Thread: 410 A Help!

  1. #1
    Join Date
    Jul 2008
    Posts
    24
    Post Likes

    410 A Help!

    What is the difference in temp from supply and return air in 410 A. Like the R22 is typically 20 degrees sifference. What is the difference in 410A? What should they do? I have put a 410A in a restauraunt and it is not cooling.

  2. #2
    Join Date
    Dec 2007
    Location
    Ohio
    Posts
    2,931
    Post Likes
    Depends on what your other temps are really...what's the question again?
    I need a new signature.....

  3. #3
    Join Date
    Jan 2008
    Posts
    2,904
    Post Likes
    There is no expected difference in temperature differential between the two. We shoot for 20 degrees with either one.
    "Hey Lama, hey, how about a little something, you know, for the effort." And he says, "there won't be any money, but when you die, on your deathbed, you will receive total consciousness." So I got that goin' for me, which is nice. - Carl Spackler

  4. #4
    Join Date
    Sep 2007
    Location
    KY
    Posts
    79
    Post Likes
    did you change evap?
    did you change refrig lines or flush?

    R-410 is just like any other refrigerant. Understanding your PTR and the refrigeration cycle is key.
    I'm lost, I've gone to look for myself.

  5. #5
    Join Date
    Jul 2008
    Posts
    24
    Post Likes
    Thread Starter

    Confused

    THIS IS WHATS HAPPENING I HAVE INSTALLED 3- 5TON 410A HEIL PACKAGE UNITS .IN A 2500SQ FT OLD BRICK BULDING THAT HAS COMPLETLY REMOLDED,AND HAS BEEN MADE INTO A RESTARANT/BAR.HOWEVER THE BULDING HAS NO CELING JUST EXPOSED RAFTERS AND DUCT . . WELL WITHOUT WRITING AN ENTIRE BOOK ITS YOUR TYPICAL OLD DOWTOWN BULIDING.ITS HAS BEEN WORKING FINE FOR THE LAST THREE MONTHS. UNTILL THIS PAST TUESDAY SO I CHECKED ALL THE UNITS THEY WERE ALL RUNING .FINE BUT ALL T-STATS WERE SET AT 7O BUT AVERAGE TEMPERATURE WAS 77.SO I DISCOVED THAT THE 410A HEIL UNITS HAVE 1 COMPRESSOR BUT 2 STAGES OF COOLING SO I JUST TIED Y2 AT THE PACKAGE UNIT TO Y1 AND REMOVED FILTERS THAT HADE BEEN LEFT INSIDE INSIDE UNIT FROM FACTORY.THEY LOOKED SOMEWHAT DIRTY AND THERE WERE ALL READY FILTERS INSIDE BULDING SO DIDNT THINK WE NEEDED DOUBLE FILTERS.THE OWENERS SAID THE UNIT WORKED GREAT AFTER THOSE2 CHANGES 4- 3 DAYS ANYWAY. NOW HOWEVER THERE NOT KEEEPING UP IT WAS 78 AT 6.00PM IM WONDERING WHAT THE HELLS SUDDENLY CHANGED. TO CAUSE THE WHOLE BULDING TO STOP COOLING I ONLY PUT THE 410A UNITS IN BECAUSE THEY WERE ALL OUT R22S THE DAY WE HAD TO PUT UNITS ON ROOF.IM STUMPED OR STUPID .I GUESS ITS THE LATER IM LOOKING FOR ANY ANSWERS .ALL DUCT WORK WAS INSTALLED TO ENGINNERS PLANS IM LOST WITH THE 410A

  6. #6
    Join Date
    Jul 2008
    Location
    Denver, CO
    Posts
    4,379
    Post Likes
    Check your super heat, ambient temp.,Room temp., Pressures, sub cooling, humidity and temperature drops across the evaporator. One must know all this information before a diagnosis can be made

  7. #7
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    is the make up air working for the venthood

  8. #8
    Join Date
    Apr 2007
    Posts
    626
    Post Likes
    Hard to say with the info given. But one thing I can tell you for sure, is the R410A is not the cause.

  9. #9
    Join Date
    Mar 2001
    Location
    North Carolina
    Posts
    428
    Post Likes
    What the heat load call for? was all equipment, lighting, ventilation and people included for peak hours? if so most likely the hood's makeup air or lack of would be the most common problem with restaurants.

  10. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    What was the temp on the roof when these units would cool.

    Did you check to see if these units meet the engineers sensible cooling specs.

  11. #11
    Join Date
    Jan 2008
    Location
    s chester county,pa
    Posts
    157
    Post Likes
    as said it is nothing to do with the units. do you have economizers on any of them? check your damper minimum position and check that make up air fan is working properly

  12. #12
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes

    How many people live in this restaurant?

    .
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  13. #13
    Join Date
    Jul 2008
    Posts
    24
    Post Likes
    Thread Starter
    The make up air fan is working properly. The system was installed by engineers specs. I believe there is a maximum of 60 people in the place.

  14. #14
    Join Date
    Feb 2007
    Location
    Las Vegas,NV
    Posts
    759
    Post Likes
    Quote Originally Posted by dholladay View Post
    The make up air fan is working properly. The system was installed by engineers specs. I believe there is a maximum of 60 people in the place.

    Just found your problem, system was installed by engineers specs!

  15. #15
    Join Date
    Jul 2008
    Location
    Alabama
    Posts
    682
    Post Likes
    Quote Originally Posted by dholladay View Post
    .THE OWENERS SAID THE UNIT WORKED GREAT AFTER THOSE2 CHANGES 4- 3 DAYS ANYWAY. NOW HOWEVER THERE NOT KEEEPING UP IT WAS 78 AT 6.00PM IM WONDERING WHAT THE HELLS SUDDENLY CHANGED. TO CAUSE THE WHOLE BULDING TO STOP COOLING :
    Sounds like something else broke. You did say they were Heil, right??

  16. #16
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    What was the sensible and latent capacities the engineer speced.
    How much fresh air is being brought in.

    Between the people and hot food, you have around 6.5 tons load.
    About another 2 to 3 tons in fresh air.
    Then you got lighting load yet. Plus the structures heat gain.

    15 tons is cutting it close.

    Might be that 15 tons can't handle the peak loads.

  17. #17
    Join Date
    Jul 2008
    Location
    Pittsburgh PA
    Posts
    37
    Post Likes
    Quote Originally Posted by catmanacman View Post
    is the make up air working for the venthood
    Good call cat man!

  18. #18
    Join Date
    Jun 2008
    Location
    Morgantown, WV
    Posts
    136
    Post Likes
    Quit screaming and get rid of typing in all caps. It's not only rude it's very hard to read.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •