    Post Likes
    I always charge liquid into the suction line and have yet to kill a compressor although I have tried to in a pi$$ed off mood.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  2. #42
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by crackertech View Post
    I always charge liquid into the suction line and have yet to kill a compressor although I have tried to in a pi$$ed off mood.
    3/8" hose to the suction service valve.

    You just weren't trying hard enough...




  3. #43
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,520
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    3/8" hose to the suction service valve.

    You just weren't trying hard enough...

    Gee thanks I'll try to remember that.LOL
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  4. #44
    Join Date
    May 2000
    Location
    Monmouth Junction-NJ-USA
    Posts
    6,125
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    3/8" hose to the suction service valve.

    You just weren't trying hard enough...

    LMAO That is a GREAT TECH TIP!!!!!!!!!!
    If you really know how it works, you have an execellent chance of fixin' er up!

    Tomorrow is promised to no one...

  5. #45
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by rayr View Post
    LMAO That is a GREAT TECH TIP!!!!!!!!!!
    Always trying to be helpful.

    If you frontseat the valve, the refrigerant will charge faster due to a greater differential in pressure.




    For all the newbies out there, I should post a disclaimer.

    Do not try this at home or on the job. I am a professionally trained idiot.



  6. #46
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes

    When you have the gas out -

    Install a schrader access tee under the TXV equalizing line flare nut. Then blow liquid in there with the system running. The evap will boil it off and the low SSH will throttle the TXV.

    You can also pump 90-95% of the charge into the high side with your recycle machine before starting the compressor. Then just top off to 10 degrees subcooling and you're done.

    PHM
    --------




    Quote Originally Posted by AtoZhvac View Post
    Hi,

    I worked with a tech recently who when charging walk in coolers and freezers after compressor change outs. He would cut off the condenser fans for brief periods of time. Both R-22 and 404-A.

    Im just curious at what this was accomplishing and do any of you guys also do this and why? And how is this done properly etc...

    Another thing say you are charging an R22 refrigeration system (large pan cooler) which requires 34 pounds of R-22. I had a heck of a time getting that much charged in. I ran warm water over the container many times to get the pressure back up to charge in the vapor.

    Any tricks out there at speeding this process up? I know that charging liquid is considered a no no and the little liquid charge restrictor device is pretty slow as well.


    Thanks
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  7. #47
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by Poodle Head Mikey View Post
    Install a schrader access tee under the TXV equalizing line flare nut. Then blow liquid in there with the system running. The evap will boil it off and the low SSH will throttle the TXV.

    You can also pump 90-95% of the charge into the high side with your recycle machine before starting the compressor. Then just top off to 10 degrees subcooling and you're done.

    PHM
    --------
    I always enjoy hearing ideas. Thanks, PHM!
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  8. #48
    Join Date
    Mar 2008
    Posts
    258
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    Always trying to be helpful.

    If you frontseat the valve, the refrigerant will charge faster due to a greater differential in pressure.




    For all the newbies out there, I should post a disclaimer.

    Do not try this at home or on the job. I am a professionally trained idiot.
    LOL I had to quote this one...but it was a good laugh

  9. #49
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes

    Come over and hang out for two weeks

    I promise that you Will hear some ideas! <g>

    PHM
    ---------


    Quote Originally Posted by timebuilder View Post
    I always enjoy hearing ideas. Thanks, PHM!
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  10. #50
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,346
    Post Likes
    Quote Originally Posted by crackertech View Post
    I always charge liquid into the suction line and have yet to kill a compressor although I have tried to in a pi$$ed off mood.


    x1000



    .

  11. #51
    Join Date
    Nov 2006
    Location
    Iowa
    Posts
    86
    Post Likes
    I dont do a lot of refrigeration but on a smaller walk in I will calculate how much liquid the cond coil will hold and then the receiver. I add 80% of what the receiver will hold and what the cond coil will hold. I have done this 3 times and havent had a problem with being short in the winter or overcharged in the summer.
    Bring back rotary phones so we dont have to press 1 to proceed in ENGLISH!!!!

  12. #52
    Join Date
    Oct 2007
    Location
    ATLANTA
    Posts
    121
    Post Likes
    Thread Starter
    Quote Originally Posted by hvacr man View Post
    I dont do a lot of refrigeration but on a smaller walk in I will calculate how much liquid the cond coil will hold and then the receiver. I add 80% of what the receiver will hold and what the cond coil will hold. I have done this 3 times and havent had a problem with being short in the winter or overcharged in the summer.

    Hi

    Please tell me how you calculate how much refrigerant to put into the condenser and the receiver.

    Something that really bothers me about the Sporlan Head Master charging data is nothing is considered for the evaporator or the line set. Am I wrong that that does not matter when making a proper charge?

    Thanks

    ps please some of you guys lay off of turning this thread into a joke fest!
    I am sincerley trying to learn something important here and I honestly can not tell when some of you are contributing something useful or joking about something.



    Thanks

  13. #53
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by AtoZhvac View Post
    Hi


    Something that really bothers me about the Sporlan Head Master charging data is nothing is considered for the evaporator or the line set. Am I wrong that that does not matter when making a proper charge?
    Yes. I cracked a few jokes, but now I get to be a jerk.

    Did you read the Sporlan instructions? Really?

    If so, you would know that the first step is to charge the system to a clear sightglass.

    This automatically accounts for linesets and evap and all that.

    If you're going to learn something, make it the right thing.



  14. #54
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by AtoZhvac View Post
    Hi

    Please tell me how you calculate how much refrigerant to put into the condenser and the receiver.

    Something that really bothers me about the Sporlan Head Master charging data is nothing is considered for the evaporator or the line set. Am I wrong that that does not matter when making a proper charge?

    Thanks

    ps please some of you guys lay off of turning this thread into a joke fest!
    I am sincerley trying to learn something important here and I honestly can not tell when some of you are contributing something useful or joking about something.



    Thanks
    Something bothers me about this reply.

    The sporlan method allows you to calculate the amount of refrigerant required to flood the condenser at low ambient conditions.

    The receiver does not enter into these calculations except that it must be large enough to hold that excess when it isn't needed.

    I don't understand how low ambient is going to affect the amount of refrigerant held in the evap or the lineset, nor do I see how the semi-scientific WAG method offered compensates for them anyway.

    If you want more calculations, look up the Heatcraft installation manual. It has all the numbers to calculate the entrained charge very, very closely. If you are having trouble with the math, bring the numbers here and we will help you with it.

    We DO joke and fool around, but there is more than a little knowledge and experience hanging around here.



  15. #55
    Join Date
    Oct 2007
    Location
    ATLANTA
    Posts
    121
    Post Likes
    Thread Starter
    Quote Originally Posted by jpsmith1cm View Post
    Yes. I cracked a few jokes, but now I get to be a jerk.

    Did you read the Sporlan instructions? Really?

    If so, you would know that the first step is to charge the system to a clear sightglass.

    This automatically accounts for linesets and evap and all that.

    If you're going to learn something, make it the right thing.


    jpsmith1cm,

    Yes indeed I "REALLY" read the Sporlan instructions. You seem to have missed the fact that my post that you quoted was my reply to a post that was made by hvacr man who says he calculates how much the cond coil will hold AND the receiver. See the quote below please.

    posted by hvacr man :
    "I dont do a lot of refrigeration but on a smaller walk in I will calculate how much liquid the cond coil will hold and then the receiver. I add 80% of what the receiver will hold and what the cond coil will hold. I have done this 3 times and havent had a problem with being short in the winter or overcharged in the summer."

    So yes jpsmith1cm I certainly wanted to know what procedure that "hvacr man" uses to calculate for the cond coil and the receiver!
    As far as I know it could be as good or even better method than the Sporlan instructions.

    Also please forgive me for assuming that if the condenser tubing and bends can be calculated for charging purposes that similar measurements and calculations might also apply as well to the evaporator and the lineset.

    After all I have seen systems with NO sight glass on them.

    Im not going to take the route of being a jerk,sarcastic,or condescending on this forum to another member and I would encourage everyone to do the same.

    I continue to believe that this thread will be helpful not only to me but potentially to others as well.

    Best Regards
    Last edited by AtoZhvac; 10-20-2009 at 06:02 PM.

  16. #56
    Join Date
    Nov 2006
    Location
    Iowa
    Posts
    86
    Post Likes
    atozhvac
    I am not sure that the way I have done it is correct, but it netted the results I needed. I really expected some yeahs or neys to my method. I do know that this cant be used for all systems. I have looked for the info on the receivers on the net but cant find it. I do have a hard copy so all I can do is give you an example, but you should be able to locate it on the net or call a refrigeration supply house. So anyway I calculate the cond tubes and u bends just like the sporlan instructions then I measure the reciever and refer to the chart that I only have a hard copy of. Example from the chart: A 6inch dia. x 12long vertical reciever will hold 10lbs of r-22 @ 90 degrees and 90%full. We get hotter here than that some times so I figure a little less. I would then add that to the number I came up with on the sporlan chart for the cond volume and put that total into the system. I am NOT saying that this is the way to do it, but 2 of the 3 or 4 times I have done this I cross checked with the full formula from sporlan and they came out very very close.
    Bring back rotary phones so we dont have to press 1 to proceed in ENGLISH!!!!

  17. #57
    Join Date
    Oct 2007
    Location
    ATLANTA
    Posts
    121
    Post Likes
    Thread Starter
    Quote Originally Posted by hvacr man View Post
    atozhvac
    I am not sure that the way I have done it is correct, but it netted the results I needed. I really expected some yeahs or neys to my method. I do know that this cant be used for all systems. I have looked for the info on the receivers on the net but cant find it. I do have a hard copy so all I can do is give you an example, but you should be able to locate it on the net or call a refrigeration supply house. So anyway I calculate the cond tubes and u bends just like the sporlan instructions then I measure the reciever and refer to the chart that I only have a hard copy of. Example from the chart: A 6inch dia. x 12long vertical reciever will hold 10lbs of r-22 @ 90 degrees and 90%full. We get hotter here than that some times so I figure a little less. I would then add that to the number I came up with on the sporlan chart for the cond volume and put that total into the system. I am NOT saying that this is the way to do it, but 2 of the 3 or 4 times I have done this I cross checked with the full formula from sporlan and they came out very very close.

    Hi

    Thanks for the reply!
    Does your chart have an address or info on it that could lead me to where to get one? Could you email a copy of it to me? if so please email to <Please put your email address in your profile, not in post, thank you>


    Thanks
    Last edited by beenthere; 10-20-2009 at 08:40 PM. Reason: Removed email address

  18. #58
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by AtoZhvac View Post
    jpsmith1cm,

    Yes indeed I "REALLY" read the Sporlan instructions. You seem to have missed the fact that my post that you quoted was my reply to a post that was made by hvacr man who says he calculates how much the cond coil will hold AND the receiver. See the quote below please.

    posted by hvacr man :
    "I dont do a lot of refrigeration but on a smaller walk in I will calculate how much liquid the cond coil will hold and then the receiver. I add 80% of what the receiver will hold and what the cond coil will hold. I have done this 3 times and havent had a problem with being short in the winter or overcharged in the summer."

    So yes jpsmith1cm I certainly wanted to know what procedure that "hvacr man" uses to calculate for the cond coil and the receiver! As far as I know it could be as good or even better method than the Sporlan instructions
    .

    Also please forgive me for assuming that if the condenser tubing and bends can be calculated for charging purposes that similar measurements and calculations might also apply as well to the evaporator and the lineset.

    After all I have seen systems with NO sight glass on them.

    Im not going to take the route of being a jerk,sarcastic,or condescending on this forum to another member and I would encourage everyone to do the same.

    I continue to believe that this thread will be helpful not only to me but potentially to others as well.

    Best Regards
    Point #1. Refrigeration is 95% of what I do. I work on stuff that hold 7 ounces of gas and I work on stuff that holds 1700# of gas and everything in between. I've done it wrong and I've done it right. I have learned the hard way what works and what doesn't.

    Point #2. Somehow I seriously doubt this.

    Point #3. Systems without sightglasses are typically critically charged systems with a weighed in charge and not pertinent to this discussion.


    I have tried to help you. You have refused to accept the advice that has been given you. There is a right way and a wrong way to do things. You can accept the advice of someone who admits to not doing a lot of refrigeration work, or you can take the advice of the people who design the equipment that you are working on.

    Your call.



  19. #59
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by AtoZhvac View Post
    Hi

    Thanks for the reply!
    Does your chart have an address or info on it that could lead me to where to get one? Could you email a copy of it to me? if so please email to

    Thanks
    Probably the same chart I offered you a while ago.

    Last edited by beenthere; 10-20-2009 at 08:40 PM. Reason: Removed email address



  20. #60
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,520
    Post Likes
    Quote Originally Posted by AtoZhvac View Post
    Hi

    Thanks for the reply!
    Does your chart have an address or info on it that could lead me to where to get one? Could you email a copy of it to me? if so please email to

    Thanks
    please remove your E- mail addy
    Last edited by crackertech; 10-20-2009 at 09:24 PM. Reason: Removed email address
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

+ Reply to Thread
Page 3 of 6 FirstFirst 123456 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •