    Went out on a york call today. With unit off pressures read, lo 28 & hi 58. It was about 85 out. Started the unit up and the liquid line started to freeze all the way to the evap coil.
    I shot some r22 in and the liquid line thawed out immediately. Unit was blowing off plenty of heat but pressures would not seperate. There was about 20 degrees difference. I stopped adding r22 and the pressure started dropping, as if a major leak.
    I pull the disconnect to listen for a leak. No leak outside. The pressures had dropped to about 28 lo, & 48 hi, just before pulling the disconnect.
    After the disconnect was pulled , the pressures rose to 151 lo & 161 hi.
    I reinserted the disconnect and the pressure pulled down to 50 lo & 73 hi, in just about 3 minutes.
    The compressor was having some trouble, kind of like shuddering just a little, a couple of times.
    The o.s. unit is a york stellar series s# wfnm026603, m# h4db030s06a.
    The inside coil was a s# efws305045, m# g-ut037sa, central cooling.
    What is going on?
    Apr 2012
    Paper Street Soap Company
    Liquid line drier restriction.
    Apr 2012
    Might be in the Condenser.
    Dec 2011
    bedford ind
    I wondered about that, but the line froze from the service valve all the way to the coil. I expected just the point of blockage to freeze quickly, but the whole line did. thanks
    Quote Originally Posted by ironpit View Post
    one thing i notice , i think one of your guages are off . Hook up the low side to a jug of 22 or whatever you have , then your high , and make sure they read the same.
    Look at a pressure / temp chart and see how much psi the jug should be at.
    2nd .... the unit was almost completely empty when u arrived ... maybe had half a pound in it.
    3rd ... if you only got 73 psi on the high side , you may have a junk compressor , or a big time restriction.
    Throw your amp meter on
    Is there a drier hidden inside the OD unit ?
    4th .... make sure both service port king valves are open. Get out your allen wrench and verify.
    If both were indeed all the way open , then lets do a simple compressor test , close the high side king valve , crank her up , and make sure the low side can pull down to 0
    If it does , then atleast ur compr has a potential to be repaired
    Indoor fan is working correct ?
    Lotts of air comming out vents ?
    Report back with your findings
    Jul 2012
    central VA
    Does the unit have a TXV at the evap coil. If it does try
    Putting the bulb in hot water and check your pressures.
    Jul 2012
    central VA
    Please post what your findings were
    Feb 2012
    Toronto Canada
    Low on Gas
    Was the Blower working?
    Yes there was one on the inside of these units when it came from the factory.
    Whether or not it has been removed by some other tech, is another thing.
    Jul 2012
    central VA
    Take the bulb loose from the suction line and stick it in hot water. This will open the TXV wide open and your pressure should come up.
    I rather do nothing and be happy than to do something and not be happy
    Jan 2010
    new orleans
    Your down stream of your restriction and probably low charge ! Look where the frost starts and there is your problem.
    Dec 2011
    bedford ind
    I put a new filter on, arrow pointing inside. Pulled a vacuum to below 500 microns, released the refrigerant (r22) and inserted the disconnect. The condenser fan came on immediately, the compressor came on about 7 minutes later.
    I had checked the values on the 35/5 cap. They were 34.8 and 5.0.
    The pressures were equal until the compressor came on. at first they rose, then they started dropping , maintaining about 20 psig apart until I pulled the disconnect.
    At first the unit was putting out a lot of heat, decreasing as the pressures dropped.
    The blower was putting out plenty of air.
    This time the liquid line did not attempt to freeze or sweat.
    Dec 2011
    bedford ind
    no txv inside
  14. #14
    Jul 2012
    central VA
    If the compressor started 7 min after the condenser fan then the compressor is at fault. What is the amp draw of the compressor running? Also does it make any noises before it starts, if it does whats the amp draw. Sounds like it maybe a no pumper if the pressures stay equal.
  15. #15
    Dec 2011
    bedford ind
    Also, no king valves, just regular. The unit would not pull down below 60,with the high side shut. Both valves were fully open to start.
  16. #16
    Jul 2012
    central VA
    Also is this a heat pump, if so remove the O wire and see what the pressures do maybe the reversing valve is not all the way in cool mode
  17. #17
    Dec 2011
    bedford ind
    I didn't do an amp draw after the behavior of the compressor. Sounded fairly normal on start-up. I did an amp draw before the compressor came on and it was .09, for the fan.
  18. #18
    Dec 2011
    bedford ind
    Straight a/c
  19. #19
    Dec 2011
    bedford ind
    The unit pumps down. both sides. The pressures were about 39 lo and 64 hi when I pulled the disconnect.
  20. #20
    Jul 2012
    central VA
    Ok the compressor is bad then. It comes on but doesn't pump refrigerant. Thats called a no pumper