    Does anyone use this for a low temp box in the -10 Degree range and if so do you have a particular expansion valve suitable for low temps that you can remember? I working on a box with this setup and the expansion valve says its for that type of refrigerant but I'm having a hard time understanding the pressures when I gauge the system and getting the box below 10 degrees. I tried doing a search for this but no one really covers mp 39 in any real detail.
    The only decision in life is to decide what to do with the time given to you

  2. #2
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    This topic has had extensive discussions over the years here on HVAC-Talk. If you enter the right keywords in the site Search, you'll find lot's of them.

    Here's one of the more recent ones:

    http://hvac-talk.com/vbb/showthread.php?t=803352

    Generally speaking, MP-39 (R401A) and its cousin R409A are best suited for medium & high temperature R12 applications. Although it will work on low temp R12, there is only one which is designed for that temperature range...ie, MP-66 (R401B) and it performs much better.

  3. #3
    Join Date
    Nov 2006
    Location
    Wisconsin
    Posts
    550
    Post Likes
    It was My understanding that MP66 is better for low temp applications. As far as the pressures go, just get a pt chart.

  4. #4
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes

  5. #5
    Join Date
    Jan 2006
    Posts
    149
    Post Likes
    Thread Starter
    The thing that suck is I have already been adding the 401 a back into the system and trying to set up the tev to work with the pressures is confusing me. If you wanted a box to maintain that range temperatures (-10 - 0) that would mean that my average evap. temp would be the same right? And then I would figure in the glide of 6, because I think they say its actually <11.5 right? It would be added to the superheat? Too much math and I'm getting confused. Not too often do I have to do this but this is a first for 401a. Anyone have a better way to explain this? I feel I'm not doing it right.
    The only decision in life is to decide what to do with the time given to you

  6. #6
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Quote Originally Posted by HighTekk^ View Post
    The thing that suck is I have already been adding the 401 a back into the system and trying to set up the tev to work with the pressures is confusing me. If you wanted a box to maintain that range temperatures (-10 - 0) that would mean that my average evap. temp would be the same right? And then I would figure in the glide of 6, because I think they say its actually <11.5 right? It would be added to the superheat? Too much math and I'm getting confused. Not too often do I have to do this but this is a first for 401a. Anyone have a better way to explain this? I feel I'm not doing it right.
    Let's see if we can help clear this up for you a little...

    First, the TXV's sole job in the system is to control refrigerant flow to the evaporator according to the superheat of the refrigerant vapor leaving the evaporator. It's not a pressure regulator.

    Secondly, if the refrigerant temperature inside the evaporator were the same as the box temperature, how could there be any heat transfer? The evaporator temp must always be at a lower temperature. With a walk-in box, this temperature difference (TD) is usually about 10ºF whereas reach-ins usually run around a 15ºF TD. (I'll use a 10ºF TD in the following for simplicity.)

    DuPont T/P Chart: http://www2.dupont.com/Refrigerants/...ofit_guide.pdf

    With a 0ºF box running R401A and a 10F TD, you should expect to run an evap temp of -10ºF. That would correspond to a saturated pressure of 2.8 psig. At that point the TXV should be set to control the superheat to approximately 6-8ºF leaving the coil...ie, the suction line temp at the sensing bulb should read around -2ºF to -4ºF.

    When you use a T/P chart, the saturated temps in the lower ranges typical are the dewpoint temperatures, which already accounts for the refrigerant's glide.

  7. #7
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Others are R408 & R422C used for R502 replacement. Low temp. Was your box refrigerant originally R12 or R502 ?

  8. #8
    Join Date
    Jan 2006
    Posts
    149
    Post Likes
    Thread Starter
    Good deal, I think I see the light. I'm currently adjusting the sh, adding refrigerant as the box cools. That seem normal? Lots of frost to. Seems to be going in the right direction.
    The only decision in life is to decide what to do with the time given to you

  9. #9
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Quote Originally Posted by HighTekk^ View Post
    Good deal, I think I see the light. I'm currently adjusting the sh, adding refrigerant as the box cools. That seem normal? Lots of frost to. Seems to be going in the right direction.
    Properly charging the system brings up another set of issues.

    What exactly is this system you're working on? Is it a walk-in box with a remote condensing unit with a receiver or a self-contained reach-in with no receiver?

    If it's a walk-in system with a receiver, you should have a sightglass in the liquid line after the filter-drier. For proper charge, just clear the glass (unless it has a Headmaster condenser flooding control...which is another matter).

    If it's self-contained with no receiver, the system would be critically charged...meaning you need to weigh-in the refrigerant. There should be a factory recommended charge stated on the data plate for the box. With R409A, since it's less dense than R12, will require less weight than the factory charge amount. This is determined by the density ratio of R409A to R12:

    Density Ratio = 76 lbs/cu ft / 81.8 lb/cu ft = R12 Weight X .93

  10. #10
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Quote Originally Posted by VTP99 View Post
    Others are R408 & R422C used for R502 replacement. Low temp. Was your box refrigerant originally R12 or R502 ?
    We're assuming this was originally an R12 LT system.

  11. #11
    Join Date
    Jan 2006
    Posts
    149
    Post Likes
    Thread Starter
    Its an old bohn evaporator that had r12 in it, converted a while ago, then sat for about a year when some other contractor tried condemning it. Owner said the contractor reported it had multiple leaks and a bad compressor, quoted him a really high price for replacement and repair. So coming into it I had my doubts. But today I finally was able to get the box down to 6-8 degrees. I played with the valve and charge and ended up with a suction of 8 and a head of 110 and my superheat as measured at the condenser was 8-12. This was after removing refrigerant until I seen flash in the sightglass for at least a 20 min period. Everything was done for at least 20 minutes at a time, including expansion valve adjustments and refrigerant adding/subtracting. But little by little I added refrigerant until the sg cleared and then that's when I started adjusting the tev. I'm just trying to understand why they went with 401a to begin with and was really unsure if it could maintain what they wanted. I was already committed to the 401a because I had ordered it from the supply house and broke the seal before I started having doubts that it would work. Funny how it all works out though. I'll check tomorrow to see if the box has reached proper temps. My question now is how do I get down to a 2-3 suction without causing flash in the sightglass?
    The only decision in life is to decide what to do with the time given to you

  12. #12
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Quote Originally Posted by HighTekk^ View Post
    Its an old bohn evaporator that had r12 in it, converted a while ago, then sat for about a year when some other contractor tried condemning it. Owner said the contractor reported it had multiple leaks and a bad compressor, quoted him a really high price for replacement and repair. So coming into it I had my doubts. But today I finally was able to get the box down to 6-8 degrees. I played with the valve and charge and ended up with a suction of 8 and a head of 110 and my superheat as measured at the condenser was 8-12. This was after removing refrigerant until I seen flash in the sightglass for at least a 20 min period. Everything was done for at least 20 minutes at a time, including expansion valve adjustments and refrigerant adding/subtracting. But little by little I added refrigerant until the sg cleared and then that's when I started adjusting the tev. I'm just trying to understand why they went with 401a to begin with and was really unsure if it could maintain what they wanted. I was already committed to the 401a because I had ordered it from the supply house and broke the seal before I started having doubts that it would work. Funny how it all works out though. I'll check tomorrow to see if the box has reached proper temps. My question now is how do I get down to a 2-3 suction without causing flash in the sightglass?
    Thanks for the blow-by-blow description. That's helpful in letting me know where you are at this point.

    Stop playing with the charge trying to affect a change in suction pressure.

    Just charge to a full SG. Add a pound or two more to be sure it'll stay clear and forget about it for the time being.

    Set the TXV superheat leaving the evaporator, not at the entrance of the condensing unit. The location of the TXV's sensing bulb is precisely where I'm referring to.

    Once all this is done, please remember this advice. You cannot force the suction to where you want it to be, as it will always tend to go to a point at which the system is balanced with the load imposed upon it.

    That basically says, "What you'll see is what you'll get."

  13. #13
    Join Date
    Mar 2007
    Location
    AR
    Posts
    2,489
    Post Likes
    like he said, charge until glass is clear. then 6-8 deg s.h. at the bulb. copeland wants 20 at the inlet of the compressor, sometimes thats hard to do depending on the length of the lineset. focus on the s.h. at the bulb. once i get it to 6 at the bulb its usually very close. ill then adjust very slightly until i get it to its most stable point.

    thats all the unit will do at that point. squeezing down the txv to lower your suction in attempt to get a colder evap will only starve the evap and make the txv hunt

  14. #14
    Join Date
    Jan 2006
    Posts
    149
    Post Likes
    Thread Starter
    MP 39 was a failure, I couldn't get the box below 25 degrees without starving the system for refrigerant and creating flash before the tev. Gonna reclaim and try out mp 66, as I have heard is the only low temp. replacement for r-12. After clearing the sightglass my suction psig at the compressor was around 16-20 which won't really do me any good. I'll be out there probably tomorrow to fool around with it some more.
    The only decision in life is to decide what to do with the time given to you

  15. #15
    Join Date
    Jan 2006
    Posts
    149
    Post Likes
    Thread Starter
    Looking at the pt chart hp80 would give me the lowest temp possible for the pressures I have, ya think that might pan out better?
    The only decision in life is to decide what to do with the time given to you

  16. #16
    Join Date
    Jan 2006
    Posts
    149
    Post Likes
    Thread Starter
    Quote Originally Posted by icemeister View Post
    You can't use HP-80 (R402A) because it would overload that compressor which was designed to run on R12.
    Not too sure about that but I do know this about the box...

    Was originally an R-12 Low temp box that was converted to 404a(which I recently found out after working on another piece of equipment that described changing everything onsite to 404a).

    The old expansion valve had failed shut so it was replaced with a sporlan EFSE-1/2-ZP. As you know this is good for low temp R-404A, R-502, R-402A or R-507.

    In addition to replacing the valve I also had ordered an additional powerhead for the TEV that would work for R-134A, R-12 and R-401A. As the 401a was the cheapest refrigerant I could buy I opted to go with it but it never cooled the box below 10 degrees.

    So now I am considering using the HP80, MP66 or 404A, which I have a bottle of each in my possession. I just don't want to wast another day reclaiming, changing dryer, pressure-testing, evacuation and so on.

    I would like to keep the box at -10 degrees if possible when its fully loaded on a warm day.

    What do you think? I have read many threads on here but there is a lot of conflicting posts.

    This box has thrown me through a loop, just when you try to experiment and cut a itty bitty corner it turns around and bites you in the a**. So I was wondering if anyone has any particular experience in this overall situation.
    The only decision in life is to decide what to do with the time given to you

  17. #17
    Join Date
    Sep 2011
    Location
    Augusta, ME
    Posts
    135
    Post Likes
    I myself would convert back to 404a i like that refrigerant

  18. #18
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Quote Originally Posted by HighTekk^ View Post
    Not too sure about that but I do know this about the box...
    If the compressor is designed for R12 LT, I'm quite sure of that.

    Quote Originally Posted by HighTekk^ View Post
    Was originally an R-12 Low temp box that was converted to 404a(which I recently found out after working on another piece of equipment that described changing everything onsite to 404a).
    You somehow failed to mention that little piece of information earlier. Was the compressor changed to an R404A LT or is it still the original R12 compressor?

    Quote Originally Posted by HighTekk^ View Post
    The old expansion valve had failed shut so it was replaced with a sporlan EFSE-1/2-ZP. As you know this is good for low temp R-404A, R-502, R-402A or R-507.

    In addition to replacing the valve I also had ordered an additional powerhead for the TEV that would work for R-134A, R-12 and R-401A. As the 401a was the cheapest refrigerant I could buy I opted to go with it but it never cooled the box below 10 degrees.

    So now I am considering using the HP80, MP66 or 404A, which I have a bottle of each in my possession. I just don't want to wast another day reclaiming, changing dryer, pressure-testing, evacuation and so on.

    I would like to keep the box at -10 degrees if possible when its fully loaded on a warm day.

    What do you think? I have read many threads on here but there is a lot of conflicting posts.

    This box has thrown me through a loop, just when you try to experiment and cut a itty bitty corner it turns around and bites you in the a**. So I was wondering if anyone has any particular experience in this overall situation.
    The first thing you must realize is the refrigerant you must use is determined by what compressor you have. You can't dump R404A into a system with an R12 compressor and expect it to work.

    What is the model number of the compressor you're dealing with? That would be a major help for us who want to help you with this.

  19. #19
    Join Date
    Jan 2006
    Posts
    149
    Post Likes
    Thread Starter
    Its a techum. M#AH410EF-509-A4
    The only decision in life is to decide what to do with the time given to you

  20. #20
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Quote Originally Posted by HighTekk^ View Post
    Its a techum. M#AH410EF-509-A4
    That's a Bill Of Material number, but my Tecumseh info says it's an AHA2445AXD, which is an R12 low temp compressor. Whoever "converted" this to R404A didn't know what he was doing.

    If you are to use this compressor, your one and only hope is R401B (MP66) and that the compressor itself is fully functional...ie, no bad valves and it's not worn out.

    Otherwise, go with a new R404A condensing unit of equal capacity, change the TEV and charge her up with orange juice.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •