working on a carrier gas pack model 48ss-024060301 ,board is flashing 6 flashes. does anyone have the carrier codes for this, thanks
Reply With Quote
  #2  
Old 12-12-2005, 09:45 PM
Lusker's Avatar
Lusker Lusker is offline
Professional Member
 
Join Date: May 2004
Posts: 7,805
Table 7 — LED Indications
ERROR CODE LED INDICATION
Normal Operation On
Hardware Failure Off
Fan On/Off Delay Modified 1 Flash
Limit Switch Fault 2 Flashes
Flame Sense Fault 3 Flashes
Four Consecutive Limit Switch Faults 4 Flashes
Ignition Lockout Fault 5 Flashes
Induced-Draft Motor Fault 6 Flashes
Rollout Switch Fault 7 Flashes
Internal Control Fault 8 Flashes

http://www.xpedio.carrier.com/idc/gr...ss,sx-12si.pdf


If the motor is running, it may be the hall effect sensor
  #3  
Old 12-12-2005, 09:50 PM
smileyman smileyman is offline
Professional Member
 
Join Date: Nov 2003
Location: north carolina
Posts: 41
thanks
Reply With Quote
  #4  
Old 12-12-2005, 10:02 PM
djken djken is offline
Regular Member
 
Join Date: Nov 2004
Posts: 238
Perform the following to check Hall Effect Senser,

With the three-wire plug unplugged:
With power applied to the unit, unplug the three-wire plug and measure the pins as follows:
1. Connect the negative or black lead of the meter to pin three on the circuit board.
2. Connect the positive or red lead of the meter to pin one.
3. The meter should read between 7.5 and 10 volts DC.
4. Move the red or positive lead to pin two. It should read between 21 and 24 volts DC.
5. Replace the circuit board if these pins are outside these readings.

With the three-wire plug plugged in:
With power applied to the unit and the three-wire plug in place, measure the pins as follows:
1. Connect the negative or black lead of the voltmeter to pin three on the circuit board.
2. Connect the positive or red lead of the voltmeter to pin one.
3. Slowly rotate the induced draft motor. On half of one rotation of the induced draft motor shaft the voltage reading should be less than 1 volt DC. On the other half of one rotation the voltage reading should be between 6.5 and 9 volts DC.
4. If the voltage reading is not less than 1 volt DC on half of the rotation of the motor shaft and not between 6.5 volts and 9 volts DC of the other half of the shaft rotation, replace the Hall Effect Switch.
5. Move the red or positive lead to pin two. It should read between 16.5 and 21 volts. If not, replace the Hall Effect Switch
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Sponsors


» Sponsors





All times are GMT -4. The time now is 03:32 PM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
HVAC-Talk is proudly provided by:
Contracting Business MagazineAd Management by RedTyger

© 2010 Penton Media, Inc.