Thread: Trane SWUD Current transducer problems (Maxter?)

  1. #1
    Join Date
    Oct 2011
    Posts
    10
    Post Likes

    Trane SWUD Current transducer problems (Maxter?)

    Is there an easy or hard way to disable the circuitry for the indoor blower current transducers? I am aware of the kit including the 1U4 board, but there must be an easier way! Trane says no, but I'm certain that someone out there has had to retro a VFD into an existing system. I could restore the old contactor if need be. But the owner would like to have the VFD leypad active at all times. I remote-mounted the new Yaskawa keypad to the front panel for his accesiblity. The unit is ridiculously "touchy" now, and will lock out on CE anywhere from 5-60 minutes of runtime. The motor is fine naturally
    I suspect a "backkick" from the drive perhaps or something like that. I could mount huge chokes on the input, but previous experience tells me that that is a very expesive gamble. Any ideas?

  2. #2
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    UCP-1 ?? if this is a UCP-1 blue leds the exsisting supply fan contactor when they came in with the VFDs from Macon used it as the power contactor to supply the VFD from the UCP A07 call.the CTS stay because the UCP has to see amperage resistance for proof the fan is started....did you redip the switches for IGV/VFD SWUD might still be running configurations for Constant Volume... i need a beeeer new VFD might be pushing the CTs into a CE overload motor trip shouldn't be doing full HRz only in morning warm up or night setback..where is the staic sensing...shouldn't be over 1.5" for a SWUD on a unit wher the duct goes straight out to the space with a true return back
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  3. #3
    Join Date
    Oct 2011
    Posts
    10
    Post Likes
    Thread Starter
    Huh? Yes we have a circa '97 board in this one(blue led's) actually they look like vacuum fluorescent to me. I miss your point about the unit driving the ct's into overload... My understanding of the circuitry is the the ct's are monitoring current draw of the IDB motor, hence I wouldn't expect them to actually do anything. The unit is operated by a 0-10vdc source (third party.. Alerton, I think) And tries to maintain a 1.5" WC static. It operated just fine on the vanes (Until they worked loose)
    Last edited by unclemikey509; 10-16-2011 at 01:13 AM. Reason: typo's

  4. #4
    Join Date
    Oct 2011
    Posts
    10
    Post Likes
    Thread Starter
    Hmmm I thought a bit more about your reply Maxter. If the unit were looking for a given amount of motor current draw for what a designer anticipated for a given static pressure and did not see that, would it actually lock out? My God, if that were true I would give a real hats off to the designer. But if I were him I would also worry about putting a unit into the field that could lock out at the slightest provocation. My prior experience w/Trane says they wouldn't do somethimg like that... Hmm

  5. #5
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    the SWUD connection to its VFD are the 1U4 ramping module,run signal NO,shutdown NC,and the 3 phase thru the old CV fan contactor.i'm rethinking the CV ..CT location on the L side of that fan contactor...i'm remember seeing one in the VFD panel as was when Magatek was the first into them with just one? have to dig print up to see if it was added or taken from the top of that SF contactor? do you have full blown SWUD prints showing a VFD wiring?on the current vs static Macon had no idea what static was in relation to effecting the motor.the staic probe as right on the fan housing in the 80s then was moved out onto the duct, before the first VAV...middle of the VAVs... end of the duct run. i'll get back on stuff
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  6. #6
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    that was easy........... the SWUD W/inverter print shows the olfd fan contactor retagged as the driv contactor with no CTs on the L side as with CV unit.they take 1T8 and run the T3 coming out of the VFD thru it the CT is connected into the 1U1 at A4J5 pin.again the dip switch resetting will have the module look at the single CT there and not the typical # off the old CV contactor....i made up an actual static vs DC ramp signal having read them to see how the numbers move at and below setpoint.just from experience if a space is comfortable and your last cooling signal A21 just dropped off.the VFD should not be above 30Hz the VAVs should be backed down and the static SP met and even lower is cool... typical as said 55F at 1.5" static even less on the static depending on the ducted supply turns and rises.any counter rotation prior to start will trip the unit into CE,coming out of MWUP or NSB i found the control goes back up onto the VAVs for occupied,but the VFD is at 60Hz,and can't ramp down quick enough thru the 1U4 module so you can get a CE trip there.you have to dump the VAVs during unoccupied runs and the unit is looking at the return air settings for MWUP/NSB as you see on the 1U1 just throwing out stuff i remember....biggy here if you come up on a unit with the compressor CTs tripped... it's not the compressors the condensers are fouled or check the strainers the CTs will trip them before HI Pressure is tripped...that ones free
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  7. Likes Mr. NO liked this post.
  8. #7
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Maxster,

    You're giving very good advice.

    Please take a minute and apply for your AOP * before posting in AOP forum.



  9. #8
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    i'm not a owner just answering the guys question....what's with all the rules i didn't even want PM status....... just looking to help others...
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  10. #9
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by maxster View Post
    i'm not a owner just answering the guys question....what's with all the rules i didn't even want PM status....... just looking to help others...
    You don't need to be an owner to be an AOP Pro.

    It'll take 5 minutes to fill out the form and we won't have to hassle you anymore.




  11. #10
    Join Date
    Oct 2011
    Posts
    10
    Post Likes
    Thread Starter
    Maxter, I truely appreciate your advice. To the system admin: I would take this discussion elsewhere if I were more facile with computers. Just an old guy here trying to
    make a unit run.

  12. #11
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    hey,... i'm 58 who you calling OLD might go over to messeger in the site to continue we'll see if the prime movers dabble only trying to help out and their busting shoes
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  13. #12
    Join Date
    Oct 2011
    Posts
    10
    Post Likes
    Thread Starter
    I am 59 so I am the older I guess. Hey,... I don't feel that old. Except recently HA!

  14. #13
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Maybe I'm misunderstanding.

    Unclemikey,

    Are you a tech? If so, then this thread needs to be moved to the proper forum.



  15. #14
    Join Date
    Oct 2011
    Posts
    10
    Post Likes
    Thread Starter

    Tech

    Yes, I am a tech. Sorry if I violated site rules, please excuse my ignorance.
    I found his reply via a bot search filled out the appropriate forms to gain access here, but must have overlooked a rule. Will leave presently.

  16. #15
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    move it to the SWUD section...
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  17. #16
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by unclemikey509 View Post
    Yes, I am a tech. Sorry if I violated site rules, please excuse my ignorance.
    I found his reply via a bot search filled out the appropriate forms to gain access here, but must have overlooked a rule. Will leave presently.
    No need for you to leave. I'd actually encourage you to stay, learn the rules (I'm still learning stuff about this site) and become a Professional Member where we can share more detailed information about the equipment we work on.

    Since you are both techs, this thread will be moved to the appropriate section "tech-to-tech chat Commercial"



  18. #17
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    dang.

    It actually worked!!



  19. #18
    Join Date
    Oct 2011
    Posts
    10
    Post Likes
    Thread Starter
    Ok Thanks. The current problem I'm having has the techs in Georgia stumped, so you can imagine my dilemma. Mike.

  20. #19
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    Mike..how many unit do you have with the VFD add on after the IGVs went nuclear...nuke cleee r.now thinking about it 97 isn't bad on the motor.future applications a motor change might be in order using a motor that has seen a constant 60Hz then all of a sudden the Hz are being slid in and that voltage when it is ramping up/down can do a job on the insulation...anybody meg the motors on those jobs especially to ground maybe a heat up might cause a CE trip...Ray
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  21. #20
    Join Date
    Oct 2011
    Posts
    10
    Post Likes
    Thread Starter
    Hey Maxster, I haven't megged the motor, but did do a passive resistance check prior and it was well over 20 meg on all three (actually six) windings. This is one of seven and the only one I've converted. It initially ran fine for two hours and still will sometimes. The VFD is one I've installed at least twenty of (six on different Trane units BTW) and to date have had no problems. BTW if the VFD sees anything wrong with the motor it will shut down immediately. This motor was swapped out in 2006 and is listed for vfd use. Not once has the vfd tripped. My problem is definitely in the unit somewhere. I caught your note on the ribbon cables and will inspect them closely tomorrow AM. BTW Thank you for your replies, I appreciate it. Mike.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •