Nice work
The testo 300 is amazing. Check out YouTube with Steve Lav for a demo on it.
Magnets to attach to plenums and real time read outs of 6 parameters with back lit display.
Awesome piece of gear.
Thanks for the pro status tip. I’ll try to get into that.
In the field I have a red seal journeyman plumber, journeyman gas fitter, 4th class power engineer, and backflow tester certifications....
Thanks.
I did check resistance on the motor. That was my first step.
Low: 35 ohms
Med: 25 ohms
High: 10.5 ohms.
I also read the motor book you referenced.
Thanks for that tip on the voltages, pecmsg.
I’ll read the info you attached.
Also - newer to hvac. Not heating/ plumbing.
Thanks for the quick replies. Off to work ✌️ peace
I did check the capacitor. Capacitor is fine.
Hi
120 vac goes to PECO stat then down to terminal strip where connections for fan are located.
Fan spins freely with no voltage applied and...
I recently attended a service call for a blower motor that wouldn’t spin.
I’m newer to hvac calls.
the fan is 3 speed, 120 vac.
When the stat calls for fan, the fan is receiving 120 vac...
Anyone?
I’m prefacing this with: I’m getting more into HvaC with the commercial plumbing company I’m at.
I recently attended a service call for a bad blower fan. The blower fan was in a wall mounted fan...