Thread: Trane guys I have a question

  1. #1
    Join Date
    Jan 2004
    Posts
    169
    Post Likes

    Confused Trane guys I have a question

    Ok here it goes I have a Trane mod. SEHFC754N167A8AD9C01A0W00G0K000RT008000 ser. C02c01857
    Let me first explain I am not a apprentice and I have a Trane unit as mentioned above that is having issues on above 95 degree days. We which is one of my top teck and I have looked at this unit and found that the condenser is under sized at the design load conditions. I will give the details we are seeing. first I live in Denver and we don't have near the air you guys do at sea leavel so here are the readings. Trying to maintain a discharge air of 55 degrees and the oat is 95 with a 30% humidity level on the day we are seeing this. Pressures are at 70 suction with a 20 degree superheat as we removed freon to confirm what we were seeing and the discharge pressure was at 410 plus and rising and it tripps at 420psi. We removed enough Freon R-22 to get as low as 4 degrees subcooling and it still tripps if all three compressors are runing. I cleaned the condenser coil for circuit #2 just to see what would happen and the unit would stablelize at 410 psi but we did notice the fan blades have been changed with 5 blade fans and they are at rated amps and this was done by trane after the oringinal install.
    so here we are trying to figure this out. We disconnected one compresor on both circuits and the unit will cool the space and stay running. So I am wondering if the condenser is under sized as we removed enough freon to where the superheat will continue to rise. Any thoughts
    If you find it bad 3 different ways- ~its bad~

  2. #2
    Join Date
    Feb 2009
    Location
    Thonotosassa, FL
    Posts
    804
    Post Likes
    Did you pull the condensor coils apart to clean them.

  3. #3
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    4,021
    Post Likes
    I know what's wrong it! The model numbers too long! Throw it in the garbage!

  4. #4
    Join Date
    Dec 2010
    Location
    On a Peninsula in NE NC
    Posts
    1,904
    Post Likes
    Quote Originally Posted by GREGHVACGUY View Post
    Did you pull the condensor coils apart to clean them.
    I pack is not a split coil
    It's hard to stop a Trane. but I have made one helluva living keeping them going.

  5. #5
    Join Date
    Dec 2010
    Location
    On a Peninsula in NE NC
    Posts
    1,904
    Post Likes
    have you pulled charge an weighed?
    It's hard to stop a Trane. but I have made one helluva living keeping them going.

  6. #6
    Join Date
    Jul 2002
    Location
    Yuma, AZ
    Posts
    2,755
    Post Likes
    Quote Originally Posted by teckster View Post
    Ok here it goes I have a Trane mod. SEHFC754N167A8AD9C01A0W00G0K000RT008000 ser. C02c01857 Packaged unit, commercial with 3 (or 4??) compressors, 2 separate circuits. Let me first explain I am not a apprentice and I have a Trane unit as mentioned above that is having issues on above 95 degree days. We which is one of my top teck and I have looked at this unit and found that the condenser is under sized at the design load conditions. I will give the details we are seeing. first I live in Denver and we don't have near the air you guys do at sea leavel so here are the readings. Trying to maintain a discharge air of 55 degrees and the oat is 95 with a 30% humidity level on the day we are seeing this. Pressures are at 70 suction with a 20 degree superheat as we removed freon to confirm what we were seeing and the discharge pressure was at 410 plus and rising and it tripps at 420psi. We removed enough Freon R-22 to get as low as 4 degrees subcooling and it still tripps if all three compressors are runing. I cleaned the condenser coil for circuit #2 just to see what would happen and the unit would stablelize at 410 psi but we did notice the fan blades have been changed with 5 blade fans and they are at rated amps and this was done by trane after the oringinal install. Are all of the blades' rotation correct? so here we are trying to figure this out. We disconnected one compresor on both circuits and the unit will cool the space and stay running. So I am wondering if the condenser is under sized No way. as we removed enough freon to where the superheat will continue to rise. Any thoughts
    Previous techs may have left air or nitrogen in the systems. Even R410A is possible. In any event the purity of the refrigerant must be checked against a PT chart. Recover the refrigerant, test the purity, recharge with pure R22 by weight and see what happens. Restricted driers ahead of the SC temperature reading point could be hiding an overcharge.There is no reason why the discharge pressure should exceed 340 psig on a 100°F ambient. Recirculation of condenser discharge air or wind may contribute to your problem but I doubt that this would be a major factor.
    "I have never let my schooling interfere with my education."
    Mark Twain
    NEVER STOP LEARNING.

  7. #7
    Join Date
    Sep 2008
    Location
    Woodsville, NH
    Posts
    1
    Post Likes
    I agree with the above statement. must pull apart coil. with multi circiuts there is more then one coil on top of each other and from the outside coil may look clean but when pulled apart there will be a thick layer of dust. If still a problem and is believed to be first statement, then remove all refrigerant, purge, evacuate and recharge with factory amount of refrigerant. Also never hurts to call Trane tech support they are very helpfull.

  8. #8
    Join Date
    May 2000
    Location
    Stafford, Va. USA
    Posts
    225
    Post Likes
    Hi Teckster,
    The IntelliPak unit does NOT have a split coil like the Voyager II units. The IntelliPak has a single coil as Southern Mech stated.
    Do the procedures that Lynn Comstock has recommended. Pay close attention to the liquid line drier, if it is stopped up and the unit was running low suction, someone may have thought the unit is low on refrigerant, and added some refrigerant. Now the unit is overcharged and running high head pressure.
    The condenser is not undersized. Your unit was built in March of 2002, the temperatures have certainly been at 95 degrees or higher since then. That sort of problem would have been found before now.
    Good Luck,
    Allen
    UA Local 602
    A man who says that he can't learn anything in a class is exactly right.

  9. #9
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    You can also check the purity of the refrigerant by pumping down the unit, then manually run the condenser fans (no compressor), and see if the saturated refrigerant temp in the condenser matches the outside ambient temp.

  10. #10
    Join Date
    Feb 2006
    Location
    Atlanta,GA.
    Posts
    1,024
    Post Likes
    I would pull charge replace driers w/ shell driers with valves on both sides and weigh charge in. I had some units a little older than that driers were stopped up and someone had overcharged unit

  11. #11
    Join Date
    Aug 2011
    Location
    fayetteville nc
    Posts
    18
    Post Likes
    Sorry to get off subject, i have a unit with a bad baysensorsomthing19b. Can I switch to a conventional stat by switching from the numbers to the y r g w terminals. Or is there another control ill need.

  12. #12
    Join Date
    Aug 2011
    Location
    Los Angeles, CA
    Posts
    34
    Post Likes
    If you have the UPC board with the #'s and the letters. Yes you can switch to a conventional stat. If you have the UPC board with no connections on it, then you would need the C.T.I board. (Conventional Thermostat Interface)

  13. #13
    Join Date
    Aug 2011
    Location
    fayetteville nc
    Posts
    18
    Post Likes
    Thanks a lot. I have seen that cti but never knew what was for.

  14. #14
    Join Date
    Aug 2011
    Location
    Los Angeles, CA
    Posts
    34
    Post Likes
    It reconfigures the L.T.B for conventional thermostats. The pain in the neck is to see if your unit is pre 93 or after 93. They change where the wires land on the LTB

  15. #15
    Join Date
    Aug 2011
    Location
    fayetteville nc
    Posts
    18
    Post Likes
    Ok, ill check. It is a reliatel board. It is cool all the things u can do it just cost to much to replace.

  16. #16
    Join Date
    Aug 2011
    Location
    Los Angeles, CA
    Posts
    34
    Post Likes
    Yeah. I like working on Trans units. They are usually pretty easy. I hate Yorks, no field experience by anyone in the factory, the electrical panel is way to small.

  17. #17
    Join Date
    Aug 2011
    Location
    fayetteville nc
    Posts
    18
    Post Likes
    I'm new to commerical. So I have a lot to learn about walkins and econimizers. I don't understand yorks compressor lockouts. Is it only lock if low voltage amp draw is to high to it ? I don't understand how it sence the amps.
    Last edited by vanillaIce84; 08-31-2011 at 07:26 AM. Reason: incorrect spelling

  18. #18
    Join Date
    Oct 2007
    Location
    Richmond, VA
    Posts
    373
    Post Likes
    Quote Originally Posted by vanillaIce84 View Post
    I'm new to commerical. So I have a lot to learn about walkins and econimizers. I don't understand yorks compressor lockouts. Is it only lock if low voltage amp draw is to high to it ? I don't understand how it sence the amps.
    With all due respect, you hijacked the thread. Why not start a new thread and talk all you want about cti boards and York compressor lockouts.

    PS. Welcome to the forum.

  19. #19
    Join Date
    Aug 2011
    Location
    fayetteville nc
    Posts
    18
    Post Likes
    I can do that if it bothers you

  20. #20
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    Quote Originally Posted by vanillaIce84 View Post
    I can do that if it bothers you
    Hello my friend and welcome to the forum!
    It's not that it bothers him, but the person who started this thread is looking for help with his Trane unit and when you hijack a thread and change the subject, it takes away from the original person looking for help. Its no big deal, we've all done it (including me).

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •