Thread: Duel Evaporators Defrost termination

  1. #1
    Join Date
    Jul 2009
    Location
    Zephyrhills Florida
    Posts
    89
    Post Likes

    Confused Duel Evaporators Defrost termination

    I have a walk in freezer with 2 Witt evaps. Both evaps have 3 terminal adjustable defrost termination stats. Not sure how these stats are suppose to work in a duel evap system. Does one stat just disable heaters on it's own evap temp rise and the other stat energize coil in defrost timer to terminate defrost cycle early or should both stats be capable of terminating defrost at the defrost timer? Or should both stats just disable heaters in their evaporators therefore forcing the defrost cycle to go on as set without heaters until end of cycle. My understanding is that these stats close on temp rise to energize coil in defrost timer so I don't see how they could disable heaters in the heater circuit. I'm confused just asking this question. I don't think I have a problem here I am just wondering if I have to deal with this someday. Thanks.
    Happiness is a bloodtrail in the snow. If it's beer can cold your too old.

  2. #2
    Join Date
    Mar 2007
    Location
    tx
    Posts
    1,109
    Post Likes
    Does your defrost clock have a solenoid in it to kick it back into freeze and terminate the defrost? If so, they may be wired to only kill the heater thier own coil. if your clock has the ability to terminate defrost by the soleniod, then and can be done a couple of other ways.
    Bad information is worse than no information at all.

    There are three kinds of people in this world. Those who can count and those who can't!

  3. #3
    Join Date
    Mar 2007
    Location
    tx
    Posts
    1,109
    Post Likes
    I read your post better, now let me try again. You have a defrost termination solenoid that takes you out of defrost and back into a freeze cycle. The t-stats force it out of defrost and kills the circuit to the heaters which is coming thru the clock (normally open contacts). In a freeze, we are running the refrigeration off of the clock thru the normally closed contacts. More than likely, they (defrost termination t-stats) are run in series circuit with the solenoid bacause we want them both closed to energize the solenoid and terminate defrost.
    Bad information is worse than no information at all.

    There are three kinds of people in this world. Those who can count and those who can't!

  4. #4
    Join Date
    Apr 2001
    Location
    Camel City, NC
    Posts
    6,234
    Post Likes

    Witt

    Maybe found what you need in the educational forums. Start on page 12 for multiple evaps. wiring
    http://69.41.183.10/documents/SuperEasy%20IOM.pdf
    Be safe not fast. body parts don't grow back

  5. #5
    Join Date
    Sep 2007
    Location
    NH
    Posts
    1,424
    Post Likes
    They get wired in series back to the X terminal off the time clock which will terminate defrost when powered. The clock will stop defrost even if there is more time left when power comes back on X. Just use a differnt leg of power then what ever is powering one side of the defrost solenoid (normally L1)...I think...

  6. #6
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    4,021
    Post Likes
    Check out the manual that Selfemployed posted. You can use 2 relays that won't allow L2 back to the clock soleniod until both defrost are terminated. Cool

  7. #7
    Join Date
    Jul 2009
    Location
    Zephyrhills Florida
    Posts
    89
    Post Likes
    Thread Starter

    Smile

    Quote Originally Posted by selfemployed View Post
    Maybe found what you need in the educational forums. Start on page 12 for multiple evaps. wiring
    http://69.41.183.10/documents/SuperEasy%20IOM.pdf




    Thanks everyone this download is just what I needed.
    Happiness is a bloodtrail in the snow. If it's beer can cold your too old.

  8. #8
    Join Date
    Mar 2007
    Location
    tx
    Posts
    1,109
    Post Likes
    Quote Originally Posted by surenuff View Post
    I read your post better, now let me try again. You have a defrost termination solenoid that takes you out of defrost and back into a freeze cycle. The t-stats force it out of defrost and kills the circuit to the heaters which is coming thru the clock (normally open contacts). In a freeze, we are running the refrigeration off of the clock thru the normally closed contacts. More than likely, they (defrost termination t-stats) are run in series circuit with the solenoid bacause we want them both closed to energize the solenoid and terminate defrost.
    like I said.
    Bad information is worse than no information at all.

    There are three kinds of people in this world. Those who can count and those who can't!

  9. #9
    Join Date
    Jul 2009
    Location
    Zephyrhills Florida
    Posts
    89
    Post Likes
    Thread Starter

    Smile

    Quote Originally Posted by surenuff View Post
    like I said.



    I think this is what I have. Thanks Surenuff.
    Happiness is a bloodtrail in the snow. If it's beer can cold your too old.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •