  • 07-17-2023, 08:59 PM
    ehsx
    Heat exchangers &, piping contract & expand also….
  • 07-17-2023, 08:00 PM
    gustavhorna
    Quote Originally Posted by pecmsg View Post
    Starting at 600# and 70*
    Ending at 65*
    You’ll loose 5#’s of pressure

    It’s accurate!
    and you know what is the temperature inside of the condenser, evaporator, line set in the ground etc.... no way
  • 07-17-2023, 03:02 PM
    R600a
    Quote Originally Posted by VTP99 View Post
    There was a PT chart for that floating around here somewhere
    The link above works too.
  • 07-17-2023, 12:53 PM
    pecmsg
    Quote Originally Posted by VTP99 View Post
    There was a PT chart for that floating around here somewhere
    Ice posted it!
  • 07-17-2023, 12:49 PM
    VTP99
    There was a PT chart for that floating around here somewhere
  • 07-17-2023, 12:38 PM
    R600a
    Quote Originally Posted by pecmsg View Post
    Starting at 600# and 70*
    Ending at 65*
    You’ll loose 5#’s of pressure

    It’s accurate!
    Yep and even more accurate if you compensate for temperature.
  • 07-17-2023, 12:35 PM
    pecmsg
    Quote Originally Posted by R600a View Post
    But it definitely changes pressure.
    Starting at 600# and 70*
    Ending at 65*
    You’ll loose 5#’s of pressure

    It’s accurate!
  • 07-17-2023, 10:17 AM
    R600a
    Quote Originally Posted by VTP99 View Post
    Nitrogen is much more stable than refrigerant
    But it definitely changes pressure.
  • 07-17-2023, 10:15 AM
    VTP99
    Nitrogen is much more stable than refrigerant
  • 07-17-2023, 10:14 AM
    dschiffer
    Quote Originally Posted by gustavhorna View Post
    over 24h the climatic conditions change too much for any useful conclusion. Pressure depends on temperature. Now if your temp changed 3F, is the drop by 20 psi a leak or temperature drop? You cant even measure the temp across all lines, indoor, outdoor etc. So no, more than 15-30 mins is not useful
    I use this calculator for long pressure tests for exactly this reason.

    https://www.oceanhvac.com/nitro.php
  • 07-17-2023, 10:08 AM
    gustavhorna
    Quote Originally Posted by rider77 View Post
    Care to elaborate?
    over 24h the climatic conditions change too much for any useful conclusion. Pressure depends on temperature. Now if your temp changed 3F, is the drop by 20 psi a leak or temperature drop? You cant even measure the temp across all lines, indoor, outdoor etc. So no, more than 15-30 mins is not useful
  • 07-17-2023, 12:52 AM
    VTP99
    On Deck 👇🏻
  • 07-17-2023, 12:49 AM
    VTP99
    Before 👇🏻
  • 07-17-2023, 12:45 AM
    VTP99
    Do it all the time. I'll be doing it in the next few days on a 4 ton heat pump.
    Should I take pictures 🖼️
  • 07-17-2023, 12:26 AM
    R600a
    Quote Originally Posted by VTP99 View Post
    I'm still hung up on the 12 hours to vacuum down a 4 ton system without pulling the cores [emoji44]
    I've never seen a proper vacuum pulled with the cores in and I don't believe it exists.
  • 07-17-2023, 12:25 AM
    VTP99
    More like 12 minutes 😁
  • 07-17-2023, 12:24 AM
    VTP99
    I'm still hung up on the 12 hours to vacuum down a 4 ton system without pulling the cores 😲
  • 07-16-2023, 11:10 PM
    rider77
    Quote Originally Posted by gustavhorna View Post
    nonsense
    Care to elaborate?
  • 07-16-2023, 10:53 PM
    gustavhorna
    Quote Originally Posted by shaggs2broke View Post
    I think I have pinpointed my problem, the vacuum gage I purchased new appears to be defective. I suspected it after my overnight 620psi pressure test with no drop. i felt I should be able to hold vacuum with same setup but vacuum gage in place of pressure gage but couldn't say for sure until I used another vacuum gage. I pulled down to 20 microns and held it under 500 microns through 3 feet of 1/4" tubing for over an hour. As soon as I added my other vacuum gage and tried again it wouldn't hold at all. Damn CPS and their vacuum gages!
    There is such type of leak that leaks only in one direction. Holds pressure but leaks under vacuum (or vice versa). It's real
  • 07-16-2023, 10:48 PM
    gustavhorna
    Quote Originally Posted by rider77 View Post
    Your pressure test is insufficient. Many manufactures call for over 500 PSI for as much as 24 hours.
    nonsense