Utica High Efficiency boiler "flutters" when gas is applied during ignition cycle.

7.8K views 15 replies 8 participants last post by  ebierley  
#1 ·
Utica High Efficiency boiler "flutters" when gas is applied during ignition cycle.

I have a Utica High Efficiency boiler that flutters (sometimes softly, sometimes hard) when gas is applied during the ignition cycle. This fluttering sometimes interrupts the cycle causing it to purge and try again. If it fails three times in a row, the system goes into lockout and requires manual restart (valve indicator on control board flashes).

Does anyone have any recommendations as to what the possible cause of this is? Utica tech support said to check CO2 levels with a combustion analyzer but one is not available. They also said that supply gas pressure needs to be minimum of 4 in W.C. while firing and we are only getting 3.5 in W.C. Could this be the problem?

Any recommendations would be greatly appreciated.
 
#4 ·
It is a series Q90-200, model UB90-200, serial 350500221. A little history on the system: When my boss took over this system it was installed in an apartment complex controlling 15 zones. It was determined (by an engineer) that the system was incorrectly piped (did not have a bypass loop). The engineer told the property owner that the incorrect pipping may have damaged the system. The system has "fluttered" ever since my boss took it over but seemed to get worse after cleaning the burn chamber this fall. Per the recommendation of the Utica Tech Support person, I re-cleaned the burn chamber and that improved the fluttering slightly but not completely. When the combustion intake is removed the fluttering stops. There seems to be a back pressure created at the moment of combustion that causes the pressure switch to flutter which in turn causes the gas valve to flutter. Also, the carbon monoxide reading at the outside exhaust is 4000ppm. That is as high as my reader goes so it may be higher.

Any recommendations or assistance would be greatly appreciated.
 
#7 ·
hook up a combustion analyzer to the boiler. 4000ppm is way to high and should be corrected to fire under 400ppm. if over 400ppm ANSI standards is to red tag and disable boiler.

could be your venting length, venting size, incorrect venting, etc.....

combustion analyzer should tell you your problems.
 
#8 ·
I have worked on many q90-100 and they had a burner change that resolved ignition rumbling noise.. I will see if I can find the bulletin. I had one last year that I got involved in,,, replace the burner and it was like night and day.. Check your inlet screen (sandwiched in the Fernco)
 
#16 ·
Do the pressure switch hoses have an orifice in them close to the barbed fittings? I had one doing what you described and the orifices fixed it.


Sent from my iPad using Tapatalk
 