active mode show...
  42. Thank you for your reply! I do have a copy of...

    Thank you for your reply! I do have a copy of the Rover service tool. I have always wondered when I would need to utilize active mode. I have only used passive mode. I don't have NlUtil and...
  43. Tracer SC Lonworks Protonode Integration Questions

    I have a building with a Tracer SC that has a Lonworks protonode with three Paterson Kelley boilers connected to it. The customer just had one of their boilers changed out with a newer Patterson...
  44. Replies
    34
    Views
    16,951

    Username: aam Password: integra I doubt...

    Username: aam
    Password: integra

    I doubt that these credentials will work. Most contractors don’t use default credentials.


    Sent from my iPhone using Tapatalk
  45. Replies
    20
    Views
    2,741

    I saw you tried to email me as well. I have a...

    I saw you tried to email me as well.

    I have a lot of documentation. However, most of my training documentation is in large lab books. I would have to check on what I have over electronic. I...
  46. Replies
    20
    Views
    2,741

    Yes, you’re correct. Integra is just a ABB...

    Yes, you’re correct. Integra is just a ABB branded JACE. It is very similar to Distech. The Distech JACE uses a BCP network with built in tuning policies and functionality for their controllers...
  47. Replies
    13
    Views
    1,486

    When your setpoints aren't matching what you're...

    When your setpoints aren't matching what you're sending it is almost always a scaling issue. Even though a GBAS module may be rated for 0-5 VDC (as an example) you may have to have your scale set at...
  48. Replies
    20
    Views
    2,741

    I have included product data sheets for the...

    I have included product data sheets for the Matrix, Nexus, and Enterprise below so you can compare certain specifications.

    844567

    844569

    844571
  49. Replies
    20
    Views
    2,741

    The Nexus and Matrix are Aspect's version of a...

    The Nexus and Matrix are Aspect's version of a JACE. The only difference between the two controllers is the type of devices they can integrate and the amount of project resources they can handle. A...
  50. Replies
    13
    Views
    1,486

    We you go to setpoint source selections, do you...

    We you go to setpoint source selections, do you see the discharge air cooling setpoint? If so, what does it say next to it? (Human Interface)? When you use the + and - buttons what options do you...