Trane RTU pluged orifice

We have 20 of these RTUs, alot with the same isues pluged orifice, what is the best way of cleaning, some of these units have bad compressors in them so system will be opened up to change out comp.
M: TCD301K40ACA
Reply With Quote
  #2  
Old 07-30-2010, 11:58 AM
Painful Chafe Painful Chafe is offline
Regular Member
 
Join Date: Jul 2010
Posts: 25
Are these the ones with several orifices pinched into the lines on the header on the evaporator coil.?One orifice for each circuit in the evaporator. Or is it just one?
Reply With Quote
  #3  
Old 07-30-2010, 01:46 PM
jtricor's Avatar
jtricor jtricor is offline
Professional Member
 
Join Date: Mar 2004
Location: Janesville WI
Posts: 402
yes they are
Reply With Quote
  #4  
Old 07-30-2010, 01:49 PM
jtricor's Avatar
jtricor jtricor is offline
Professional Member
 
Join Date: Mar 2004
Location: Janesville WI
Posts: 402
Its a header system there must be 6-10 of these orifices in there
Reply With Quote
  #5  
Old 07-30-2010, 04:44 PM
Painful Chafe Painful Chafe is offline
Regular Member
 
Join Date: Jul 2010
Posts: 25
I have seen this caused by a filter drier core coming apart. Also, excesive moisture can cause it, but it would need to be a lot of moisture. You can try to blow the evap out backwards. I would cut into the liquid and the suction pipe just before the headers going into the evap to get as much nitrogen flowing through the evap as possible. Blast it out with 300psi of nitrogen. Then toss a half a can of Rx11 in it(get the kit if you don't have one) and blast it out with nitrogen again. Hold a clean rag an inch or so away at the liquid line that you cut and see if you get anything out. Unfortunately if you get pieces of drier core out its almost impossible to get it all out. You may be looking at new evaporator coils on all of them. Experiment with one first and see what you get. Let me know what you find. I'm a bit curious.
Reply With Quote
  #6  
Old 07-30-2010, 04:51 PM
yellowirenut's Avatar
yellowirenut yellowirenut is offline
Professional Member
 
Join Date: Jan 2009
Location: Indiana
Posts: 2,166
replacing that orifice manifold sucks....plane and simple it sucks. Expect it to take most of a day, plus a half hour of crying over your lunch.
Reply With Quote
  #7  
Old 07-30-2010, 05:02 PM
lynn comstock lynn comstock is offline
Professional Member
 
Join Date: Jul 2002
Location: Yuma, AZ
Posts: 585
The suggestion of Post #5 (Painful Chafe) may work. Since you have multiple units with this problem, I would learn as much as possible before doing any remedial work.
  1. Recover the gas
  2. Test for acid
  3. Remove the drier, cut it open and examine it
  4. Remove any problem orifices and examine them to see the actual obstruction
  5. Depending on what I saw as an obstruction I would plan a remedy for the problem.
  6. The remedy would include a new HH Sporlan drier and a liquid line shutoff ball valve ahead of the drier.
  7. The remedy would probably include a suction line drier.

Never forget to make a profit. If you can't...Walk away.
__________________
Help us help you...We need DATA, not opinions
  1. Job city
  2. Refrigerant
  3. Type of metering device
  4. Outdoor ambient entering condenser
  5. Outdoor condenser leaving air temperature
  6. Return air wet bulb temperature
  7. Return air temperature at AH
  8. Supply air temperature at AH
  9. Head (high side) pressure
  10. Liquid line temperature
  11. Back (low side) pressure
  12. Suction line temperature
  13. External Static Pressure to the fan bearing unit of a ducted system.
Reply With Quote
  #8  
Old 07-30-2010, 05:40 PM
BergerMech Rob BergerMech Rob is offline
Professional Member
 
Join Date: Mar 2007
Posts: 1,229
Clean the coils.

Fix the leaks.

Don't go back with the short orifice assembly, instead, go with the TXV upgrade.
__________________
The toes you step on today may be connected to the *** you have to kiss tomorrow
Reply With Quote
  #9  
Old 07-30-2010, 07:21 PM
bdclark's Avatar
bdclark bdclark is offline
Professional Member
 
Join Date: Sep 2006
Location: Tennessee
Posts: 372
Have you performed any superheat tests on these units? I would bet that your headers have been freezing up. Are there any crankcase heaters installed? Jumping off of a cliff here, but I think you might find somewhere in the ballpark of 25º-30º of superheat on a hot day, and the answer you are looking for is thermal expansion valves. I don't know everything about these Voyagers, although I do work for Trane and have done a boatload of factory warranty work on them. I could be wrong, but the nameplate on these units will tell the tale. Manufactured dates between 1996 and 2002 would suggest that I may just be correct. Just my two cents.

