Siemens AZL Modbus?

Has anyone had any luck pulling the modbus points out of the AZL controller connected to a LMV linkageless burner control system?
Reply With Quote
  #2  
Old 01-21-2010, 08:22 AM
ntech64 ntech64 is offline
Professional Member
 
Join Date: Mar 2008
Location: Concord, NH
Posts: 114
Do you have the correct point map but the communication is not successful? ...or are you looking for the point map/documentation? (see attachment)
Attached Files
File Type: pdf AZL52.pdf (185.8 KB, 19 views)
Reply With Quote
  #3  
Old 01-21-2010, 09:20 AM
noskilltech noskilltech is offline
Regular Member
 
Join Date: Mar 2007
Posts: 75
I have the documentation. Tried connecting directly from my serial port to the controller via RS-232 with a flat 8 wire cable that had RJ-45 plugs on the ends and a RJ-45-DB-9 connector using pins 1,3,4 to pins 2,3,5 on the 9 pin then reading the port directly with modscanner, but no luck acquiring data.

All the configurations in the AZL were set up for modbus. Slave address, parity, BAS on, etc. all set the way the documentation suggested, but I could not acquire data.
Reply With Quote
  #4  
Old 03-04-2010, 03:07 PM
rgonza rgonza is offline
New Member
 
Join Date: Mar 2010
Posts: 2
Hi, we have the situation, we follow the complete instruction according to azl manual but no luck to poll data from azl.
Thanks
Rgonza
Quote:
Originally Posted by noskilltech View Post
I have the documentation. Tried connecting directly from my serial port to the controller via RS-232 with a flat 8 wire cable that had RJ-45 plugs on the ends and a RJ-45-DB-9 connector using pins 1,3,4 to pins 2,3,5 on the 9 pin then reading the port directly with modscanner, but no luck acquiring data.

All the configurations in the AZL were set up for modbus. Slave address, parity, BAS on, etc. all set the way the documentation suggested, but I could not acquire data.
Reply With Quote
  #5  
Old 03-04-2010, 03:58 PM
noskilltech noskilltech is offline
Regular Member
 
Join Date: Mar 2007
Posts: 75
Are you converting to lon or bacnet? Or just trying to read the modbus points.

My first problem I had with the project was that I found out that it is pretty much written in stone that RS-232 cannot be in a wire run more than 10 feet. Also if you have too much data per pollgroup, you will run into issues with communication errors. And if you convert to RS-485, no matter how short the run is, you will most likely have communication errors if you don't use end resistors.

My project is working now, but I will try my best in the future to avoid modbus if at all possible.
Reply With Quote
  #6  
Old 03-04-2010, 08:15 PM
rgonza rgonza is offline
New Member
 
Join Date: Mar 2010
Posts: 2
hi, i just trying to read it from rs232 modbus, how you do for got data from azl using modbus 232? we using modbus scanner.

thanks
rob
Quote:
Originally Posted by noskilltech View Post
Are you converting to lon or bacnet? Or just trying to read the modbus points.

My first problem I had with the project was that I found out that it is pretty much written in stone that RS-232 cannot be in a wire run more than 10 feet. Also if you have too much data per pollgroup, you will run into issues with communication errors. And if you convert to RS-485, no matter how short the run is, you will most likely have communication errors if you don't use end resistors.

My project is working now, but I will try my best in the future to avoid modbus if at all possible.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Sponsors


» Sponsors





All times are GMT -4. The time now is 03:38 PM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
HVAC-Talk is proudly provided by:
Contracting Business MagazineAd Management by RedTyger

© 2010 Penton Media, Inc.