    I hope they have a low ambient kit installed....

    I hope they have a low ambient kit installed. 61-65*F is a tall order. I’d be surprised if their indoor coil wasn’t partially freezing
  2. If you hook gauges to it you are wasting your...

    If you hook gauges to it you are wasting your time. Recover, fix leak, evacuate, weigh in new charge. Make sure to pressure check to at least 650PSI
  3. Replies
    25
    Views
    2,363

    I really recommend doing everything you can to...

    I really recommend doing everything you can to avoid using dye. Do you have a good electronic leak detector? I love my H-10. Dye is just terrible. But if you must use it and have a decent amount of...
  4. Thread: MO-99

    by BollingJ3068
    Replies
    24
    Views
    7,176

    I personally am not a fan of drop in’s. Will...

    I personally am not a fan of drop in’s. Will never have an issue if you use the refrigerant it’s supposed to take. Just my opinion
  5. Replies
    63
    Views
    116,365

    I didn’t notice the original post date. I noticed...

    I didn’t notice the original post date. I noticed the last comment on 8-16-20. I literally just started using this site today
  6. Replies
    63
    Views
    116,365

    I do not. I was told this by a coworker who I...

    I do not. I was told this by a coworker who I trust immensely. I do not know if it is true or not but he’s usually not wrong. But he’s the only one I’ve ever heard say that
  7. If you have a Ductulator you can check duct...

    If you have a Ductulator you can check duct sizing. That brings us back to airflow lol
  8. Replies
    63
    Views
    116,365

    Reading that made me cringe! NOOOOO ITS NOT OK!...

    Reading that made me cringe! NOOOOO ITS NOT OK! He needs to recover it all, changed the filter drier, evacuate and charge with fresh refrigerant at minimum. However my understanding is 410A is...
  9. Replies
    17
    Views
    3,398

    Summer 2018 carrier inverter boards for the...

    Summer 2018 carrier inverter boards for the 24VNA9’s (5 stage inverter AC) were sometimes back ordered 30+ days. They had a massive issue with them and a ton of boards failed. Our supply house in...
  10. Replies
    8
    Views
    1,068

    To be fair, why are you trying to repair an 8...

    To be fair, why are you trying to repair an 8 year old $250 dehum? Throw that thing out and buy a new one 😂
  11. Sounds like lack of airflow. I understand you...

    Sounds like lack of airflow. I understand you have it set at 400 CFM per ton but are you actually moving 400 per ton is the question. I would confirm that.

    You also said it’s a new house? Make...
  12. I can’t speak for Bosch specifically because...

    I can’t speak for Bosch specifically because we’re a Clomatemaster dealer but I’ve had the same issue and the sensor was grounding out to the metal drain pan. Was intermittent and didn’t do it all...
  13. Replies
    4
    Views
    10,591

    I second what the guy above me said. Put in a...

    I second what the guy above me said. Put in a Honeywell Prestige with a wireless outdoor sensor and run the heat pump to 40*F then after that have it kick over to gas. I’d install at least a 2 stage...