You may also want to consider replacing the LL driers with 30 cu. in. driers and adding 1.5 lbs of refrigerant to each circuit.
__________________
UA LOCAL 614...WE DO IT RIGHT THE FIRST TIME

Always remember, those who hate you don't win, unless you hate them. And then, you destroy yourself. -Richard Nixon-
Reply With Quote
  #10  
Old 07-30-2010, 10:32 PM
Painful Chafe Painful Chafe is offline
Regular Member
 
Join Date: Jul 2010
Posts: 25
Quote:
Originally Posted by bdclark View Post
Have you performed any superheat tests on these units? I would bet that your headers have been freezing up. Are there any crankcase heaters installed? Jumping off of a cliff here, but I think you might find somewhere in the ballpark of 25º-30º of superheat on a hot day, and the answer you are looking for is thermal expansion valves. I don't know everything about these Voyagers, although I do work for Trane and have done a boatload of factory warranty work on them. I could be wrong, but the nameplate on these units will tell the tale. Manufactured dates between 1996 and 2002 would suggest that I may just be correct. Just my two cents.

You may also want to consider replacing the LL driers with 30 cu. in. driers and adding 1.5 lbs of refrigerant to each circuit.
Are you saying to install a TEV instead of the orifices. I'm not sure how you would remove the orifices. They are crimped in the line. Maybe someone knows if there is some type of conversion kit. New manifold(which would be pretty difficult to put it, I imagine) and a TEV. I've done Trane orifice to TEV conversion but never on the crimped in multiple orifice coils.
Reply With Quote
  #11  
Old 07-30-2010, 11:19 PM
FLTUDITECH FLTUDITECH is offline
Regular Member
 
Join Date: Apr 2010
Location: Tampa, FL
Posts: 5
I just repaired a 10 ton Carrier with the same setup. Orifices are pinched in line with the evaporator and were plugged and freezing up. The local Johnstone branch had a fix that worked great. It entailed cutting off the entire manifold and brazing in a distributor assembly that they have. They mix and match 4,6,7 and 8 tube distributors and orifices to match the tonnage of the unit. Today was the first time I installed one and it worked great and the unit set up perfectly. Drop me a line and Ill see if I can send you some pictures. Haven't been on here in a while and forgot how to post.

Steve
Reply With Quote
  #12  
Old 07-31-2010, 04:10 AM
Painful Chafe Painful Chafe is offline
Regular Member
 
Join Date: Jul 2010
Posts: 25
Quote:
Originally Posted by FLTUDITECH View Post
I just repaired a 10 ton Carrier with the same setup. Orifices are pinched in line with the evaporator and were plugged and freezing up. The local Johnstone branch had a fix that worked great. It entailed cutting off the entire manifold and brazing in a distributor assembly that they have. They mix and match 4,6,7 and 8 tube distributors and orifices to match the tonnage of the unit. Today was the first time I installed one and it worked great and the unit set up perfectly. Drop me a line and Ill see if I can send you some pictures. Haven't been on here in a while and forgot how to post.

Steve
Interesting. I'm trying to imagine what it looks like. Does it look like what you cut out and match right up? Pictures would be great if you are going to be at the job again. You can just upload pictures at a site like photobucket.com and post the "img code" here.
Reply With Quote
  #13  
Old 07-31-2010, 08:49 AM
FLTUDITECH FLTUDITECH is offline
Regular Member
 
Join Date: Apr 2010
Location: Tampa, FL
Posts: 5
I have pictures but they didnt turn out the best. Try to picture that entire header gone. Basically I cut off the entire header just after the orifice with a pair of side cutters. Then opened the cut pipe just enough so that I could slide my capillary tube in and then pinched it back down. Then you just pipe into the distribution tube with your liquid line.
Attached Thumbnails
Click image for larger version

Name:	IMG00081-20100730-1318.jpg
Views:	81
Size:	36.2 KB
ID:	113852   Click image for larger version

Name:	IMG00080-20100730-1318.jpg
Views:	68
Size:	36.2 KB
ID:	113862  
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Sponsors


» Sponsors





All times are GMT -4. The time now is 03:41 PM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
HVAC-Talk is proudly provided by:
Contracting Business MagazineAd Management by RedTyger

© 2010 Penton Media, Inc.