    Question Flow Change Rate to a Carrier 30HXA chiller

    Does anyone know where I can find the flow change rate to a Carrier model: 30HXA186RZ-630ZB. The cooler mod is: 10HX400013. The reason I ask is that I'm looking at going to variable flow using a primary pump. I have two of these chillers piped in parallel and would like to know if the chillers could handle this.
    More information is posted in the controls forum under pressure tranducers and VFDs. Any help would be appreciated.
    Last edited by whec720; 02-12-2007 at 01:09 PM. Reason: mis-spell
    "Nearly all men can stand adversity, but if you want to test a man's character, give him power."
    -Abraham Lincoln

  2. #2
    Join Date
    Jan 2005
    Posts
    605
    Post Likes
    Well ya might check out Carrier's literature available on their site.
    Start here http://www.xpedio.carrier.com/idc/gr...t/30hx-6pd.pdf
    Check out page 20, Application Data, gives min. flow rates. You will certainly be changing the selection data for the existing chillers. Some of what you may want to do may be trial and error. Not sure.

  3. #3
    Join Date
    Jan 2005
    Posts
    605
    Post Likes
    Here's a quote from the Application Data

    "Variable cooler flow rates — These variable rates may
    be applied to standard 30HX series chillers. However, the
    unit will attempt to maintain a constant leaving chilled-fluid
    temperature. In such cases, minimum fluid loop volume
    must be in excess of 3 gpm per ton (3.2 L per kW) and
    flow rate must change in steps of less than 10% per
    minute. Apply 6 gal per ton (6.5 L per kW) fluid loop volume
    minimum if flow rate changes more rapidly."

  4. #4
    Join Date
    May 2006
    Location
    Western NY
    Posts
    4,377
    Post Likes
    Thread Starter

    Wink

    Quote Originally Posted by Carrene #2 View Post
    Here's a quote from the Application Data

    "Variable cooler flow rates — These variable rates may
    be applied to standard 30HX series chillers. However, the
    unit will attempt to maintain a constant leaving chilled-fluid
    temperature. In such cases, minimum fluid loop volume
    must be in excess of 3 gpm per ton (3.2 L per kW) and
    flow rate must change in steps of less than 10% per
    minute. Apply 6 gal per ton (6.5 L per kW) fluid loop volume
    minimum if flow rate changes more rapidly."
    Carrene,

    Thank you. Now I have a good starting point to see if this can work effectively. I'll agree, its going to be a lot of trial and error.
    "Nearly all men can stand adversity, but if you want to test a man's character, give him power."
    -Abraham Lincoln

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •