  #1  
Old 07-28-2010, 06:59 AM
khc95 khc95 is offline
Regular Member
 
Join Date: Jul 2010
Posts: 49
Poor Humidity Removal

Other than fan speed and sizing of unit is there any other factors to affect moisture removal. Unit has no problem cooling conditioned space, but temerature needs to be cranked down low to acheive a "comfortable" humidity. Cooling is supplied via a roof top, all ductwork in the conditioned space. Unit has run now for three years without this issue and nothing has changed within the envolope that I am aware of. What am I missing.
Thanks
Reply With Quote
  #2  
Old 07-28-2010, 07:01 AM
beenthere beenthere is offline
Moderator
 
Join Date: Jan 2004
Location: Lancaster PA
Posts: 48,384
May need a clean and tune.
__________________
How many times must one fix something before it is fixed?

The toes you step on today, may be attached to the butt you kiss tomorrow.
Reply With Quote
  #3  
Old 07-28-2010, 08:44 AM
teddy bear's Avatar
teddy bear teddy bear is offline
Professional Member
 
Join Date: Jun 2003
Location: Madison, WI/Cape Coral, FL
Posts: 3,552
Quote:
Originally Posted by khc95 View Post
Other than fan speed and sizing of unit is there any other factors to affect moisture removal. Unit has no problem cooling conditioned space, but temerature needs to be cranked down low to acheive a "comfortable" humidity. Cooling is supplied via a roof top, all ductwork in the conditioned space. Unit has run now for three years without this issue and nothing has changed within the envolope that I am aware of. What am I missing.
Thanks
Tha amount of fresh air entering the building, the outdoor dew point of the fresh air, and the number of occupants/activities are other issues. Don't forget the why the a/c is function-refrigerant charge and settings.
Regards TB
__________________
Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
Use +Merv 10 air filter. -Don't forget the "Golden Rule"
Reply With Quote
  #4  
Old 07-28-2010, 08:54 AM
Airmechanical's Avatar
Airmechanical Airmechanical is offline
Professional Member
 
Join Date: Dec 2006
Location: Middle Tennessee
Posts: 9,934
*

Quote:
Originally Posted by teddy bear View Post
Tha amount of fresh air entering the building, the outdoor dew point of the fresh air, and the number of occupants/activities are other issues. Don't forget the why the a/c is function-refrigerant charge and settings.
Regards TB
Teddy are you implying he does not need a dehumidifier

i am very proud of you

we love ya man



.
__________________
do it right or don't do it at all
Reply With Quote
  #5  
Old 07-28-2010, 02:35 PM
teddy bear's Avatar
teddy bear teddy bear is offline
Professional Member
 
Join Date: Jun 2003
Location: Madison, WI/Cape Coral, FL
Posts: 3,552
Quote:
Originally Posted by Airmechanical View Post
Teddy are you implying he does not need a dehumidifier

i am very proud of you

we love ya man
.
Not so fast. khc95 did not ask if he needed a dehumidifier, only the factors effecting humidity levels. In the final senirio, he will need a dehumidifier to maintain <50%RH during low/no cooling load conditions.

The amount of dehumidification depends on all of the above. When the outside dew point is above the inside desired dew point, an properly set-up a/c with a considerable cooling with maintain reasonable humidity levels. But as the cooling load subsides during the shoulder season, the %RH will rise to the point where a dehumidifier in need to maintain low humidity.
I get worried when you guys think I a reasonable guy.
Regards TB
__________________
Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
Use +Merv 10 air filter. -Don't forget the "Golden Rule"
Reply With Quote
  #6  
Old 07-28-2010, 09:09 PM
khc95 khc95 is offline
Regular Member
 
Join Date: Jul 2010
Posts: 49
Confused

The amount of dehumidification depends on all of the above. When the outside dew point is above the inside desired dew point, an properly set-up a/c with a considerable cooling with maintain reasonable humidity levels. But as the cooling load subsides during the shoulder season, the %RH will rise to the point where a dehumidifier in need to maintain low humidity.

I could see that but this is in the middle of the summer with 95 to 100 temperatures. Evap and filters are clean with an 18 degree temperature drop ?
Reply With Quote
  #7  
Old 07-29-2010, 09:21 AM
teddy bear's Avatar
teddy bear teddy bear is offline
Professional Member
 
Join Date: Jun 2003
Location: Madison, WI/Cape Coral, FL
Posts: 3,552
Quote:
Originally Posted by khc95 View Post
The amount of dehumidification depends on all of the above. When the outside dew point is above the inside desired dew point, an properly set-up a/c with a considerable cooling with maintain reasonable humidity levels. But as the cooling load subsides during the shoulder season, the %RH will rise to the point where a dehumidifier in need to maintain low humidity.

I could see that but this is in the middle of the summer with 95 to 100 temperatures. Evap and filters are clean with an 18 degree temperature drop ?
It is very clear, if you want to lower %RH by 10%, lower the indoor dew point by 3^F, by lowering the coil temperature by 3^F. This will give you 21^F drop. This will work as long as the a/c operates enough to remove enough moisture. On cool damp days when the a/c operates less, the indoor %RH rises above the dehumidistats set point, dehumidifier will remove the excess moisture without overcooling the space. Slick!
Or if you are an a/c guy, you keep lowering the coil temp until the ducts sweat of the coil freezes. The last thing you want to do is add a lowely dehumidifier. It shows you are not a man!
Regards TB
PS All dehus are created equal. Some use <50% of the energy and last 2X as long.
__________________
Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
Use +Merv 10 air filter. -Don't forget the "Golden Rule"
Reply With Quote
  #8  
Old 07-29-2010, 06:33 PM
khc95 khc95 is offline
Regular Member
 
Join Date: Jul 2010
Posts: 49
Hey Teddy

I can appreciate what your saying but as for the last three years the rooftop has done the job on it's own and now suddenly for no apparant reason it is not. I am going to slow the fan down to increase moisture removal, but I am must be missing the real issue that caused this to happen. Input has been appreciated.
Reply With Quote
  #9  
Old 07-29-2010, 06:57 PM
Kevin O'Neill's Avatar
Kevin O'Neill Kevin O'Neill is offline
Professional Member
 
Join Date: Mar 2007
Location: Myrtle Beach, SC
Posts: 2,085
1. Outdoor humidity is especially high this year.

2. If you can drop the indoor temperature to 70 degrees to control humidity, likely the unit is oversized.

3. Measure air flow. Use a hood. Or use static pressure and blower charts. Or use an annemometer and do a traverse. But measure air flow, don't guess. Should be 350 to 400 CFM per ton.

4. Have your tech clean the indoor coil.

5. Have your tech check refrigerant levels with super heat and sub cool, not just pressures.

6. Make sure you do not have outside air dampers stuck open.

7. Install a ducted dehumidifier.

It could be other things, but I would start there. What is the building used for? That could give us clues.
__________________
Remember, Air Conditioning begins with AIR.
Reply With Quote
  #10  
Old 07-29-2010, 07:00 PM
martyinlincoln martyinlincoln is offline
Regular Member
 
Join Date: Jul 2010
Location: nebraska
Posts: 90
I've seen txv's fail to maintain a good superheat and not dehumidify well. Matter of fact had to replace mine two days ago because the humidity was running 65-68% with a 73 degree setpoint. Superheat went from 27 to 12 and the condensation flowed like a faucet. No idea if your rooftop has one or not but the tech will figure it out quick enough.
Reply With Quote
  #11  
Old 07-29-2010, 07:06 PM
Kevin O'Neill's Avatar
Kevin O'Neill Kevin O'Neill is offline
Professional Member
 
Join Date: Mar 2007
Location: Myrtle Beach, SC
Posts: 2,085
Quote:
Originally Posted by martyinlincoln View Post
I've seen txv's fail to maintain a good superheat and not dehumidify well. Matter of fact had to replace mine two days ago because the humidity was running 65-68% with a 73 degree setpoint. Superheat went from 27 to 12 and the condensation flowed like a faucet. No idea if your rooftop has one or not but the tech will should figure it out quick enough.
Unfortunately, not all techs are good enough. But a good tech will find that problem.
__________________
Remember, Air Conditioning begins with AIR.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Sponsors


» Sponsors





All times are GMT -4. The time now is 03:40 PM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
HVAC-Talk is proudly provided by:
Contracting Business MagazineAd Management by RedTyger

© 2010 Penton Media, Inc.