    7/8 lineset on a 5 ton system

    I have seen at least 2 AC 5 ton R-410 systems run with 7/8 lineset instead of 1 and 1/8".
    I didn't take any readings, but the owners said they are running fine.
    What do you guys think?

  2. #2
    Join Date
    May 2011
    Location
    Western, KY
    Posts
    3,430
    Post Likes
    Quote Originally Posted by jdere View Post
    I have seen at least 2 AC 5 ton R-410 systems run with 7/8 lineset instead of 1 and 1/8".
    I didn't take any readings, but the owners said they are running fine.
    What do you guys think?
    They are most likely fine. Not every 5 ton calls for an 1 1/8 line set, sometimes it's actually better to keep up your velocity.

  3. #3
    Join Date
    Sep 2005
    Posts
    58,704
    Post Likes
    Tricky subject...
    Length of lineset and location of coil and AC unit (over/under and how much)... Different manufacturers say different things... And if it is a 2 stage... most will go with 7/8.

    Usually running a too small SL will reduce efficiency by 3-4-5%... not a huge amount if re-running the lineset was difficult.
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

  4. #4
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Many are happy with that, especially 410.

  5. #5
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Even with fairly long lines, 50-70', with a few fittings, AS/Trane's piping software will almost always spit out 7/8" as the recommended SL size for a 5 ton R-410 AC or heat pump system.
    For shorter line set applications, it will even recommend, a 3/4" SL, or at least list it as an approved alternative.

    For the ARI ratings manufacturers will run short, larger diameter, suction lines to maximize the efficiency ratings, but the size that yields the most reliable system is generally smaller.

  6. #6
    Join Date
    May 2004
    Location
    Malden Mass
    Posts
    414
    Post Likes
    Thread Starter
    Thanks for all the replies!

  7. #7
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    I've seen FAR more problems with 5 tons systems being attached to less than 2,000 CFM worth of ductwork...

  8. #8
    Join Date
    Oct 2012
    Location
    Sacramento,ca
    Posts
    205
    Post Likes
    I have seen multiple compressor failures from companies putting 1 1/8 on current systems. If you look in most install manuals on current 14 plus seer systems they specifically warn you about oversizing lines because it will starve the compressor of oil especially on long runs.

    Also according to Rheem install manuals it is not efficiency you loose with oversized or undersized lines its capacity. for instance i put a 3 ton 15 seer on a home that had a 5/8 suction 3/8 liquid at 70 ft long and there was no way of changing it and the rheem manual stated that i would only loose 3% of capacity so instead of 36kbtu i would only get 35kbtu. Not worth tearing the home apart.

  9. #9
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Quote Originally Posted by Barrettservices View Post
    Also according to Rheem install manuals it is not efficiency you loose with oversized or undersized lines its capacity.
    The small capacity loss directly causes a small loss of efficiency.
    Lower btuh per watt = lower efficiency.

    I'd rather have a more reliable system, that is 1-3% less efficient though.

    Not worth tearing the home apart.
    I absolutely agree.
    In most cases, the potential increase in efficiency from changing to the ideal refrigerant line size won't cover the cost of replacing it within the life span of the system, or even the next system.

  10. #10
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    If you really want to help lower power bills for the homeowner install a 2.5 ton instead of the 3 ton. If it can't keep up fix the leaks/solar gain in the house. Fudging the numbers on manual J calculations to get about 500sqft per ton that has been used since the 60's has got to stop. It's rare that a well designed house with a properly installed HVAC and duct system should need more than 750sft per ton.

  11. Likes Premium Comfort liked this post.
  12. #11
    Join Date
    Oct 2012
    Location
    Sacramento,ca
    Posts
    205
    Post Likes
    Quote Originally Posted by 54regcab View Post
    If you really want to help lower power bills for the homeowner install a 2.5 ton instead of the 3 ton. If it can't keep up fix the leaks/solar gain in the house. Fudging the numbers on manual J calculations to get about 500sqft per ton that has been used since the 60's has got to stop. It's rare that a well designed house with a properly installed HVAC and duct system should need more than 750sft per ton.
    I agree however there are thousands of homes in our area that were built without dual pane windows, wall or floor insulation and very little insulation in the attic. The majority of homewners will not spend the money to fix those issues so we have to install slightly larger systems to compensate.

  13. #12
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Quote Originally Posted by Barrettservices View Post
    I agree however there are thousands of homes in our area that were built without dual pane windows, wall or floor insulation and very little insulation in the attic. The majority of homewners will not spend the money to fix those issues so we have to install slightly larger systems to compensate.
    Agree, older homes with single pane windows/leaks/poor insulation typically need more cooling per sqft. My gripe is newer homes being sized the same ton per sqft as older homes.

  14. #13
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    6,067
    Post Likes
    Quote Originally Posted by mark beiser View Post
    The small capacity loss directly causes a small loss of efficiency.
    Lower btuh per watt = lower efficiency.

    I'd rather have a more reliable system, that is 1-3% less efficient though.
    Its actually more complicated than that. When you reduce capacity, you reduce the work being done by the compressor, which in turn reduces its amp draw. So even if the restricted line causes a 3% capacity reduction, efficiency reduction might only be 1% or even nothing.

  15. #14
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,420
    Post Likes
    Quote Originally Posted by craig1 View Post
    Its actually more complicated than that. When you reduce capacity, you reduce the work being done by the compressor, which in turn reduces its amp draw. So even if the restricted line causes a 3% capacity reduction, efficiency reduction might only be 1% or even nothing.
    under sized suction lines cause a capacity loss and hi velocity.....
    it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair

  16. #15
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Quote Originally Posted by craig1 View Post
    Its actually more complicated than that. When you reduce capacity, you reduce the work being done by the compressor, which in turn reduces its amp draw. So even if the restricted line causes a 3% capacity reduction, efficiency reduction might only be 1% or even nothing.
    I was just pointing out that you do in fact lose efficiency, not attempting to exactly quantify the efficiency loss.

    Continuing the discussion though, when you are dealing with total system capacity losses due to pressure losses, and other issues within the system, the electrical consumption per btuh of net refrigeration usually doesn't go down, or even stay the same.
    Typically it will go up.

    Either way, in most instances the small efficiency loss, due to the small capacity loss incurred by having the smallest recommended vapor line for the application, isn't worth the cost of replacing the refrigerant lines.

  17. #16
    Join Date
    Oct 2010
    Location
    AZ
    Posts
    647
    Post Likes
    Quote Originally Posted by carmon View Post
    under sized suction lines cause a capacity loss and hi velocity.....
    Quote Originally Posted by mark beiser View Post
    I was just pointing out that you do in fact lose efficiency, not attempting to exactly quantify the efficiency loss.

    Continuing the discussion though, when you are dealing with total system capacity losses due to pressure losses, and other issues within the system, the electrical consumption per btuh of net refrigeration usually doesn't go down, or even stay the same.
    Typically it will go up.

    Either way, in most instances the small efficiency loss, due to the small capacity loss incurred by having the smallest recommended vapor line for the application, isn't worth the cost of replacing the refrigerant lines.
    Quote Originally Posted by craig1 View Post
    Its actually more complicated than that. When you reduce capacity, you reduce the work being done by the compressor, which in turn reduces its amp draw. So even if the restricted line causes a 3% capacity reduction, efficiency reduction might only be 1% or even nothing.
    Yes, it is more complicated than that. Remember pump laws and fan laws state that when you block flow, the amp draw is reduced. How much would be hard to determine and you may gain/lose efficiency or stay the same. Calculations for this stuff are just estimations, and you would really have to test it and get real numbers and plot an efficiency curve to find out. But with such a small difference, it doesn't really make sense to worry about. There are a lot of other things that can make a bigger difference, one being orientation and location of the condenser to minimize solar radiation effects which can raise the head pressure considerably and drop efficiency.
    Last edited by dijit; 02-16-2013 at 05:06 AM. Reason: grammar

  18. #17
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by dijit View Post
    Yes, it is more complicated than that. Remember pump laws and fan laws state that when you block flow, the amp draw is reduced. How much would be hard to determine and you may gain/lose efficiency or stay the same. Calculations for this stuff are just estimations, and you would really have to test it and get real numbers and plot an efficiency curve to find out. But with such a small difference, it doesn't really make sense to worry about. There are a lot of other things that can make a bigger difference, one being orientation and location of the condenser to minimize solar radiation effects which can raise the head pressure considerably and drop efficiency.
    Solar radiation doesn't have much effect either. unless the condenser is on a roof, or other surface that is reflecting both radiant heat and convection heat.

  19. #18
    Join Date
    Apr 2016
    Location
    Medicine Hat, AB, Canada
    Posts
    1
    Post Likes

    Thumbs Up

    Quote Originally Posted by 54regcab View Post
    If you really want to help lower power bills for the homeowner install a 2.5 ton instead of the 3 ton. If it can't keep up fix the leaks/solar gain in the house. Fudging the numbers on manual J calculations to get about 500sqft per ton that has been used since the 60's has got to stop. It's rare that a well designed house with a properly installed HVAC and duct system should need more than 750sft per ton.
    Its finally nice to see someone else thinking on the same page. I've been using for rough estimates around 700sft/ ton on sizing. It would be great if the "old guys" in the industry would pick up their socks, open their eyes and realize it's approx 40 years after their way was relevant. The worst is, most of the young apprentice's listen to them because they have been doing it for years. I had a guy tell me the other day that he was told by one of the head engineers at ******* furnace manufacturer, that static pressure was irrelevent. not to worry about it, that his ducts were fine. PARDON????

  20. #19
    Join Date
    Jul 2012
    Posts
    2,366
    Post Likes
    I have a 1.5 ton in an apartment with a 7/8 x 3/8 running 10 feet. The condenser is below grade of the coil. I hope my pressure drop is not severe.lol

  21. #20
    Join Date
    Mar 2015
    Location
    ARK.
    Posts
    3,389
    Post Likes
    So, How do 'you size an old house,built in '27 with NO 'upgrade's?
    My 'socks are just 'fine and,Yes,I do account for the Future.
    No matter how long you have been doing this,
    Go back and reread the Basic's.You WILL Learn something.
    Why is it called,an Act of GOD when IT has Nothing to do with Him?
    Will of the Devil would be more appropriate IMO.Just Saying.
    PSALMS, 18 & 25.
    I am Tired of High Efficiency Propaganda.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •