Thread: Low superheat normal subcooling 2.5 ton txv ?

  1. #1
    Join Date
    Jun 2012
    Location
    Pittsburgh PA
    Posts
    57
    Post Likes

    Low superheat normal subcooling 2.5 ton txv ?

    Just installed arcoaire 2.5 ton 410a txv system and cant get any superheat?
    any advice would be helpful. triple evacuated to 50 microns with dry nitrogen

  2. #2
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    did you braze near that txv ?

    if so did you have a soaking wet rag on it ?

  3. #3
    Join Date
    Jun 2012
    Location
    Pittsburgh PA
    Posts
    57
    Post Likes
    Thread Starter
    I used heat sink and never had a problem before, would that cause no superheat?
    I thought it would close off the valve if overheated. thanks alot for your time

  4. #4
    Join Date
    Jun 2012
    Location
    indiana
    Posts
    12
    Post Likes
    Indeed, could have warped the valve body. Double check that the bulb is insulated so it's not picking up ambient air temp.

  5. #5
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    indoor blower turning correct direction ?

    make sure you have good air flow out the vents , if its not blowing well , check that wheel direction

  6. #6
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    indoor blower turning correct direction ?

    make sure you have good air flow out the vents , if its not blowing well , check that wheel direction

  7. #7
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by Brad gall View Post
    Just installed arcoaire 2.5 ton 410a txv system and cant get any superheat?
    any advice would be helpful. triple evacuated to 50 microns with dry nitrogen
    What is your "normal" SC?
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  8. #8
    Join Date
    Jun 2012
    Location
    Pittsburgh PA
    Posts
    57
    Post Likes
    Thread Starter
    Would overheating the bulb cause no superheat and normal subcooling, also the unit is cooling, however im concerned about the superheat and didnt want to change it out unless necessary , or could it be another problem?

  9. #9
    Join Date
    Jun 2012
    Location
    Pittsburgh PA
    Posts
    57
    Post Likes
    Thread Starter
    12 degree is what the unit is calling for.

  10. #10
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by Brad gall View Post
    Would overheating the bulb cause no superheat and normal subcooling, also the unit is cooling, however im concerned about the superheat and didnt want to change it out unless necessary , or could it be another problem?
    Overheating the bulb, could cause it to act improper in many different ways, or not act at all.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  11. #11
    Join Date
    Jun 2012
    Location
    Pittsburgh PA
    Posts
    57
    Post Likes
    Thread Starter
    bulb is instulated, Ive never had this problem on a new install and just hoping for any advice. Sure hope i dont have to change it out

  12. #12
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by Brad gall View Post
    12 degree is what the unit is calling for.
    So if you have the 12° SC what is the SH? or do you have the 12° SC?
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  13. #13
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by Brad gall View Post
    bulb is insulated, Ive never had this problem on a new install and just hoping for any advice. Sure hope i don't have to change it out
    Well just FYI on the next job, never braze your copper with the bulb attached, your just asking for problems.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  14. #14
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    you didnt install it backwards didya ...

  15. #15
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,312
    Post Likes
    I would be concerned to if a new install is running with zero superheat.

    Liquid refrigerant is most likely making it back to the compressor. If its not causing damage by way of slugging its washing the oil and eventually you'll experience bearing failure.

    Its hard to believe you have any liquid seal with a Txv wide open. If you've confirmed your readings are correct and there is no adjsutment on that TXV then your only option is to replace it.

  16. #16
    Join Date
    Jun 2012
    Location
    Pittsburgh PA
    Posts
    57
    Post Likes
    Thread Starter
    Thanks alot for all the help.... 12 degree subcooling and 0 on the superheat both measured at the condenser. everything else seems fine and its cooling well, I should have disconnected the bulb rather than relying on the heat sink though. If anyone thinks of anything else to check id rather not have to change out the valve. thanks again

  17. #17
    Join Date
    Jun 2012
    Location
    Pittsburgh PA
    Posts
    57
    Post Likes
    Thread Starter
    The txv was factory installed and insulated I did use heat sink around the connection, maybe not enough

  18. #18
    Join Date
    Jun 2012
    Location
    Pittsburgh PA
    Posts
    57
    Post Likes
    Thread Starter
    Thanks SIX I thought overheating the bulb would close off the txv??

  19. #19
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by Brad gall View Post
    .12 degree subcooling and 0 on the superheat both measured at the condenser..
    This just don't make sense to me, you would think with only a 12° SC if you were able to get that with a wide open valve, that there would be some flashing, and not have a 0 SH, heck you got me. That coil come with a piston and you forgot to remove it?
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  20. #20
    Join Date
    Jun 2012
    Location
    Pittsburgh PA
    Posts
    57
    Post Likes
    Thread Starter
    I just checked my notes on the job the unit is requiring 12 degrees of subcooling and i had 10. Could it be slightly overcharged?

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •