+ Reply to Thread
Page 3 of 4 FirstFirst 1234 LastLast
Results 41 to 60 of 77

Thread: oil pressure problem

  1. #41
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Post Likes
    Thread Starter
    gggg

  2. #42
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Post Likes
    Thread Starter
    gggg
    Quote Originally Posted by jayguy View Post
    low head pressure usually = low suction pressure. low suction pressure = low refrigerant flow rates. low refrigerant flow rates = poor oil return. poor oil return = no oil. no oil = 0 oil psid. < 10 psid = trip oil pressure switch. trip oil pressure switch = unhappy customer. unhappy customer = unhappy service tech.

    math is fun!

  3. #43
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Post Likes
    Thread Starter
    I like your math. I resemble that remark. I do not have low head nor do I have low suction therefor your great math doesn't solve my problem. When the unit trips it doesn't matter if it is 29 or 89 degrees. It trips when it takes a notion to no matter the ambient. I wonder if it is possible to have rod bearings worn enough to cause a oil pressure drop by letting too much oil escape too quickly. I say this because the oil pump pressure out put on start up is around 85 PSI and drops off to around 55 PSI in about 5 minutes.
    Quote Originally Posted by jayguy View Post
    low head pressure usually = low suction pressure. low suction pressure = low refrigerant flow rates. low refrigerant flow rates = poor oil return. poor oil return = no oil. no oil = 0 oil psid. < 10 psid = trip oil pressure switch. trip oil pressure switch = unhappy customer. unhappy customer = unhappy service tech.

    math is fun!

  4. #44
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by welling service View Post
    ...the oil pump pressure out put on start up is around 85 PSI and drops off to around 55 PSI in about 5 minutes.
    i think that this may be more of a key than first noted. this sounds like a compressor that is 'warming up' the oil/parts. crankcase heater working? does the net oil pressure stay the same after that?
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  5. #45
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Post Likes
    Thread Starter
    The NPOP stays around 15PSI and the CC heater is working. This unit has been running for a week now and hasn't tripped on anything. I hate this sneaky compressor.
    Last edited by welling service; 11-22-2012 at 01:22 PM. Reason: add thought

  6. #46
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by welling service View Post
    The NPOP stays around 15PSI and the CC heater is working. This unit has been running for a week now and hasn't tripped on anything. I hate this sneaky compressor.
    Do you have a rack controller or is it running on pressure controls?

    What's the rest of the oil system look like? Is it a turbashed oil system or a standard separator/reservoir/OCV type system?

    Could the oil float be sticking at the compressor? In the separator?

    While, technically, 15# is 'good enough' I'm not happy with it at all.

    If you've got 15# with a clean pickup screen, a proper oil level and a new oil pump that is properly installed, I'm quite suspicious of the bearing condition of that machine.



  7. #47
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Post Likes
    Thread Starter
    This system has no controls except for a defrost timer for each LLSV. It supplies 6 different open face cases with with no stats. It never shuts off. This system has 2 comp piped in parallel and only runs one at a time. The other comp never trips. It has a new seprator/reservoir and each comp has oil level controller. The oil seprator return cycles from hot to ambient so I know the seperator is working. I agree, I like a little higher net oil pressure also. I really leaning toward a bearing problem. I have recently replaced the other comp. It had a broken rod and the crankshaft was in pretty bad shape. I pulled the suction end bell and found a lot of copper dust and just plain ole crud caked on the windings. I inherited this system just system. The previous tech solved problems by using jumped wired around controls and fuses.
    Last edited by welling service; 11-22-2012 at 05:20 PM. Reason: Correction

  8. #48
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,205
    Post Likes
    welling

    you are really up against it here, but i admire your thoroughness. If that sump screen is ok, you have to have something internally wrong. you already tried an oil pump, and with a clean sump screen I have to say that you have a worn bearing there. I have seen a unit do this before, the oil was getting real hot and thinning out and causing this, by getting superheat undercontrol the problem went away. The unit had an old ragged out condenser coil as well. discharge temps were too high there as well. doesnt seem like you are having that issue though.
    since you had a massive failure in a parallel compressor, could you have debris from the old compressor that got into your common lube sytem?

  9. #49
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Post Likes
    Thread Starter
    very possible. I have changed the oil in both compressors twice. I really think it is worn bearings.

  10. #50
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    I'm in the worn bearing camp as well.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  11. #51
    Join Date
    Apr 2008
    Location
    Tucson, AZ
    Posts
    331
    Post Likes
    There are many reasons for oil fail. What is the superheat at the compressor? If it is low, below 20*, you may be getting flood back at times, which would explain broken rods. It could be intermittent as load changes. Liquid could feed to one compressor more than another because of piping. You will not always see foam. It will foam when suction pressure drops and boils off gas. If suction pressure is steady, no foam. I have seen many oil pumps changed; and in the process of pumping it down, they remove the liquid refrigerant from the crank case. They think they fixed it for awhile.
    If Superheat is real high, crank case is hot, the compressor could be getting hot and going off on thermal overloads, because the contactor is pulled in, it's still looking for oil pressure on the control circuit. It depends on how it's wired of course.
    The contactor or wire connections could be bad causing a thermal overload. Is it a mechanical or Sentronic oil safety? If Sentronic, the sensor could be bad, screen plugged, or the little o-ring could be bad that separates suction & oil pressure to get net oil pressure. It times out after 120 seconds below 9 psi, net, for Copeland.
    Other questions not necessarily for your problem: is the sight glass dirty at the half way point so it looks half full? Is there an oil separator working ? Are there oil level controls sticking or plugged or stuck open feeding one compressor too much causing loss of differential pressure from the separator-reservior.
    In a supermarket 60% of the time it's flood back, Sometimes it only floods coming out of defrost, sometimes only after product is real cold. Sometimes it drives me crazy. too late.

  12. #52
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Post Likes
    Thread Starter
    mccann, the OPC is mechanical, compressor SH is around 25 to 30 degrees, sight glass is clean, oil level controls are working just fine and I have never seen any flood back but I am not there 24 hours a day so it could be a possibility. Oil separator is new. I recently installed it because the old one was a welded unit and it did not work. You cannot do any maintenance on these welded units. The oil pressure control is tripped so I'm pretty sure it is an oil pressure problem. For some unknown reason it has been on line for almost two weeks and hasn't tripped. I only run one of these compressors at a time and the other compressor maintains a NPOP around 65 PSI.

  13. #53
    Join Date
    Apr 2008
    Location
    Tucson, AZ
    Posts
    331
    Post Likes
    You fixed it! When I check an oil fail, I list Suction, Discharge, Net oil pressure, superheat at compressor, oil level in each compressor, oil level in oil reservoir (if one), oil differential from oil reservoir to oil level controls (if any). Oil separator line is feeding, pick up screen is clean. oil level control screen is clean. Wires are tight, contactor is good Amp draw. no logging in heat reclaim, refrigerant level, what other work has been done lately. A always do something like change the contactor, then I go home and hope and perhaps got lucky. Good luck.

  14. #54
    Join Date
    Nov 2009
    Location
    Richmond, working under tarps
    Posts
    1,051
    Post Likes
    how are the safeties wired?

    If 1&2 terminals still see power and the compressor is off on another safety, the heater in the Oil failure will still be on.

  15. #55
    Join Date
    May 2003
    Location
    Charleston SC
    Posts
    172
    Post Likes
    Sounds to me like the bearings are worn, main and or rod bearings. The excess clearance between the crankshaft and bearings wont allow oil pressure to stay up.

    Coolairman

  16. #56
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Post Likes
    Thread Starter
    mccann I did all of the above except changing the contactor. Maybe I got lucky anyway. Side note: why does contactor always come up as a misspelled word on these post?
    Quote Originally Posted by mccann View Post
    You fixed it! When I check an oil fail, I list Suction, Discharge, Net oil pressure, superheat at compressor, oil level in each compressor, oil level in oil reservoir (if one), oil differential from oil reservoir to oil level controls (if any). Oil separator line is feeding, pick up screen is clean. oil level control screen is clean. Wires are tight, contactor is good Amp draw. no logging in heat reclaim, refrigerant level, what other work has been done lately. A always do something like change the contactor, then I go home and hope and perhaps got lucky. Good luck.

  17. #57
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Post Likes
    Thread Starter
    Sure looks that way to me also C_A_M.
    Quote Originally Posted by coolairman View Post
    Sounds to me like the bearings are worn, main and or rod bearings. The excess clearance between the crankshaft and bearings wont allow oil pressure to stay up.

    Coolairman

  18. #58
    Join Date
    Apr 2008
    Location
    Tucson, AZ
    Posts
    331
    Post Likes
    If we could spell, we wouldn't have to be doing this for a living. Ha ha.

  19. #59
    Join Date
    Nov 2009
    Location
    Richmond, working under tarps
    Posts
    1,051
    Post Likes
    If it where clearences, I find it difficult to believe that you would have not seen it, after 10mins of run time.
    Last edited by indy2000; 11-29-2012 at 08:51 PM. Reason: grammar

  20. #60
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by indy2000 View Post
    If it where clearences, I find it difficult to believe that you would have not seen it, after 10mins of run time.
    that is what i thought too.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

+ Reply to Thread
Page 3 of 4 FirstFirst 1234 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •