Results 1 to 17 of 17

Thread: Honeywell DH90 Whole House Dehumidifier

  1. #1
    Join Date
    May 2007
    Location
    Minnesota / Tennessee
    Posts
    19
    Post Likes

    Honeywell DH90 Whole House Dehumidifier

    We have two of these units installed in our home that don't seem to be working properly.

    We're located in eastern Tennessee. We have a dual fuel system to cover the main portion of our home. This consists of an American Standard heat pump and furnace, plus the Honeywell DH90 dehumidifier (and a Honeywell humidifier as well). The house is split into three zones. We have Honeywell VisionPRO IAQ thermostats in all three zones but the dehumidifier can only be set from the primary thermostat which is located in the basement level. We were told that the unit will actually operate based on the average humidity level of all three zones but we know no way at present of verifying that.

    We also have a completely separate HVAC system to cover a studio space located above our garage. This has an American Standard heat pump plus the Honeywell DH90 dehumidifier. This is a single zone controlled by the same type of Honeywell thermostat.

    For the past two weeks our local daytime temps have been in the 90s with high humidity, dropping to the 70s at night. We have the dehumidifier set to maintain a relative humidity of 50%. The actual humidity readings we're seeing, however, range from highs of 62% to 64% during the hottest part of the afternoon, down to as low as 38% around 11:00 p.m. (and for all we know it may drop even lower overnight). Our thermostats are set at 78 degrees, which is quite comfortable for us provided the dehumidifier is doing its job.

    One of our main reasons for purchasing the dehumidifier units was so we could maintain a stable level of humidity, but we're seeing fluctuations of 24%to 26% in a single day. The units cannot seem to keep up with humidity during the day, but they don't shut off when they reach the set level at night, either. Our installer had no answer for why this was happening and was going to research the problem (these are the very first whole-house dehumidifiers he has ever installed), but now he is simply not returning our calls.

    Is this large of a fluctuation in humidity levels to be expected? Isn't this bad for our wood floors, woodwork, etc.? Is there a solution?

    We'd greatly appreciate any insight the experts here could provide.

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Incorrect sizing. Incorrect installation, or set up.
    You may need to call in another contractor.

    Yes, its bad for your hardwood floors.

  3. #3
    Join Date
    Jun 2001
    Location
    DFW
    Posts
    685
    Post Likes
    Are you using the visionpro thermostats for your humidity measurments?

    Are you sure that the humidifier is staying off?

    As a bandaid approach until a real fix is found, I would turn the water off to the humidifiers to see if that helps.

  4. #4
    Join Date
    Jun 2008
    Location
    Perry Village, Ohio
    Posts
    164
    Post Likes
    I'm confused about something. If someone has a central cooling system, why would you need a dehumidifier as I thought the AC did all the dehumidifying?

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    An A/C can only dehumidify while its running. If it has a poor latent capacity. It will cool the temp quicker then it removes humidity.

    In a basement, there is not a big cooling load, so an A/C will cool the area to quick to remove enough moisture.

  6. #6
    Join Date
    May 2007
    Location
    Minnesota / Tennessee
    Posts
    19
    Post Likes
    Thread Starter
    I'm not sure what size units were put in, but we did have load calcs done for the house by a PE (this is new construction), so if I find out the unit size the PE would be able to tell us if they were correct, right?

    As far as installation, how should the dehumidifier be hooked into the supply/return for the system? Seems like there was some discussion and confusion about this on the part of our installer. The two units were initially hooked up differently and then one got changed, but I wouldn't be surprised if both were incorrect. The studio unit has already been replaced once as well.

    Yes, we are using the VisionPRO thermostats to tell us what the current humidity levels are, as well as to set the level we would like.

    I'm pretty sure the humidifiers aren't running, but it's definitely a good idea for us to double-check that. The thermostat allows us to set relative humidity separately for the humidifier and the dehumidifier and to turn simply turn either unit off completely.

    We don't like having a really cold house in the summer, which is what we'd have if we relied solely on the AC to remove the humidity. We're quite comfortable at 78 or 76 degrees with 50% relative humidity and we couldn't achieve that in this climate without the dehumidifier.

  7. #7
    Join Date
    Jun 2004
    Location
    4H: Hot, Humid Houston H.O.
    Posts
    3,304
    Post Likes
    Unsure whether this is a productive question, but how hard would it be to measure the dehumidifier condensate output for a day?

  8. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    It may be miswired.
    It could be that the IAQ is not configured right.

    There are several ways it can be installed. One is of coursed connected to the duct system.

    You can measure how much condensate it is remmoving. But if its low, without knowing how long it ran, you won't know if its under performing, or if it isn't receiving a call to run when it should.

  9. #9
    Join Date
    May 2007
    Location
    Minnesota / Tennessee
    Posts
    19
    Post Likes
    Thread Starter
    Good idea, but that would be difficult. The condensate pipe goes right into the drainage system for our gutters and downspouts.

    I'm wondering if it would be worthwhile to purchase a few humidity gauges to measure the actual relative humidity at various places around the house in case the thermostats are wrong. The only thing is, I knew right away the humidity was too high when I walked in my studio the first time -- I could feel the stickiness. That's when the thermostat said it was 64%.

  10. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    What zone control panel are you using.

  11. #11
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Quote Originally Posted by MandJ View Post
    We have two of these units installed in our home that don't seem to be working properly.

    We're located in eastern Tennessee. We have a dual fuel system to cover the main portion of our home. This consists of an American Standard heat pump and furnace, plus the Honeywell DH90 dehumidifier (and a Honeywell humidifier as well). The house is split into three zones. We have Honeywell VisionPRO IAQ thermostats in all three zones but the dehumidifier can only be set from the primary thermostat which is located in the basement level. We were told that the unit will actually operate based on the average humidity level of all three zones but we know no way at present of verifying that.

    We also have a completely separate HVAC system to cover a studio space located above our garage. This has an American Standard heat pump plus the Honeywell DH90 dehumidifier. This is a single zone controlled by the same type of Honeywell thermostat.

    For the past two weeks our local daytime temps have been in the 90s with high humidity, dropping to the 70s at night. We have the dehumidifier set to maintain a relative humidity of 50%. The actual humidity readings we're seeing, however, range from highs of 62% to 64% during the hottest part of the afternoon, down to as low as 38% around 11:00 p.m. (and for all we know it may drop even lower overnight). Our thermostats are set at 78 degrees, which is quite comfortable for us provided the dehumidifier is doing its job.

    One of our main reasons for purchasing the dehumidifier units was so we could maintain a stable level of humidity, but we're seeing fluctuations of 24%to 26% in a single day. The units cannot seem to keep up with humidity during the day, but they don't shut off when they reach the set level at night, either. Our installer had no answer for why this was happening and was going to research the problem (these are the very first whole-house dehumidifiers he has ever installed), but now he is simply not returning our calls.

    Is this large of a fluctuation in humidity levels to be expected? Isn't this bad for our wood floors, woodwork, etc.? Is there a solution?

    We'd greatly appreciate any insight the experts here could provide.
    Judging from the low evening %RH, the dehus must continue operating below their set-point. The range of humidity will not damage wood and is less than the winter/range.
    There is both dehumidification and humidification controls on the Honeywell stat. A simple mix-up in wires could account for the dehus not being controlled. The dehus must be operating continuously to achieve low %RH over-night when the a/c is not operating.
    Check to confirm that the a/c fan is in the "Auto" which reduces the %RH levels during high cooling loads. Duct leakage when the a/c fan is operating, a not cold enough a/c cooling coil, and excess fresh air ventilation could account for high day time humidity. Have A/C contractor contact the Honeywell Rep for assistance to resolve the problem. Regards TB
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  12. #12
    Join Date
    May 2007
    Location
    Minnesota / Tennessee
    Posts
    19
    Post Likes
    Thread Starter
    Quote Originally Posted by beenthere View Post
    What zone control panel are you using.
    Honeywell EnviraZone in the house.

    There are no zones in the studio -- 900 sq. ft. separate from the house, on it's own system but no zones necessary. That's where the humidity fluctuations are the worst. There is a Honeywell Equipment Interface Module.

    I'm thinking we really should have someone more knowledgeable than our installer come and take a look at our system, but how can we be sure to find someone who really knows about this stuff? Our installer seems to be just that -- a bare bones installer who wanted to put all our ductwork in the unconditioned attic until we nixed that plan. Is there any kind of professional designation or the like that we can look for? We're located just outside Knoxville, TN.

  13. #13
    Join Date
    May 2007
    Location
    Minnesota / Tennessee
    Posts
    19
    Post Likes
    Thread Starter
    Quote Originally Posted by teddy bear View Post
    Check to confirm that the a/c fan is in the "Auto" which reduces the &#37;RH levels during high cooling loads. Duct leakage when the a/c fan is operating, a not cold enough a/c cooling coil, and excess fresh air ventilation could account for high day time humidity. Have A/C contractor contact the Honeywell Rep for assistance to resolve the problem. Regards TB

    A/C fan is set on Auto. We also had a duct blaster test run and that came out okay. I've now also turned the humidifier setting to Off on both thermostats to see if that makes any difference. I notice that I cannot set the regular ventilation schedule on the thermostats. I can only set it for a one-time ventilation. The manual says the regular ventilation schedule is set by the installer, so it sounds like we should ask him what he set it for (if we ever hear from him again). What might be considered an excessive level?

    That's exactly what our installer said he was going to do -- talk to his Honeywell Rep. Only problem is that now he is not returning our phone calls. Makes me think he heard something he didn't want to hear, like perhaps incorrect installation. Our dehumidifiers are connected into our ductwork (not a separate system), but maybe not the right way.

  14. #14
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Try finding a contractor thru Honeywell.
    Select product, and enter your zip.

    http://yourhome.honeywell.com/Consum...torLocator.htm

  15. #15
    Join Date
    May 2007
    Location
    Minnesota / Tennessee
    Posts
    19
    Post Likes
    Thread Starter
    Quote Originally Posted by beenthere View Post
    Try finding a contractor thru Honeywell.
    Select product, and enter your zip.
    Ahhh, thank you! That's very helpful.

  16. #16
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Here a wiring diaghram for t-stat/dehu. Regards TB
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  17. #17
    Join Date
    May 2007
    Location
    Minnesota / Tennessee
    Posts
    19
    Post Likes
    Thread Starter
    Quote Originally Posted by teddy bear View Post
    Here a wiring diaghram for t-stat/dehu. Regards TB
    Thanks. This is very timely. Our general contractor finally got hold of the HVAC sub today, and he was muttering something about hoping he hadn't "got those two wires crossed" He's supposed to come out tomorrow to check things out.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •