Thread: Is there an add-on Ice Sensor for existing home AC units?

  1. #21
    Join Date
    Jul 2011
    Location
    Delaware
    Posts
    41
    Post Likes
    Thread Starter
    Thanks pecmsg. So your saying they need to have a vacuum pump capable of pulling down to a low micron reading, that only a micro meter can read? What should you pull on a 3T unit in Florida heat?

    I will verify how low they pulled. They also said that they have a 30 minute hold period ... what would be an exceptable vacuum drop ... zero microns?

  2. #22
    Join Date
    Dec 2010
    Location
    Woodbridge Twp, NJ
    Posts
    1,309
    Post Likes
    Quote Originally Posted by KevimK2 View Post
    Thanks pecmsg. So your saying they need to have a vacuum pump capable of pulling down to a low micron reading, that only a micro meter can read? What should you pull on a 3T unit in Florida heat?

    I will verify how low they pulled. They also said that they have a 30 minute hold period ... what would be an exceptable vacuum drop ... zero microns?
    500 microns. If they don't know what a micron gauge is, make sure they don't do any work on your equipment and call the boss to get a thorough tech out there. It's time they stopped playing.
    Every customer you take for granted today will be someone else's tomorrow.

  3. #23
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    using a vacuum test for a leak check is stupid , its best to pressure test with nitrogen then bubble check your braze joints

  4. #24
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    Quote Originally Posted by catmanacman View Post
    using a vacuum test for a leak check is stupid , its best to pressure test with nitrogen then bubble check your braze joints
    In most respects, I agree with carmanacman because the micron gauge will climb higher due to minute amounts moisture yet left in the system.
    Therefore, how well it holds the pulled down microns is more of a test on whether the refrigerant system is sufficiently evacuated.

    Always do a nitrogen pressure test prior to evacuation procedures.

    This is how some procedures are performed:
    When a system has been evacuated below 500 microns, the pump is valved-off with the micron gauge connected, if the vacuum rises to 1500 microns and stops, there is moisture remaining in the system. If it rises above 1500 microns & continues to rise there is a leak. You should allow at least 15 minutes after the pump has been shut off for an accurate micron gauge reading. When a system will not evacuate below 1500 microns there is either a lot of moisture in the system or there is a refrigerant system leak. Keep the oil changed in the vacuum-pump & make sure it is working properly.

    The R-410A systems ought to be double evacuated; some even use a triple evacuation procedure like is used on low-temp systems.
    Purging with dry-nitrogen prior to evacuation & purging between pump-downs helps speed-up the evacuation process.

  5. #25
    Join Date
    Sep 2002
    Location
    Northeast Ohio
    Posts
    4,890
    Post Likes
    The freeze stat is not the answer when you have a PROBLEM, which you do. You will end up doing a lot more damage to her system by allowing it to cycle on and off while all the time it is low on refrigerant. If your current HVAC company can't properly identify and fix the problem(s), fire them and hire a company that is competent. Pressure testing and properly evacuating a system is the most basic of refrigeration procedures. It does not take fancy, exotic, super expensive equipment. Any company installing AC equipment MUST have the tools AND the expertise to do these things. No wiggle room here, zero, nada, zilch, NONE.
    A good HVAC tech knows how, an educated HVAC tech knows why!

    DEM


  6. #26
    Join Date
    Jul 2011
    Location
    Delaware
    Posts
    41
    Post Likes
    Thread Starter
    Quote Originally Posted by heaterman View Post
    The freeze stat is not the answer when you have a PROBLEM, which you do. You will end up doing a lot more damage to her system by allowing it to cycle on and off while all the time it is low on refrigerant.
    Thanks for the pos. I have thought about that cycling issue, and I spent an hour trying to find a freeze-stat with a simple warning lite that my mother could see, but I did not find anything with a light. But I wondered how much system damage was caused in building up 6" of ice on the evaporator? I assume it would try to run and then kick out, but perhaps not?

    If your current HVAC company can't properly identify and fix the problem(s), fire them and hire a company that is competent. Pressure testing and properly evacuating a system is the most basic of refrigeration procedures. It does not take fancy, exotic, super expensive equipment. Any company installing AC equipment MUST have the tools AND the expertise to do these things. No wiggle room here, zero, nada, zilch, NONE.
    I agree. Looking at the Work Orders, they did a vacuum test after the 1st leak fix (compressor replaced), but there was no comment about a vacuum test on the 2nd leak fix (suction line by the compressor).

    The compressor was sent back to the factory, and I'm in the process of asking them to do a failure analysis on this 1 year old compressor that leaked at the seal for the power line.

    Regarding a new company, it's easy for a pro like you to quicky come up with a better company. But she is 1000 miles away, and I'm a professional mechanical engineer that actually does hard core engineering, vs doing the typical cook-book code reading and/or managing, but I've only learned about H&V stuff here, and dealing with the contractor, Atzil. The local distributer, Gemaire, is giving me a list of companies that they feel would result in better system reliablility.

    One question: they are supposed to do a vacuum test after breaking the line. How long is it supposed to hold 500-1000 microns of HG, and what if any is an acceptable vacuum drop in the test period ??

    Thanks for the help.

  7. #27
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Pressure testing with a nitrogen/refrigerant mix can at times find leaks that a vacuum test can't. Also, with the vacuum test, the tech won't know WHERE the leak is, only that he's not holding a vacuum. So if he detects a leak with a vacuum, what does he then have to do? Gas up the system and go hunting. Might as well do that first, find all leaks possible, and THEN pull a vacuum. Always better to do things in the right order vs. doubling back and eating up time and money.

    If a system is tight, a tech looks for the following reality when pulling a vacuum:

    System should hold at 500 microns or lower. If microns rise, level off, and hold, system has moisture in it and requires more evacuation. If system micron level rises to atmospheric, there's a leak.

    Freeze stat is not the answer. Allowing a system to run low on refrigerant, even if it still appears to cool the house, puts the compressor under stress. If the compressor can't be cooled sufficiently by suction gas, and oil return to the compressor becomes spotty, compressor life will be short and it will die an ugly death.
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  8. #28
    Join Date
    Jul 2011
    Location
    Delaware
    Posts
    41
    Post Likes
    Thread Starter
    Thanks for the detailed explanation Shophound. I now have enough background knowledge to ask the supervisor what was done.

    And collectively, HVAC-Talk has got me off the freeze-stat theme .... doh!

    Kevin

  9. #29
    Join Date
    Oct 2006
    Location
    The Beach
    Posts
    1,025
    Post Likes
    Good for you. Installing a freeze stat will not solve the problem. Just get the system fixed and your mother will be cool.
    Blue Fox

  10. #30
    Join Date
    Jul 2011
    Location
    Delaware
    Posts
    41
    Post Likes
    Thread Starter
    Vaccum Meter

    I talked to the tech super yesterday. I asked about the final vacuum test, and he said they pull a vacuum for about 30 minutes, followed by a 10 min hold ... if no change it's leak free. I then mentioned that microns of HG are a very small unit of measure. He started avoiding my statement, then for whatever reason, he offered up that they don't have micron meters, and they use the "meters from when Freon was used".

    Any idea what unit those meters read out? inches HG?

    As long as it is stable for 10 minutes, is that enough to verify no leak, using the old meters?

    Thanks a bunch guys!

    Kevin

  11. #31
    Join Date
    Jun 2006
    Location
    Richmond, VA
    Posts
    4,184
    Post Likes
    Quote Originally Posted by KevimK2 View Post
    Vaccum Meter

    I talked to the tech super yesterday. I asked about the final vacuum test, and he said they pull a vacuum for about 30 minutes, followed by a 10 min hold ... if no change it's leak free. I then mentioned that microns of HG are a very small unit of measure. He started avoiding my statement, then for whatever reason, he offered up that they don't have micron meters, and they use the "meters from when Freon was used".

    Any idea what unit those meters read out? inches HG?

    As long as it is stable for 10 minutes, is that enough to verify no leak, using the old meters?

    Thanks a bunch guys!

    Kevin
    no, sounds like they just use their compound guages- which won't tell you a thing.

    sometimes it takes longer than 30 min to get less than 500 microns.....
    I wish I had a $1.00 for every response I deleted.....

    "Decidedly Superior in a twisted pathetic way".....

  12. #32
    Join Date
    Jul 2011
    Location
    Delaware
    Posts
    41
    Post Likes
    Thread Starter
    Guys, I'm in the process of finding a new contractor, for servicing my Mom's 3T AC system in Florida.

    And I appreciate all the help so far, but they have pulled a new one on me/Mom.

    She lost cooling 2 times in 3 weeks last month:

    She lost cooling on the 10th, restored on the 12th, and lost cooling again on the 15th, restored on the 17th.

    Last Sunday, Mom had to run the system all afternoon, non-stop, to maintain 80 degrees on a 88 degree day. The delta between the inlet and outlet flow was only 10 degF, vs the usual 16 degF + delta that quickly cools the house.

    Now the wierd stuff:

    On this past Monday, a bright new tech, old Rick, came out to find the problem. He said the dryers that were installed a few weeks ago had a high pressure drop across them. He thought this was due to too much heat during the solder installation. I asked him to check for Ice on the evaporator, and he said he was too old to go up the rickity drop-down stairs.

    He wrote down on the call sheet that new dryers were needed, as he discussed with me on the phone. And there was no mention of evaporator trouble on the call sheet.

    I call Mom on Tuesday, when the new dryers were going in. Another tech answers the phone and says he is installing a new evaporator. He has already done the dryers.

    I call the manager "SAM" Saten. I asked why a new evaporator was being installed, he coul not sat, but nhe did say all or nothing, so I had to say "all" to get my Mom's AC working again, but I had a bad feeling about changing out a major organ of the cooling system. I was right ... they coul not get the old evap down the fold down steps in the garage, so they were afraid to bring the new evap upstairs. They gave up and left my Mom with still no AC !!!!!

    Question

    Is it possible that the manager just inflated the warrenty work on this job, by just arbitrarily adding that a new evap coil was needed, that was only 8 months old, to fatten his pocket ???

    I appreciate your professional opinions about this problem where the tech said it was not needed, but the manager added it on anyways.

    Thanks a bunch,

    Kevin

  13. #33
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    We don't make money on warranty jobs. And the older guy wouldn't even look at the evap so how could he say one way or another?

  14. #34
    Join Date
    Jul 2011
    Location
    Delaware
    Posts
    41
    Post Likes
    Thread Starter
    The system was not loosing 410A, and the evap was only 8 months old. He felt the dryers were the only problem, based on the pressure drop across them.

    Is it possible that on issue begot the other? Like the bad dryers some how messed up the evaporator? It does not work the other way, as he determined how the excessive heat (lack of using a heat sink, like wet cloth) damaged the dryers when they were installed about 3 weeks ago.

  15. #35
    Join Date
    Jul 2011
    Location
    Delaware
    Posts
    41
    Post Likes
    Thread Starter
    Quote Originally Posted by SBKold View Post
    We don't make money on warranty jobs ...
    If the work load is light for a couple of days, I though major warranty work would be welcomed.

  16. #36
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Quote Originally Posted by KevimK2 View Post
    If the work load is light for a couple of days, I though major warranty work would be welcomed.
    That's not really the issue. What is the issue is that nobody so far appears to have done a thorough investigation...although measuring a pressure drop across a drier was a good move. However, if a drier plugs up, that's a sign someone working on the system in the past may not have used proper procedures regarding brazing and/or evacuation (vacuuming).

    But now you're saying that this crew removed the old evaporator BEFORE they realized they couldn't get the replacement up the attic access stairs? Or did they realize that fact prior to removing the old evaporator?

    There's no reason to change an entire evaporator coil if it's not leaking. If there's a restriction it will likely be in the metering device just prior to the evaporator, since it is the smallest portion of the entire refrigerant loop other than the driers, which are actually filters with desiccant included.

    If by some miracle the parade of techs cycling through your mother's system get the refrigeration portion of her system working perfectly, and the evaporator STILL freezes up, then that's an airflow problem, period. Getting that resolved will mean finding somebody who understands duct design and layout, who is a person as rare as hen's teeth, it seems.
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  17. #37
    Join Date
    Jul 2011
    Location
    Delaware
    Posts
    41
    Post Likes
    Thread Starter
    Quote Originally Posted by Shophound View Post
    That's not really the issue. What is the issue is that nobody so far appears to have done a thorough investigation...although measuring a pressure drop across a drier was a good move. However, if a drier plugs up, that's a sign someone working on the system in the past may not have used proper procedures regarding brazing and/or evacuation (vacuuming).

    But now you're saying that this crew removed the old evaporator BEFORE they realized they couldn't get the replacement up the attic access stairs? Or did they realize that fact prior to removing the old evaporator?
    Yes, they removed the 8 month old evaporator before they brought up the new evaporator. I had begged Sam the boss from Heck, not to mess with the evaporator, because nobody said it was bad, and ther was a high probability that they, Axtil, will create new problems in the process.

    There's no reason to change an entire evaporator coil if it's not leaking. If there's a restriction it will likely be in the metering device just prior to the evaporator, since it is the smallest portion of the entire refrigerant loop other than the driers, which are actually filters with desiccant included.

    If by some miracle the parade of techs cycling through your mother's system get the refrigeration portion of her system working perfectly, and the evaporator STILL freezes up, then that's an airflow problem, period. Getting that resolved will mean finding somebody who understands duct design and layout, who is a person as rare as hen's teeth, it seems.
    We already suffered from 2 of the 3 years this new Rheem system has been running, due to low airflow. It eventual caused so much vibration at the compressor that is shook all the outdoor unit's anchor bolts out of the tapped holes in the anchors ... all but one of the four bolt were dancing on the floor of the outdoor unit. I used the excellent install instructions, and determined that when they installed my Mother's old simple analog thermostat after the 1st year of operation, they forgot to change the dip switches on the air handler, so she never ran on the high speed for 2 years, and was constanty beating on the compressor.

  18. #38
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Quote Originally Posted by KevimK2 View Post
    Yes, they removed the 8 month old evaporator before they brought up the new evaporator.
    Unbelievable. So what has happened in eight month's time that the evaporator in the attic can fit through the access hole but the one that is supposed to replace it cannot fit?


    We already suffered from 2 of the 3 years this new Rheem system has been running, due to low airflow. It eventual caused so much vibration at the compressor that is shook all the outdoor unit's anchor bolts out of the tapped holes in the anchors ... all but one of the four bolt were dancing on the floor of the outdoor unit. I used the excellent install instructions, and determined that when they installed my Mother's old simple analog thermostat after the 1st year of operation, they forgot to change the dip switches on the air handler, so she never ran on the high speed for 2 years, and was constanty beating on the compressor.
    I doubt just running the blower on low speed caused her compressor to strain at the bolts. Sounds to me like a gross overcharge or a system full of air and moisture vs. a mere dip switch blunder. And now they're chasing their own tails without ever sitting down long enough to target the source of ALL of your headaches and correct it. If they don't find the core problem, stand by for lather - rinse - repeat.
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  19. #39
    Join Date
    Jul 2011
    Location
    Delaware
    Posts
    41
    Post Likes
    Thread Starter
    One correction where I was not clear enough: They removed the 8 monnth old evaporator for reasons unknown (it was not leaking), and they left it in the attic, after they found that they could not figure how to get it down the typical folding stairs from the garage ceiling. That stairway is how the 8 month old evaporator was put in the attic. They would not attempt to bring the new (allegedly identical) evaporator up the stairs and risk damaging it, until they figured out how to get the old one down.

    Bottom line, going on 2nd day of no-cooling for my 89 yo Mom, due to problem installing a new evaporator that may not have been needed! Doh!

  20. #40
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    I thinking we need a CODE that demands a proper sequence be followed when installing & also when doing Energy Efficiency work; perhaps with some kind of independent follow-up checking system.

    Far too many customers are getting obscene install & service work.
    Customer's also need education concerning these procedures.

    Wisconsin's (R) governor Scott Walker is implementing a workforce SKILLS training program, with some money even allocated to K-12 students.

    We need a very high % of HVAC folks RETRAINED to meet New Higher Standards of Performance!

    If our elected reps & us HVAC folks along with everyone in the media would began to explain the tremendous economic stimulus that would occur were there to be this kind of useful high-utility-content on Radio & Television; also, linking to Internet Videos/Audios; plus links to local forums, the economy & jobs would begin to take-off...

    Our World is trying to lower our fossil fuel carbon pollution...by investing wisely, everyone can save a lot on their utility bills while helping to solve a multiplicity of the core economic problems facing our World; a mutual win/win/win, reducing budget deficits & prospering everyone...

Page 2 of 3 FirstFirst 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •