Thread: Open fresh air return in attic

  1. #1
    Join Date
    Sep 2006
    Posts
    9
    Post Likes

    Open fresh air return in attic

    We are in process of building a home in North Texas. As part of the construction, we have encapsulated the attic with open cell spray foam. In essence, the attic is part of the home's conditioned air space.

    My HVAC contractor installed, with our blessings, a system whereby the fresh air return entails about three to four feet of duct and then is open into the attic. This is lieu of having fresh air returns using duck work to the air handler. The HVAC contractor feels the air in the attic needs to be conditioned as well as the home (1 story home).

    Prior to starting construction, I engaged an independent energy inspector primarily for the spray foam insulation. As part of his services, he also inspects the installation of the HVAC system. When he saw the open fresh air return on the HVAC, he went ballistic – stating that it violated code to use the attic as part of the fresh air return.

    My HVAC contractor provided me several names of other builders that use the open fresh air return in the attic with great success and counters that these have passed inspection. He, however, indicated that I wanted enclosed return; he would modify the system without charge. Please note that I have a green tag from the city building inspector.

    I wanted to submit this question for discussion. I ask that you not debate the enclosed attic system since it is a given.

    I would appreciate if anyone else has used the concept of using the attic as part of the return without corresponding ducting.

    Thank you for your comments.

  2. #2
    Join Date
    Dec 2006
    Location
    Dallas
    Posts
    189
    Post Likes
    Why would you aircondition your attic if you are not living in it? The attic has a great amount of surface area and unnecessary heat gains resulting in additional losses. Is the attic warmer then the house? How "Sealed" is the attic? Have they done a door blower test to prove that the attic is air tight?

    If you turn off the AC, how fast does the temperature climb and how much in the attic vs the house? Every degree adds to a loss in space you don't occupy.

    On a paranoid note, I wonder what kind of emissions the foam will have being directly sucked into your indoor air at a high rate? What ever emissions there may be, they probably taper off fairly quickly, but still, how many 20 year studies are there for the health effects of the foam used in your home when being used as part of the airflow path directly effecting indoor air quality?

    That's what I think... The pros will comment on facts.

  3. #3
    Join Date
    Apr 2002
    Posts
    11,808
    Post Likes
    a sealed attic can work great

    but I would not use it as a big plenum. I would duct the return

    I would also have a dedicated fresh air intake directly from outside

    you are supposed to condition the space, but some thing as simple as a 40 cfm supply and return from there is fine.

    People are used to doing work in stripmalls with flat roofs. They call the space below the roof and above the ceiling a return air plenum. You have the samething, but if you are not well sealed to the top of the wall plates, you have the entire perimter of the home to be a big potential leak , meaning you could get a lot of uncontrolled outside air moving in when you have the main system drawing all its return from the attic

    I tested my own sealed attic for 6 months beofre I finally conditioned it with a small amount of air. I added the air as I was storing some valuables up there- just a little safeguard to keep things extra dry.

    The main opposition from the building inspector to doing what the builder wants is because it is a new thing as far as residential goes. I would vote to duct the return for the reasons I gave.
    Last edited by Carnak; 07-17-2008 at 10:11 PM.

  4. #4
    Join Date
    May 2008
    Posts
    182
    Post Likes

    Help me understand

    I understand the concept of using the space above the ceiling as a return air plenum. It's done all the time in commercial buildings, when a dropped ceiling is used. Are return "grates" placed in rooms to allow the air to be circulated? Your contractor wanted the attic space conditioned...does that mean supply air is also going into the space? And why would you want to have to heat or cool the attic air as it enters your furnace. Seems counter-productive to me.

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Conditioning the attic space is a waste of money.
    Unless your using the attic for more then storage.
    I hope your HVAC contractor didn't install a bigger A/C to condition unused space.

  6. #6
    Join Date
    Jul 2008
    Location
    Denver, CO
    Posts
    4,379
    Post Likes
    Here is my opnion. Close off the attic. It is completely senseless to make the attic a part of the HVAC system if it is not occupied. And in most places it is NOT up to code.

  7. #7
    Join Date
    Jan 2004
    Location
    Burleson, Texas
    Posts
    1,741
    Post Likes
    Wow, Just some quick remarks (I'll have to think on this one)..

    What is the heating source? electric/heat pump or gas

    IMO, your attic is now a return plenum, so is it fire rated ?

    Will the plumbing and electrical in the attic have to be fire rated?

    How much and how long will the spray foam offgas ?

    Dust,humidity and odor issues ?

    Building pressures ?

    Storage in the attic nulled?

    What city are you dealing with?

    Not trying to be negative,but I have done houses in N.Tex with the
    sprayfoam, with great success.. But I did everything possible to seal the
    living area from the attic...

  8. #8
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    I think we have a confusion of terminology here. A "fresh air intake" is different from a "return air intake". Fresh air intake inducts fresh air from the outdoors. A return air intake is where air returning from the conditioned areas is inducted into the air handler or furnace.

    So, I'll assume you mean your sealed attic has a return air provision. And reading your post further, I think you are trying to use the entire attic as a return air plenum, with openings in the house below to allow air to return to the unit. If so, this is what is known as an "open return" system.

    I'll be frank with you...I'm not fond of open returns, period. I think they're a shortcut around a proper return air system. In humid climates, open returns cause lots of problems in commercial buildings if the area being used for the return space is not absolutely airtight. In construction, that is very hard to accomplish.

    I would need to be assured the sealed attic is indeed airtight before I'd sign off on it being an open return system. Any air leak to the outside will draw moisture through construction materials during hot, humid weather, and any fireplace chases, thermal bypass areas, etc. may do the same thing if they also are not sealed with respect to the attic and house.

  9. #9
    Join Date
    Apr 2002
    Posts
    11,808
    Post Likes
    Quote Originally Posted by beenthere View Post
    Conditioning the attic space is a waste of money.
    Unless your using the attic for more then storage.
    I hope your HVAC contractor didn't install a bigger A/C to condition unused space.
    less heat coming through the ceiling its not a 140F suana up there any more

    air handler and duct work up there are not losing 10% capacity while being radiated. Air handler will last longer.

    technically get a bigger conditioned space for no extra energy penalty.

    40 cfm keeps it a couple degrees warmer than the space below, I have no shortage of data to back this up, i built a four pleax like this
    Last edited by Carnak; 07-17-2008 at 10:27 PM.

  10. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    40 CFM is not nearly the same as using it for the full return of the system.

    40 CFM is more of a tempering, not conditioning.(perhaps a perspective thing)

  11. #11
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,881
    Post Likes
    what is your heat source??

    put a 80% furnace up there and the attic return plenum becomes a big no no.

  12. #12
    Join Date
    Apr 2002
    Posts
    11,808
    Post Likes
    Quote Originally Posted by beenthere View Post
    40 CFM is not nearly the same as using it for the full return of the system.

    40 CFM is more of a tempering, not conditioning.(perhaps a perspective thing)

    My own attic i could have ran as a return plenum, its tight.

    I just looked through a couple test runs, before I conditioned it, with a very small amount of air, it would average about 81F and 50% RH up there, and that makes it into ASHRAE's comfort zone.

    The attic temperatures were always the hottest after the sun set mainly because I have some surface mounted lights mounted on the ceilings and it traps the heat from the lights.

    So I was keeping my place about 78 F, the thermostat is 5 feet above the floor. I would imagine the air up below my ceiling is 79 degrees or so, so I had a 2F differential through the sheet rock ceiling. Not a lot of heat transfer driven to the space below.

    I added a very small amount of air 40 CFM tops, and it now averages 79F and RH about 43%

    I have seen buildings retrofitted with the foam and the attic is a plenum and I never noticed any problems. No inspector has seen this either.

  13. #13
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    To me. An 80° attic would be tempered.
    I keep my place cold.

    Doesn't the attic add about 4000 to 6000 BTU to the load, depending on roof pitch, orientation etc. On say a 2000 sq ft single story. If you try to bring it down to what the nomal occupied temp of the house is. That temp being say 72°F?

  14. #14
    Join Date
    Apr 2002
    Posts
    11,808
    Post Likes
    call it tempered if you like. The purpose of the tempering is to keep it from getting stagnant, making sure it does not get too humid. Building Science site has scenarios they are blowing 25 CFM and calling it conditioned. If you have gable walls you need to insulate them also,].

    I will look, I have some numbers for when I was keeping my place at 75, off the top of my head the attic did not follow suit exactly,it did not average three degrees lower.

    SO it would sort of being like heating your house to 72 in the winter and it is only 68 in the basement

    Malls with barjoist, built up decks, flat roofs are a very similar scenario, the space above the ceiling is a plenum but is really a sealed attic
    Last edited by Carnak; 07-17-2008 at 11:44 PM.

  15. #15
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Would having gable vents do the same?

  16. #16
    Join Date
    Aug 2006
    Location
    Dallas (Plano), TX
    Posts
    168
    Post Likes
    Quote Originally Posted by andserco View Post
    ... IMO, your attic is now a return plenum, so is it fire rated ? ...
    For my single-story 'ranch style' residence with a large attic / high roof:

    With my prior HVAC system, I had an Enerstat 3+2 (5 zone) controller, with its smoke terminals connected to my fire detection system. If a smoke/heat detector went into alarm, the fire alarm panel would close the circuit to the HVAC zoning panel's smoke terminals. This action would cause the zoning panel to shut down the HVAC equipment and close all damper motors.

    With my current HVAC system, the 'smoke terminals' are on the HVAC unit itself now, and are connected in the same manner to the fire alarm system. Same action if a smoke/heat detector goes into alarm - HVAC equipment shuts down, pumps stop, and damper motors close.

    For an attic that is conditioned air that is part of the system of breathing air for a home, I would take a careful look at strategies to ensure smoke doesn't enter into the living areas of the residence. A well thought out and aggressive smoke detection system in the attic, for an area that is conditioned air, I would think should be a must.

    Best regards,

    Bill

  17. #17
    Join Date
    Dec 2006
    Location
    Dallas
    Posts
    189
    Post Likes
    Back to the original post:
    ...He, however, indicated that I wanted enclosed return; he would modify the system without charge...
    I think I would go with this option.

  18. #18
    Join Date
    Apr 2002
    Posts
    11,808
    Post Likes
    Quote Originally Posted by beenthere View Post
    Would having gable vents do the same?
    not following gable vents, talking about a sealed attic

  19. #19
    Join Date
    Jul 2002
    Location
    Yuma, AZ
    Posts
    2,755
    Post Likes
    The sealed attic is great with return and supply duct inside of the thermal envelope of the building.
    If there is no return duct, the concept is that the attic space becomes a return air plenum and this is not uncommon in commercial plenums.

    • I have a huge concern about fire safety. As a contractor I would not consider doing that unless the National Fire Protection Association (NFPA) approved the proceedure http://www.nfpa.org/index.asp Talk to your local fire departement (It is their job to know the local codes. I don't happen to know our local position but I will look into it.)

      I would not want the responsibility or liability for property loss or loss of life in case of a fire propagated or spread through an unducted attic return air system,

    • Smoke generated by attic contents could also be a major safety concern. The foam, plastics and other items may produce toxic fumes and spread them throuhout the house along with the fire.

    • Finally the attic is sealed the day it is built. Will it be sealed after the plumbers, cable guys, and other home modifiers work in the home over the next 30 years? If not what will that do to the power bill and the home itself if incoming air brings moisture and mold problems into your attic space? This concern alone would make me unwilling to inovate. Entire homes have been destroyed by runaway moisture and mold issues. Mold insurance is out of the question...unaffordable. That makes me think that you may also want to talk to your insurance company about this matter.
    "I have never let my schooling interfere with my education."
    Mark Twain
    NEVER STOP LEARNING.

  20. #20
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by Carnak View Post
    not following gable vents, talking about a sealed attic
    Was just wondering if installing gable vents would be enough ventilation for the insulated attic.

Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •