    but I hope someone can.

    It's a Rheem RHPN-HM2421JC A/H with electric heat, installed vertical in a closet.
    The cond unit is a RARL-024JEZ two stage.
    Thermostat is a Rheem TST305.
    T-Stat is configured for two stage cooling, and no daily program.

    The customer says it runs fine all day but stops cooling somewhere between 2am and 5am. He says he looks out the window and can see the cond fan running and hears the compressor, and reach his hand to a grille nearby and it's blowing warm air.

    Then around 6am it's cooling fine again. It happens every night.
    There is no power company call box that would shut it off.

    I have checked everything, I won't even bother to list it all because of the specific time that it blows warm air. It obviously works when I'm there.

    We can have a 95 degree day and it works fine all day, but had this problem the night before and the next night.

    The board in the cond unit reads no codes.

    The guy is in his 80's or close to it I would guess.

    What do you think?

  2. #2
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    2,810
    Post Likes
    Txv for a metering device? If so there's not much else that could have the compressor and fan operating without cooling,not intermittently at least.

  3. #3
    Join Date
    Jun 2012
    Location
    Northern NV
    Posts
    3,404
    Post Likes
    Condensing unit on the west side of the home and in the sun in these hours? Could be thermal in nature and compounded by an overcharge. Either that or something is parking on the fan grille every afternoon about that time of the day. Some critters have strange behaviors. Ants in contactors, never have figured out that attraction....

  4. #4
    Join Date
    May 2005
    Location
    South
    Posts
    735
    Post Likes
    Thread Starter
    Quote Originally Posted by Juan Madera View Post
    Condensing unit on the west side of the home and in the sun in these hours? ....
    Well no, here in FL the sun isn't out between 2am and 5am

    How could it be anything mechanical when it fights 95 degree heat fine but blows warm between 2am and 5am?

  5. #5
    Join Date
    Nov 2009
    Location
    Northwest Illinois
    Posts
    283
    Post Likes
    I think the electric heat is kicking on some how and that would explain the warm air. Maybe the stat is messed up causing that problem.

  6. #6
    Join Date
    Aug 2008
    Location
    Bel Air MD
    Posts
    35
    Post Likes
    Could you try unhooking the electric heat just to eliminate that as a possibility?

  7. #7
    Join Date
    Jun 2012
    Location
    Texas Hill Country
    Posts
    53
    Post Likes
    Sounds like an old man with blood circulation problems.

  8. #8
    Join Date
    Jun 2012
    Location
    Northern NV
    Posts
    3,404
    Post Likes
    oops.... missed the AM part. Was thinking PM...

  9. #9
    Join Date
    Jun 2012
    Location
    East tx
    Posts
    164
    Post Likes
    I was also thinking a wiring issue with heat on...possibly the tsat set for heat pump accidentally? Or there is a crossed wire? Or even a relay or sequencer that's getting a signal..if he is telling the truth and not imagining the condenser running...maybe the stat is satisfied and fan in circulate mode.

  10. #10
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    Quote Originally Posted by HPpro View Post
    Could you try unhooking the electric heat just to eliminate that as a possibility?
    Unhooked the w2 from condensor board to eliminate that as a possibility.

    And see if Rev valve is energizing or if its just strips

  11. #11
    Join Date
    Oct 2007
    Location
    Broward County, FL.
    Posts
    675
    Post Likes
    Could it be moisture in the system freezing in the txv?

    At what temp does he set the stat at night?
    I miss you mom and dad.

  12. #12
    Join Date
    Apr 2012
    Posts
    44
    Post Likes
    How much heat gain does this place have that he notices it not cooling for couple hours in middle of night.

  13. #13
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by SBKold View Post
    Unhooked the w2 from condensor board to eliminate that as a possibility.

    And see if Rev valve is energizing or if its just strips
    I was thinking rev valve as well.

    Possibly hanging up intermittently



  14. #14
    Join Date
    Jun 2002
    Location
    Dacula, GA
    Posts
    23,718
    Post Likes
    Swap thermostats and see what happens. Just use a basic one. I would also throw the breaker on your electric heat. Won't need it till January if then if it is Daytona or further South. Also JP and others he did say "electric heat". This is Florida. South of Jacksonville they don't use that many heat pumps. Just air handlers with electric heat. Hey and if they have a HP they normally wouldn't have a heat strip to back up the HP which is rarely used. That's all folks. LOL. Thank you very much
    Last edited by glennac; 06-22-2012 at 08:58 PM.
    "I could have ended the war in a month. I could have made North Vietnam look like a mud puddle."

    "I have little interest in streamlining government or in making it more efficient, for I mean to reduce its size. I do not undertake to promote welfare, for I propose to extend freedom. My aim is not to pass laws, but to repeal them. It is not to inaugurate new programs, but to cancel old ones that do violence to the Constitution."
    Sen. Barry Goldwater

  15. #15
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    I was thinking rev valve as well.

    Possibly hanging up intermittently
    Well on rheem its piped energized in heat. So something would have to trigger it. Defrost board shouldn't as it opens Rev valve circuit. And should stop fan.

    I too have a problematic unit I need to go back to. It is a trane rather. I do think mine energized w2 stopped cond fan and felt it needed to defrost in cool.

  16. #16
    Join Date
    Nov 2009
    Location
    Northwest Illinois
    Posts
    283
    Post Likes
    I would rule out the rev valve seeing as its not a heat pump. Disconnect the W1 from the air handler or turn off the breaker for the electric heat.

  17. #17
    Join Date
    May 2005
    Location
    South
    Posts
    735
    Post Likes
    Thread Starter
    It's not a heat pump.
    I did think of the heat coming on, last time I was there I did think about going right to the source with the heat and taking the high voltage wires off.

    The first time I was there I replaced the thermostat because the LED didn't light properly and it was under warranty.

    I did talk to the guy recently, he said he keeps it at 76 during the day and turns it up to 78 at night (quite the opposite of what most people do), this might be a heat gain issue, as in it hits 78 between 2am and 5 am. I told him to leave it at 76 tonight.

    The system has to be working right, he has a ton of eastern exposure so when the sun rises, around 6am, when he says it starts to work again, well I don't know. The cond unit takes a direct hit from the morning sun, right when he says it starts working.
    He has just about no western exposure so I'm guessing the house is out of the sun by 5 pm or 6pm.

    Quote Originally Posted by schr8er View Post
    Sounds like an old man with blood circulation problems.
    This is why I mentioned he's old. Years ago I was getting repeat calls like this. It would get hot at night, the guy told the office to not send me out anymore, two days later he died in his sleep.

  18. #18
    Join Date
    Aug 2011
    Posts
    12
    Post Likes
    About 10 years ago I ran across a similar problem. Elderly woman complained her a/c would blow warm air. 2 visits and found nothing wrong, other than a slightly dirty condenser coil. 3rd call and I sat her down and had her explain to me EVERYTHING!. She neglected to tell me this would happen only at night and the outdoor unit she claimed was running. She lived in a manufactured home. Heat load was enough that the unit ran all day. At night the heat load would drop and the unit would cycle. What she thought was the c/u running was only the compressor (until it tripped on thermals). After cycling the cond fan motor countless times the problem showed up. A "dead spot" in the windings. It ran fine all day because it never cyled off. At night when it cycled the fan would occasionally stop in the wrong place and then lock up. As the early morning hours roled around the call for cooling would drop and the fan would free wheel a bit and fire back up in the daytime. She was also setting her t'stat higher at night. So it proved to be a bad cond fan motor

  19. #19
    Join Date
    May 2005
    Location
    South
    Posts
    735
    Post Likes
    Thread Starter
    This guy has a real good view of the cond unit, his house is built into a hill. In the front it looks like a one story, in the back it looks like a two story (if that makes sense). But I've looked at it and you can see the fan very good.

    But then again, at 2am I doubt theres enough light. Maybe I'll ask him how he can see the fan at night.

    This system does cycle during the day. I've been there at least four times before 11 am and the thermostat was satisfied.

  20. #20
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    Is it an auto changeover stat

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •