    I bet the OP is wondering when the hell someone will give him some advise lol

  2. #42
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Here's the wiring diagram for the Carrier/Bryant/Payne furnaces I've been seeing:Name:  bryant wiring diagram.jpg
Views: 13133
Size:  61.2 KB

    Notice that the Limits switches are in series with the R terminal on the board. It would be interesting to know how many are done this way vs. just killing power to the gas valve.

  3. #43
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Quote Originally Posted by Joehvac25 View Post
    I bet the OP is wondering when the hell someone will give him some advise lol
    Agreed, this thread has run away and has become more "tech to tech" than AOP. Maybe a mod could split them up for us?

  4. #44
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Thread Starter
    Quote Originally Posted by 54regcab View Post
    I'm glad to see the hydronic coils are becoming more popular, and you are promoting them. Have you done any systems that use multiple air handlers? On your setup will the water heater be doing your domestic hot water also?
    I thought I made it clear that hydronic coils have been used for quite a long time now. There is nothing new about hydronic coils or hydronic air handlers, they were available over 40 years ago when I started in the HVAC industry.

    My tankless water heater will be taking care of my domestic water heating as well as auxilliary heating for my heat pump and spot floor heating for my bathrooms and kitchen area. In most cases when I have installed systems for new houses being built where natural gas was not available, I would install an oil or LP water heater for domestic hot water and to supply hot water coils for auxilliary heating for heat pumps. Did that for decades.
    Training is important!
    Practical Training is a must!

  5. #45
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Thread Starter
    Quote Originally Posted by 54regcab View Post
    I would have like to have one of those furnaces for my own 1600sqft house. 50k isn't just for small houses, it can serve over 2,000sqft IF it's insulated right. Ask any of the building science guys about this one. Gas around here is cheap (less than 50 cents per therm), so anything over 80% doesn't have a reasonable payback time. The variable speed feature is mostly for comfort reasons, even though the payback time on that is long.

    In a daily basis I work with the Smarthours project. We install the Smarthours thermostats and run service calls when the customers call in if it doesn't work correctly. We don't repair the HVAC units or install new ones as part of this project, we just determine if the problem is with the thermostat or HVAC unit. As part of the project we see the good, bad, and the ugly as far as installs go. Some installs are excellent, others are so bad we don't even do the thermostat install for liability reasons. Most are in-between.

    Since our thermostats are system powered they go blank when a furnace shuts off on high limit, and then we get a service call. People are quick to blame our thermostat because the old battery power stat it replaced just let the furnace cycle on high limit and the customer didn't know the burners were switching off because warm air continued to come out of the vents and the thermostat "stayed on". Since the furnace is often oversized to begin with the house still stayed warm even though the burners were shut off on high limit 1/2 the time. After seeing a bunch of these through the winter it does give me prejudice to the combination over-sizing of furnaces and poor ductwork design.
    So, basically, your entire perspective of the HVAC industry comes from the standpoint of how HVAC systems affect some setback thermostat that the company you work for sells. Not exactly a very biased view of the HVAC industry.

    The only reason I keep asking you questions is that so many of your posts have very erroneous information about the HVAC industry, as well as about furnace sizing in them. If you are only seeing the HVAC industry from the perspective of a singular control that any HO can buy from any big box store or off of the internet, you really don't have a very accurate view of the HVAC industry at all.
    Training is important!
    Practical Training is a must!

  6. #46
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Thread Starter
    Quote Originally Posted by Joehvac25 View Post
    I bet the OP is wondering when the hell someone will give him some advise lol
    Plenty of advice has been given to the OP and the OP has already stated their appreciation for the advice that was given. Just exactly what have you contributed to this conversation?
    Training is important!
    Practical Training is a must!

  7. #47
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Thread Starter
    Quote Originally Posted by 54regcab View Post
    Here's the wiring diagram for the Carrier/Bryant/Payne furnaces I've been seeing:Name:  bryant wiring diagram.jpg
Views: 13133
Size:  61.2 KB

    Notice that the Limits switches are in series with the R terminal on the board. It would be interesting to know how many are done this way vs. just killing power to the gas valve.
    Once again, you show your ignorance of how furnaces work. Aside from the other safety features that come into play when the high limit switch is activated, just what else do you propose should be done?
    Training is important!
    Practical Training is a must!

  8. #48
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    Quote Originally Posted by RoBoTeq View Post
    Plenty of advice has been given to the OP and the OP has already stated their appreciation for the advice that was given. Just exactly what have you contributed to this conversation?
    I haven't contributed anything, I just sat back and read 3 pages of bickering back and forth with intermittent information being passed around. I think the OP was wondering about which furnace he should buy or how to pick a contractor, not about how a limit string works and whatever else.
    In my opinion I would tell the OP to research company's rather than brands, find someone who will do the job right.
    I'm not saying your input was faulted I was enjoying the debate myself.

  9. #49
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Quote Originally Posted by RoBoTeq View Post
    I thought I made it clear that hydronic coils have been used for quite a long time now. There is nothing new about hydronic coils or hydronic air handlers, they were available over 40 years ago when I started in the HVAC industry.

    My tankless water heater will be taking care of my domestic water heating as well as auxilliary heating for my heat pump and spot floor heating for my bathrooms and kitchen area. In most cases when I have installed systems for new houses being built where natural gas was not available, I would install an oil or LP water heater for domestic hot water and to supply hot water coils for auxilliary heating for heat pumps. Did that for decades.
    Never said that is was new, just becoming more popular. Only have seen a handful of them around here.

  10. #50
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Quote Originally Posted by RoBoTeq View Post
    Once again, you show your ignorance of how furnaces work. Aside from the other safety features that come into play when the high limit switch is activated, just what else do you propose should be done?
    I was just trying to explain what I've been running into in the field. The fix to the high limit cutoff issue lies to resolving why the furnace is overheating to begin with. The limit itself is just a safety device.

  11. #51
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Thread Starter
    Quote Originally Posted by 54regcab View Post
    I was just trying to explain what I've been running into in the field. The fix to the high limit cutoff issue lies to resolving why the furnace is overheating to begin with. The limit itself is just a safety device.
    You continue to change the intent of your accusational posts and continue to avoid answering specific questions.

    What exactly is it you are complaining about with the way the HVAC industry deals with furnaces when they reach their temperature limits?

    What is it about furnaces that has you running around the internet, especially on DIY sites, complaining about the HVAC industry? There are ways to install less heat in any system, so why are you complaining that specific furnaces are not manufactured in lower capacities?
    Training is important!
    Practical Training is a must!

  12. #52
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Thread Starter
    Quote Originally Posted by 54regcab View Post
    I was just trying to explain what I've been running into in the field. The fix to the high limit cutoff issue lies to resolving why the furnace is overheating to begin with. The limit itself is just a safety device.
    You are giving advice on and making comments on things you evidentely do not fully understand. That sort of thing may be ok on the DIY sites you are on, but that sort of thing is not acceptable on a site where there are so many professionals in the HVAC industry who have to correct your misinformation.

    When a furnace overheats, several things happen, depending on the model of the furnace. At the very least, more than just shutting off the gas valve occurs.

    It doesn't matter what type of thermostat is installed on any furnace dependent on the thermostat to initiate furnace operation. All any such thermostat is is an on/off switch that is thermally controlled.
    Training is important!
    Practical Training is a must!

  13. #53
    Join Date
    Feb 2010
    Location
    Calgary, Alberta
    Posts
    1,679
    Post Likes
    Quote Originally Posted by RoBoTeq View Post
    You are giving advice on and making comments on things you evidentely do not fully understand. That sort of thing may be ok on the DIY sites you are on, but that sort of thing is not acceptable on a site where there are so many professionals in the HVAC industry who have to correct your misinformation.

    When a furnace overheats, several things happen, depending on the model of the furnace. At the very least, more than just shutting off the gas valve occurs.

    It doesn't matter what type of thermostat is installed on any furnace dependent on the thermostat to initiate furnace operation. All any such thermostat is is an on/off switch that is thermally controlled.
    We all stand in awe of your superior intellect.

  14. #54
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    RoBoTeq it doesn't really matter how I answer your questions, you have personal issues with being 100% right 100% of the time. Even in the 10 + 13 = 8 SEER, 2nd Amendment, and Abortion discussions you're the same way. Quick to attack anybody who doesn't 100% agree with you, then go insulting them. Even when somebody DOES agree with you, you still find something to insult them about. Great professionalism shown there, you must be a real pleasure to work with...

    Oddly I agree with a lot of your posts on Social & Government issues..

  15. #55
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Thread Starter
    Quote Originally Posted by syndicated View Post
    We all stand in awe of your superior intellect.
    As well you should....
    Training is important!
    Practical Training is a must!

  16. #56
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Thread Starter
    Quote Originally Posted by 54regcab View Post
    RoBoTeq it doesn't really matter how I answer your questions, you have personal issues with being 100% right 100% of the time. Even in the 10 + 13 = 8 SEER, 2nd Amendment, and Abortion discussions you're the same way. Quick to attack anybody who doesn't 100% agree with you, then go insulting them. Even when somebody DOES agree with you, you still find something to insult them about. Great professionalism shown there, you must be a real pleasure to work with...

    Oddly I agree with a lot of your posts on Social & Government issues..
    So now you're a professional analyst, too?

    I only have issues with those who make commentaries that are wrong about HVAC issues, and you do just that....a lot. The information that you post is never supported by any facts, just your rantings that HVAC professionals don't know how to install proper sized furnaces....blah, blah..

    You have refused to respond to several specific questions I have posed to you to support comments you have made. I realize that you don't respond because you don't understand what you are posting about, yet you continue to make erroneous posts. Why are you trying to impress those of us who are professionals in the HVAC industry? Isn't it bad enough that you are giving DIYers irresponsible information on DIY sites?

    Don't get me wrong, I'd love to banter with you about thermostat controls, the only thing you seem to really be involved with in the HVAC industry. But please, stop making erroneous posts about furnace oversizing and furnace internal controls. You really do not understand what you are posting about.
    Training is important!
    Practical Training is a must!

  17. #57
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    What other DIY sites are you talking about that I'm supposedly insulting the HVAC profession? Please let me know what they hell is going on, because I have no idea what you are talking about.

    When I supported the power being disconnected from the thermostat by posting a schematic, you insult me without giving any explanation of why the schematic wasn't relevant. Do you not believe that any furnaces disconnect the power to the thermostat when they reach high limit?

  18. #58
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by 54regcab View Post
    .Do you not believe that any furnaces disconnect the power to the thermostat when they reach high limit?
    There were a lot of your earlier model furnaces prior to the 90's, that were the old draft box/hood style that the high limit did "depending on the fan limit" shut the high power leg to the furnace, but most were wired to open the low voltage. I have not really looked at the schematic you posted, but with 99.99% of all the newer furnaces, if the power were taken out with a open high limit, how would we be able to read the trouble codes when the tech arrived? I will say this. I have yet to run across any newer furnace that, unless the breaker was tripped, or maybe a bad low voltage transformer or door switch, that the board was not still active in the circuit upon arrival. I can't get into it on this forum, but trust me if your stat only needs 24v to keep it active, I could personally wire it using the same furnace transformer, to were unless the low voltage transformer was fried, it would stay powered regardless of the limits or the board being out.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  19. #59
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    MrBill, the 24V is cut to the board terminals going to the thermostat but not the boards internal CPU. The error codes work, even though there is no 24V going to the thermostat. Look close at the schematic, it's a thin "wire" from the 24V to the CPU before sending the 24V to the limit controls.

    We could wire straight to the transformer to keep 24V at all times, but won't do so. If the furnace is hitting high limit they need to call their HVAC company and have them correct what's causing the problem. We'll check the air filters to see if they are dirty or the highly restrictive type, but if it's not that we let their HVAC company deal with it. Poor ductwork is to blame for a lot of the high limit problems, clogged blower wheels and a-coils account for some of them also.

  20. #60
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by 54regcab View Post
    We could wire straight to the transformer to keep 24V at all times, but won't do so. If the furnace is hitting high limit they need to call their HVAC company and have them correct what's causing the problem.
    I could take that same board, add a simple N/O relay between the red stat wire on the board and the stat, so when the limit opens, the red wire from the stat to the board, is open, but the thermostat is still powered up. There is no more risk involved, than you adding your thermostat, this is the understanding of simple controls not rocket science.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




+ Reply to Thread
Page 3 of 9 FirstFirst 123456789 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •