  1. I use a Flir One Pro plugs into my iPhone and iPad

    I use a Flir One Pro plugs into my iPhone and iPad
  2. Trend the liquid level condenser water entering...

    Trend the liquid level condenser water entering and leaving temps , %fla and subcooling in the Optiview Trend screen over say an 8 hour period and see what the actual physical liquid level is in the...
  3. Replies
    9
    Views
    627

    Stick a magnet beside the sightglass

    Stick a magnet beside the sightglass
  4. Replies
    14
    Views
    987

    I would consider the discharge superheat as a...

    I would consider the discharge superheat as a critical part of efficiency / load / refrigerant charge analysis especially at full load
  5. Replies
    56
    Views
    19,031

    Yes you should quote to remove charge weigh it...

    Yes you should quote to remove charge weigh it and establish how is lost , typically you can lose about 40% before it starts to seriously affect and cause issues . Repair leak pressure test evacuate...
  6. Replies
    56
    Views
    19,031

    The physical liquid level in the condenser...

    The physical liquid level in the condenser sightglass should be between 1/3rd and 1/2 the level setpoint on. The screen can be anywhere between 40-60% setting , it doesn’t really matter , what...
  7. Replies
    8
    Views
    3,226

    You would have to contact PTS in Jadec York Pa...

    You would have to contact PTS in Jadec York Pa for info on OM chillers as each batch can be unique
  8. Replies
    13
    Views
    6,652

    Does the VSD have a harmonic filter too ? Are the...

    Does the VSD have a harmonic filter too ? Are the gate driver boards powered from the SCR trigger board ? Have you conducted a gate driver test using the TEST button on the VSD logic board ? Do the...
  9. Replies
    44
    Views
    11,758

    Edwards Oil sealed rotary vane vacuum pumps are...

    Edwards Oil sealed rotary vane vacuum pumps are the best in the business and been around for half a century
  10. Replies
    13
    Views
    6,652

    Did you replace the I/O logic board at the same...

    Did you replace the I/O logic board at the same time, it is the one beneath the main motherboard in the Optiview panel. Also, it is normal on power up of the Optiview to get a control panel loss of...
  11. It can vary depending on what setting you have in...

    It can vary depending on what setting you have in the sub-cooler portion of the micro-channel condenser , the level in the Flash tank is not controlled it is floating, that can also depend on the...
  12. On early machines it came from the compressor ,...

    On early machines it came from the compressor , discharge from the side of the compressor, we moved it to the downstream side of the oil separator as we found that the original position was no dry...
  13. Replies
    18
    Views
    9,978

    Why are you changing the oil ? Has the analysis...

    Why are you changing the oil ? Has the analysis recommended changing the oil ?
  14. Replies
    10
    Views
    12,344

    The reason for the alarm is because you need to...

    The reason for the alarm is because you need to ensure you always have a liquid level in the Condenser to ensure you are always feeding liquid refrigerant to the falling film evaporator , at very low...
  15. Replies
    37
    Views
    8,855

    Hi Moideen, I think even if you answer him he...

    Hi Moideen, I think even if you answer him he will then come up with something else to berate you with or berate others, if he insists on an answer get him to right the question down, sounds like he...
  16. Replies
    19
    Views
    2,730

    Are you sure what the refrigerant is and a...

    Are you sure what the refrigerant is and a picture of the plant would be nice just to give people an idea is size , capacity etc, plus although it is sensible to have planned replacement years ago...
  17. Replies
    9
    Views
    1,813

    I would dis-connect motor leads at the motor...

    I would dis-connect motor leads at the motor terminals and check the readings there at the motor terminals, is the chiller under positive refrigerant pressure? Is the refrigerant contaminated with...
  18. Replies
    19
    Views
    2,730

    Have to agree with that, well put

    Have to agree with that, well put
  19. Replies
    7
    Views
    1,620

    If only i had two mouths, i could drink more

    If only i had two mouths, i could drink more
  20. Replies
    19
    Views
    2,730

    You have got to replace with new really, the fact...

    You have got to replace with new really, the fact that this may not be a convenient time is something that should have been considered and planned for years ago. When you look at the refrigerant used...
  21. Replies
    7
    Views
    1,620

    And if the seal blows you will lose all the...

    And if the seal blows you will lose all the refrigerant a lot of oil and a big mess
  22. Replies
    9
    Views
    1,813

    Agree with HYP ,

    Agree with HYP ,
  23. Replies
    19
    Views
    4,913

    And I am guessing you run 25-50 hz on a 400/3/50...

    And I am guessing you run 25-50 hz on a 400/3/50 system so 50hz is your max speed


    Sent from my iPhone using Tapatalk
  24. Replies
    19
    Views
    4,913

    Check that your oil eductor is working correctly,...

    Check that your oil eductor is working correctly, the evaporator could be oil logged


    Sent from my iPhone using Tapatalk
  25. Replies
    4
    Views
    2,467

    2. At the keypad, login at SERVICE access level...

    2. At the keypad, login at SERVICE access level using code 1 3 8 0.
    3. Select Condenser screen.
    4. Press the FAULT ACKNOWLEDGE key on the Condenser Screen. A dialog box appears displaying “Enter...
  26. Replies
    2
    Views
    964

    You will have to contact JCI in Singapore , let...

    You will have to contact JCI in Singapore , let them know if the chiller was made in Wuxi, San Antonio or Nantes
  27. Replies
    8
    Views
    1,866

    It is the common mode fuse FU27 see page 22 of...

    It is the common mode fuse FU27 see page 22 of attached diagram

    regards

    816119
  28. Thread: YVAA fan motors

    by raptyr
    Replies
    8
    Views
    2,857

    EBM fan deck will bolt straight on there , you...

    EBM fan deck will bolt straight on there , you can even scrap the ABB and use EBM EC fans and daisy chain the signal for speed from a new discharge transducer. EBM are better quality but cost more...
  29. Thread: YVAA fan motors

    by raptyr
    Replies
    8
    Views
    2,857

    I would swap them for EBM fans, make sure the...

    I would swap them for EBM fans, make sure the little cooling fans on the ABB drive are working (if they have failed you get a loss of comms message on the ABB VFD, replace them with locally purchased...
  30. Thread: YAEP99XD9B50PA

    by raptyr
    Replies
    5
    Views
    3,171

    Did you peel the thin film off the display before...

    Did you peel the thin film off the display before mounting it ? Did the new display work fine then fail again ? or are you getting unusual characters on the display, check the cables are the correct...
  31. Not broken one yet in 18 months, so far so good ��

    Not broken one yet in 18 months, so far so good ��
  32. Good news , if you can get some logs following...

    Good news , if you can get some logs following the instructions i sent you then that would be helpful too. As for the 'setting' procedure, finally , although it is better on the YMC2 than a YK , with...
  33. mailed it Chillmac

    mailed it Chillmac
  34. check your mail Lucas

    check your mail Lucas
  35. I could email you the document but your email is...

    I could email you the document but your email is not in your profile
  36. Upload a history log for us to look at ?

    Upload a history log for us to look at ?
  37. Replies
    13
    Views
    2,998

    This may help a little 814874 Regards

    This may help a little

    814874

    Regards
  38. Replies
    13
    Views
    2,114

    How frequently is the problem happening? Do it...

    How frequently is the problem happening? Do it occur at the same time every day ? Is there a trend to it? Can you run the chiller in Local Mode with the BMS dis-connected ? Then see if it trips, you...
  39. Thread: York YR

    by raptyr
    Replies
    9
    Views
    1,232

    It could be the coalescers in the Oil...

    It could be the coalescers in the Oil sump/separator, you should check at any place you can along the compressor discharge , separator inlet, separator outlet, condenser inlet, if there are any...
  40. Thread: York YR

    by raptyr
    Replies
    9
    Views
    1,232

    I just checked a log i had from a few years ago...

    I just checked a log i had from a few years ago of one running full load , size of chiller is not really relevant but here is the log814593
  41. Replies
    13
    Views
    2,114

    Well it looks like a remote interlock is stopping...

    Well it looks like a remote interlock is stopping the chiller then re-starting it, what remote interlocks have you got wired in ?
  42. Thread: York YR

    by raptyr
    Replies
    9
    Views
    1,232

    I would expect the discharge and oil pressure to...

    I would expect the discharge and oil pressure to be pretty close, within 1-2 psig of each other but your condenser pressure is way down, you have some sort of restriction in gas feed to the condenser...
  43. Replies
    54
    Views
    9,035

    Pump wiring Star or Delta on both pumps ? ...

    Pump wiring Star or Delta on both pumps ?


    Sent from my iPhone using Tapatalk
  44. So do you have soft stop enabled ? Sent...

    So do you have soft stop enabled ?


    Sent from my iPhone using Tapatalk
  45. Moideen, what are the run hours on your...

    Moideen, what are the run hours on your compressors ? 10 years doesn't seem too bad but what parts and why were they overhauled ?
  46. Replies
    13
    Views
    2,244

    I use a combination of Fluke 289's, Fluke 435 II,...

    I use a combination of Fluke 289's, Fluke 435 II, Fluke 190-204 4 channel scopes and an 8 channel Picoscope, it covers everything i can think of on both input and output side and can be used safely...
  47. Replies
    7
    Views
    2,413

    Why do people still have millennium panels ? I...

    Why do people still have millennium panels ? I hope all working ok now


    Sent from my iPhone using Tapatalk
  48. Replies
    7
    Views
    2,413

    Is the Optiview configured for SSS type starter ,...

    Is the Optiview configured for SSS type starter , are comms established between Optiview and SSS trigger board ? Is overload setting correct in Optiview motor display ? Do you see any data in SSS on...
  49. Replies
    7
    Views
    3,098

    It could be your economizer solenoid valve is...

    It could be your economizer solenoid valve is stuck open or energised , it should become active above 120 he and shut off below 90 hz . You should also see about 6-10 F subcoolling at condenser...
  50. Replies
    11
    Views
    2,049

    Does it have a VSD or is it SSS or remote starter...

    Does it have a VSD or is it SSS or remote starter and does it have an Optiview panel?
    Are both chilled and condenser water flows stable and is condenser/evaporator water inlet temps stable ? ...
Results 1 to 50 of 353