Page 1 of 2 12 LastLast
Results 1 to 20 of 22

Thread: Need Advice- Oversized System & Bad Installation

  1. #1
    Join Date
    Jul 2008
    Posts
    4
    Post Likes

    Need Advice- Oversized System & Bad Installation

    I would greatly appreciate any advice from the forum on this. I bought a 2,800 sq ft house that was gutted, remodeled, and had an addition that doubled the house size (single story ranch). All new sheet rock, ceilings, insulation, windows, siding, plumbing, electrical, roof, and HVAC system. The builder used an HVAC contractor that never did a Manual J calc, and installed two 3-ton Goodman 16 Seer heat pump split systems with the condensers right next to the master bedroom window. I've been in the house for four months, now in middle of the hot South Carolina summer. I hired a third party, qualified HVAC contractor to give me a detailed report of the many installation deficiencies (too ugly and numerous to list) and he told me that the system is way oversized for the house.

    I bought HVAC-Calc and ran the Manual J calcs myself with great care. As an engineer and competent software user, I am confident that the software is giving me accurate results. Using this, HVAC-Calc specifies a 2.5 ton system for the Living Space zone, and a 1.5 ton system for the Bedroom zone (with conservative inputs for the infiltration, insulation, shading, windows, etc). The contractor installed a 3 ton system for the Living Space zone and another 3 ton system for the Bedroom zone. The BR zone system is double what it needs to be.

    I'm aware of the problems with having an oversized system, but the sad fact is that it is so common for HVAC contractors to oversize systems - how much of a case do I need to show negligence in order to force my builder to correct the problem and replace the system with the right sized units? When I told my builder and another Goodman contractor about the problems their first response was "it should be the right size units according to your home's square footage and using a rule of 1 ton per 500 sq ft."

    I would appreciate any helpful advice. Thanks in advance!

  2. #2
    Join Date
    Jul 2008
    Location
    Kansas
    Posts
    85
    Post Likes
    Quote Originally Posted by rb282 View Post
    When I told my builder and another Goodman contractor about the problems their first response was "it should be the right size units according to your home's square footage and using a rule of 1 ton per 500 sq ft."
    Dun dun dun.

    I shudder when I think of what other problems and spotty construction practices are scattered around your house. Seems to me "remodeled" more often than not usually means "we covered up everything bad with lots of paint and thick knock-down texture."

    I'm not really familiar with how you go back after builders for this kind of thing. But was there ever an agreement or contact outlining what you were getting? That would be a place to start. Otherwise, if you just bought the place "as-is" I doubt there is much you can do. Sounds like you've found one decent contractor though. Good luck. =\

  3. #3
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Get what you can out of the builder. After you exhaust that, Adding a whole house dehumidifier will control the indoor humidity regardless the size of the a/c. I have done that many times. All a/cs end-up over-sized during low/no cooling load. If you getting adequate fresh air during the low cooling conditions, all homes end up humid after a week. Adding 50-90 lbs./day of supplemental dehumidification keeps the entire home <50%RH. Most homes need 50-75 cfm of fresh air to purge indoor pollutants. During the winter the stack effect added to wind provides this fresh air. During the summer no stack effect and winds are intermitant. Regards TB
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Take some humudity readings and record them.
    Then have your lawyer send the builder a letter with a copy of the load calc, and your humidity readings.
    Your lawyer will know how to word it.
    You'll get a better response then.

  5. #5
    Join Date
    Apr 2007
    Location
    Tucson AZ
    Posts
    86
    Post Likes

    Lawyers are a lot more expensive than HVAC guys

    My rule is never sue anyone if its less than $10,000.
    I've eaten some bad stuff from contractors, but I'm convinced
    that's the smart thing to do.

    I'm sure you can have a smaller unit put in your bedroom
    area for a lot less than $10,000.

    I think you have a particularly hard case to make that the unit
    is oversized. Now if it was dangerous that might be another
    story. I've had dangerous.

    If this is the only issue you have I'd suggest forget sueing.

    However if you just discovered the whole house is built on
    quicksand and is going to subside its another story.

    Don't feed the lawyers!

    If you are really mad at the contractor you could threaten him
    with some bad publicity. I've had some success with this route.

  6. #6
    Join Date
    Aug 2005
    Posts
    20
    Post Likes
    I think Teddy Bear nailed this issue. The biggest problem from oversizing results in high humidity leading to mold and other health related issues. Take the $10,000 lawyer money and get a good contractor to install a whole house dehumidifier and feed yourself instead of the lawyer.

  7. #7
    Join Date
    Dec 2007
    Location
    Cedar Grove, Wi-Sheboygan
    Posts
    1,582
    Post Likes
    Here's is one suggestion you may want to entertain, Send a nice little letter to the orginal contractor stating your postion and with facts as TB suggested with taking RH readings to back your claim and ask the orginal contractor to give you the numbers of the manual J he used to size your equipment and then compare, if he didn't use manual J but used the "Rule of Thumb" to size your equipment then based on his menthod and your facts and load calc results are apples & organges then you have a case and at that point I would proceed to have him either replace what he installed with the proper size equipment or call another contractor to replace with proper size equipment and then file suit against the orginal contractor. Oh and you should not need to lawyer up if you have your facts and proof that he never properly sized the equipment in a civil matter or small claims.

  8. #8
    Join Date
    Mar 2008
    Location
    Jackson, NJ
    Posts
    176
    Post Likes
    Quote Originally Posted by superdave44 View Post
    I think Teddy Bear nailed this issue. The biggest problem from oversizing results in high humidity leading to mold and other health related issues. Take the $10,000 lawyer money and get a good contractor to install a whole house dehumidifier and feed yourself instead of the lawyer.
    Wait, I thought the primary problem from oversizing was wear/tear on the condenser?

    What is considered 'acceptable' humidity during air condition season? Also, humidity tends to rise so downstairs my be differant then upstairs (try running a humidifier in the winter in a house that has cathedral ceilings. Damn thing never turns off, but upstairs is pretty humid)

  9. #9
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Wear and tear.
    Excessive electric bills.

    A letter from a lawyer doesn't cost much. And can get results.
    Installing a dehumidifier, and saying all is well, is a bandaid.

    Selling dehumidifiers, is fine, but lets fix the real problem first.

  10. #10
    Join Date
    Jul 2008
    Location
    Rydal,Ga
    Posts
    84
    Post Likes

    DO NOT pay a lawyer for NOTHING !!!

    Quote Originally Posted by beenthere View Post
    Wear and tear.
    Excessive electric bills.

    A letter from a lawyer doesn't cost much. And can get results.
    Installing a dehumidifier, and saying all is well, is a bandaid.

    Selling dehumidifiers, is fine, but lets fix the real problem first.
    Easy fix... Find out if the HVAC guy has a legitimate state license...

    Go to the SOS or License Board Revocations and Fines Page.... and print off a couple of Cases where HVAC guys misrepresented their license obligation to others consumers. SEND IT TO THAT HVAC GUY !!!!
    Most in our state loose their licenses for a minimum of 2 Years and $10s of $1000s in fines.... For Bad Behavior, Hack Jobs..... & NO MANUAL Js

    Let him sweat $$$$.... He will call you REAL SOON!!! GUARANTEE!!!

  11. #11
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Thats presumming his state has a HVAC license.

  12. #12
    Join Date
    Jul 2008
    Posts
    4
    Post Likes
    Thread Starter
    Great suggestion, guys - please keep them coming and I will let you know how this works out. I did confirm that the SC building code clearly requires that the equipment "be sized based on building loads calculated IAW Manual J and other approved heating and cooling calculation methodologies." Duct systems have to be fabricated per Manual D, also per the building code. My town inspector gave me a copy of the code and he told me that the town can help force the builder to address the problem. The tricky part is going to be insisting that a different contractor performs the repairs and replaces the oversized unit and ducting. As far as I'm concerned the "three strikes and your out" rule applies with the original contractor who botched the install and two separate f/u visits to correct issues. In the last visit, to correct the problem of the freon lines being run across the attic service walkway, he just bent the line up, putting a big kink in the 3/4" suction line, which was hard too find under the insulation! This is just one of about a dozen examples of this horror story...

  13. #13
    Join Date
    Jun 2008
    Posts
    80
    Post Likes
    IMHO and as others have suggested, going the distance on the legal front just won't pay for itself.

    • Stern letter or two from you with the Manual J
    • Letter or two from your lawyer. Tip: have them cut and paste parts of your letters to save money.
    • Better Business Bureau
    • Attorney Generals Office
    • Any state licensing agency

    If all this fails to get results, replace the system and donate the old system to Habitat for Humanity for a tax write off, if you can.

  14. #14
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    The BBB isn't going to do anything.

  15. #15
    Join Date
    Jun 2008
    Location
    va
    Posts
    802
    Post Likes
    Big question???? Was this job or the whole job inspected? Was there permits taken out for the job? I have seen and been on jobs where permits were taken out for, but no inspections ever made through the job. Not even a final. Your local inspections department should have record of permits and inspections. If they did inspect and pass the job, you can go after them too. If there are no records of permits and/or inspections, invite them in!

  16. #16
    Join Date
    Jul 2008
    Location
    Rydal,Ga
    Posts
    84
    Post Likes

    You can't go after the inspector !!!!

    Quote Originally Posted by machery View Post
    Big question???? Was this job or the whole job inspected? Was there permits taken out for the job? I have seen and been on jobs where permits were taken out for, but no inspections ever made through the job. Not even a final. Your local inspections department should have record of permits and inspections. If they did inspect and pass the job, you can go after them too. If there are no records of permits and/or inspections, invite them in!
    You can't go after the inspector !!!!

    Now your talking about making a down payment for some lawyers girlfriend new apartment !!! (So she want tell his wife.....)

    The inspector is not at fault.... the inspector is not "Licensed" !!!

  17. #17
    Join Date
    Jun 2008
    Location
    va
    Posts
    802
    Post Likes
    Quote Originally Posted by kenny mac View Post
    You can't go after the inspector !!!!

    Now your talking about making a down payment for some lawyers girlfriend new apartment !!! (So she want tell his wife.....)

    The inspector is not at fault.... the inspector is not "Licensed" !!!
    Why not??? I have seen it done before. I have seen a few inspectors in the hot seat for passing things that should have never passed. You are correct on the inspector not being licenced, but If it was inspected, the locality or agency has to answer to or stand behind their "ruleing" or whatever you want to call it. That's part of the reason we have inspections. It gives us some backing in the event someone wants to complain. They have to answer to it as well.

  18. #18
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    In PA, 2 inspectors were sued personnaly, along with the township they worked for.

  19. #19
    Join Date
    Feb 2008
    Location
    Waffleville
    Posts
    10,486
    Post Likes
    Quote Originally Posted by superdave44 View Post
    I think Teddy Bear nailed this issue. The biggest problem from oversizing results in high humidity leading to mold and other health related issues. Take the $10,000 lawyer money and get a good contractor to install a whole house dehumidifier and feed yourself instead of the lawyer.
    mold?? has it been lab tested? otherwise its substance

    i would take the 10 grand and install the correct size system all new duct work, because we all know that if there is substance in the home its in the duct too

    then if dehumidifier is still needed it can work efficiently in conjuction with the proerly sized system
    If Guns Kill People, Do Pencils Misspell Words?

    http://www.youtube.com/watch?v=An2a1...eature=related

    Before we work on artificial intelligence why don't we do something about natural stupidity?

  20. #20
    Join Date
    Dec 2007
    Location
    Cedar Grove, Wi-Sheboygan
    Posts
    1,582
    Post Likes
    As long as you do all the proper investigations of all persons who are responsible for this fiasco along with the contractor, building inspector, owner who employs the contractor if it applies, and check on the permits and send letters to all involved as well as keep copies of everything you write and send to others for your personal file and when you go to court you will have everything in your file. You may want to copy a few of the post here but only the ones that apply to the situation as to what should have been done and things that any contractor should have done regardless of where a contractor works (Standard Operating precedure) or SOP's as there referred to you should be able to save the lawyer for more important things as I believe that as long as you do your homework there really shouldn't be any need to have one, But if you feel unsure of yourself you may still want to do all the work you can yourself and have one to file all the proper motions to ensure things on that end are done the right way.

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •