    Icynene

    My wife and I are building a home in Houston, and we are exploring our energy efficiency options. We are interested in icynene, but our builder has not used foam insulation, and has expressed some reservations about moisture buildup behing the icynene. Is this a valid concern in a humid climate such as houston. With foam insulation, what things should we insure to prevent moisture/mold problems. Additionally, what other thing are needed to ensure a fresh air environment for the home since it's now a sealed home?

  2. #2
    Join Date
    Sep 2005
    Posts
    58,702
    Post Likes
    Properly installed, there should be no moisture build-up behind foam... PROPERLY INSTALLED.

    Foam houses are structurally stronger than conventional, a good thing in hurricane proned Houston (grew up there).

    You will need an ERV (energy recovery ventilator) installed with each system. Ask your HVAC contractor to include this.

    Also, be SURE the load calc is done to reflect a foam house. It will be different (lower capacity equipment).

    I would look for a builder that has experience with foam, and an HVAC guy that has experience with foam also.
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

  3. #3
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,480
    Post Likes
    Quote Originally Posted by ga-hvac-tech View Post
    Properly installed, there should be no moisture build-up behind foam... PROPERLY INSTALLED.

    Foam houses are structurally stronger than conventional, a good thing in hurricane proned Houston (grew up there).

    You will need an ERV (energy recovery ventilator) installed with each system. Ask your HVAC contractor to include this.

    Also, be SURE the load calc is done to reflect a foam house. It will be different (lower capacity equipment).

    I would look for a builder that has experience with foam, and an HVAC guy that has experience with foam also.
    Very important, that this is done.
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

  4. #4
    Join Date
    May 2004
    Location
    south louisiana
    Posts
    3,790
    Post Likes
    most foam companies have hvac companies that they work with
    that understand the cause and effect of foam insulation and how
    it will reduce tonnage of hvac.
    load calc will relfect these inputs

    you are doing open cell??
    closed cell will cause moisture to be trapped and open cell will
    let it dry

    your best option is to foam the roofline and use conventional insulation
    in the walls. the walls should be sealed using the air tight drywall approach
    and 1" foam sheating (with seams taped)to exterior of walls.
    sole plates should be sealed to slab and attention to air sealing details

    southface inst has great air sealing factsheets.
    this is by far the most affordable and efficient way to stick build.
    more info at buildingscience.com under hot humid climates.

    best of luck.
    The cure of the part should not be attempted without the cure of the whole. ~Plato

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •