If anyone has the 4.10 and newer modules I could use them as well. Thanks!
Type: Posts; User: ccjb100
If anyone has the 4.10 and newer modules I could use them as well. Thanks!
Which preloaded application is it specifically? Also do have the ability to edit the program in GFX if needed?
Are these already set for BACnet IP? If so it's very straightforward. You should just access as documented with serial port and null modem cable (the null modem cable is necessary). Baud rate needs...
Update....i discovered tonight that when certain system graphics are being displayed the niagara station launcher CPU spikes and stays at 100%. This matches the CPU usage in the station resource...
So the problem is back one step from what you describe. It's the out value of the SCHEDULE that isn't propagating through a link TO the in16 on on the proxy point. So on a wire sheet you would see...
Do you mind clarifying this? How is it you set a tuning policy for schedule specifically? I'm assuming you don't mean the "execution time" that keeps an exported BACnet schedule linked to a Niagara...
SO I'm having almost this exact problem and was about to make a post about it. In my case its a completely different type of system. I have a recently upgrade 4.11 windows supervisor station. It has...
I can confrim. When bringing in remote points to logic in an ACM it uses COV subscriptions in the remote devices if they support it. If no change the ACM will eventually poll the point anyway...the...
I may need to look at this more. Thanks for the idea. :cheers:
Will try to update this thread later once I get it figured out.
For these small systems no, it's just a standalone S1000 with built in graphics. There are other systems yes we do, or we can add a VM to an on site server. Can you briefly describe how you are using...
We have some small standalone controls systems out there that run Distech S1000 as the front end with embedded Envysion. I'm testing one site to establish a procedure for installing a CA signed SSL...
I know ebt 3.1 will work with Visio 2016, but I can't say for sure for ebt 2.6. I would stick with an older Visio as suggested to be sure.
Sent from my Moto G (5S) Plus using Tapatalk
I don't understand the huge benefit either. So for Distech Ecylpse they have two ports which act a switch in normal operation, simple un-managed, which I think is just fine because to have a valid...
I wont overly worry about since I did already get working by parsing out the URL. However I will bring it up with dev I talked to when we did some functional testing on it. Just to make sure its...
I would literally have a heart attack if the Cisco switches did this. :grin2: ...at least in the default configuration.
I'm pretty sure the IE-2000 will do regular old RSTP, in fact the datasheet says so! It's an awfully expensive way to get spanning tree though. I understand if you have to use the active ring manager...
So in my previous reply I noted that something is odd about the body response I get that that doesn't match the responses of other similar call on this system. All the others responses I've seen are...
So get this. I think the string response is maybe not suppsoed to look like it does, but in fact should be key value pairs for "Code" and "Message" but that's not how it comes back. Interestingly...
I found it! kitControl-StringIndexOf
Thats it...sorry to ask for work. :whistle: :D You gave me jsut enough clue. I was glossing over that function because I thought it just output a true false on...
That sounds like it might work...do you know what that function is? Is it a Vykon utility? I can't seem to peg it down.
So I'm testing the OneSightSolutions API "Driver" in Niagara to do some API calls we need for an upcoming project. The end result will be using the API calls to push alarm data into the customer work...
For me step one is always make an image of the hard drive "as is" so you always have a fall back position. I second the Macrium suggestion. If the original hard drive is IDE there are combo USB to...
Yes. This did it thank you!
I have some plain Niagara numeric writable control points that are being written to from an API call. I would like to do a linear conversion on these points in order to scale them...just like the...
So I'll tell my experience. Hopefully I'm not repeating myself in this thread before because what I'm about to say I know I've written before somewhere. :)
I will say right off the bat...I knew...
Could you post what the issue and solution was? This may assist others finding this in the future! I myself am curious what you found.
Here is an example point. This is the BitString Value for the status of a wireless pulse transmitter on one Chiller. This point comes from a BACnet gateway that communicates with the transmitters in...
Update. I found away to do this that will work...but will be tedious.
BitStringValue --> kitControl SubString (read index starting 0 to 1 will give me just the value of Bit 0) --> StatusString to...
Yes I want to break it down to individual binray bit status for alarms. See my post above, they are not numbers. It's a BACnet object Bit String Value. Haven't seen it before so I'm in the fiddling...
This was the first thing I tried. It doesn't work. So the thing is that its NOT a number, it's a literal string of 8 characters that is either 0 or 1 where each represents a certain status for the...
I've got a site with a BACnet gateway for wireless pulse transmitters and one of the points available for each transmitter is a Bit String Value which is simply an array of 8 status bits in a string...
I'm sorry to say there is no point discovery for modbus. You will have to create the points manually that you need. You will need to consult the modbus register map for the fan controllers in...
OP. Yes do this. In addition after you save it to device manager, highlight the device and use the save function in device manager to save at minimum DDC and pointdata including VAV calibration...
You can't (as far as I know) bring a network value directly into niagara. You will have to link the network value to a local bacnet value first in GFX and then bring in the linked point. That or you...
You can't (as far as I know) bring a network value directly into niagara. You will have to link the network value to a local bacnet value first in GFX and then bring in the linked point.
Appreciate the responses all. I don't think SMS is viable as this is quite a remote site, however I will look into it. I have a feeling that cell reception at this site will be femtocell that rely on...
We have a customer site that has some equipment for which cooling is very critical and currently they run an in house local email server which receives the alarms. They are moving to a cloud based...
My apologies if I was over explaining it. [emoji38] But yes, you program a BCM same as any VLC field controller. If you have done that before than it should be no problem.
Sent from my Moto G...
What do you have access to as far as front end/programming? For alerton front end that would be DDC privileges on the envision or Compass front end plus available Visio+VisualLogic installed on a...
Putting aside any questions about whether you need a JACE at all, or whether you need the IP/MSTP routers rather than bringing MSTP directly into the JACE...
Another option for the long ethernet...
Aloha Dean. I drove by this array on Friday with my coworker before I went back to Oahu! (Hawaii Energy Systems). We were just wondering what was happening with this array. In any case I just wanted...
If your wireless NAT adapter device is blocking ICMP echo requests (pings) that might also account fro the device showing down. Just a thought.
You say you have port forwarding setup from WAN to LAN right? Sounds like you have port for web interface (TCP 80 and/or 443) and SNMP (UDP 161)...is that all correct? If so and you actually have...
Had anyone setup any utility or software that can pull exchange calendar information and translate it into a banner event schedule for example?
I'm looking to grab Microsoft Teams room office365...
Good news for you and anyone else looking at this thread later. Distech has been changing there portal site and now you no longer need a login to download their documentation. You can manuals for...
I have it. Message me your email and I will send it to you.
The settings they gave you would be for piping it through a Niagra Station. However if you are just trying to direct connect you would...
Let us know what you find. I have one of these routers as well.
If your talking about the Loytec docs, I can't believe that it's misunderstanding on their part. It was quite comprehensive in regards to redundancy and network design with RSTP so I can't believe...
Aye. All the above is why we are trying are migrate towards VPN as first choice for remote access. But there are some customers who insist on public web access to BMS so it will still be an issue...
Yes I understand. But still that requires registering a domain first. I was referencing above the DDNS hostname service through noip (using *.ddns.net hostnames), without any domain registration (But...