    What is the proper measurement to charge with?

    I always thought you use SH to charge with fixed orifice or distributor and SC for TXV. But even the Sporlan instructions that come with a TXV talks about charging to SH.

    One of the guys I work with went on an interview yesterday and the guy asked him the proper way to charge a system. He said SH and the guy said he was wrong. He said you charge to SC. The guy didn't specify the metering device. I told the guy I work with what I said in the first paragraph and that the guy he interviewed with didn't know what he was talking about.

  2. #2
    Join Date
    Oct 2008
    Location
    SAN ANTONIO, TX
    Posts
    6
    Post Likes
    alot depends upon application........is it sized right.........is it an old system that isnt really efficient....sometimes when trying to get to your 10 deg of subcooling on a older system you may be raising your head pressure out of sight trying to get there....compressor is most important part and you dont want your sh to be to low or to high. but check both anyways
    Last edited by cool freak; 10-31-2008 at 05:20 PM.

  3. #3
    Join Date
    Sep 2006
    Location
    Ohio
    Posts
    798
    Post Likes
    You are right, if the system has a TXV, you charge by subcooling because the TXV will maintain whatever Superheat it is set for. It is always a good idea to check both SC and SH, but charge by SC. You can also go by discharge superheat, this works well with either fixed orface or TXV systems.

  4. #4
    Join Date
    Jun 2008
    Location
    Windsor, Ont.
    Posts
    894
    Post Likes
    Charging by superheat will only guarantee you an adequate charge so long as the load doesn't change, if you have just enough refrigerant to achieve a desired superheat under a moderate load you will not have enough refrigerant to maintain that superheat when the load increases. Superheat also does not guarantee you that a full column of liquid is getting to your metering device, flashgas can occur in the liquid line before it gets to the evaporator. If there's no charging chart with a condending unit for reference, I generally charge to provide 10 deg SC and then check my suction and discharge temperatures to ensure they are in a good range.

  5. #5
    Join Date
    Apr 2002
    Location
    Dallas, TX
    Posts
    2,659
    Post Likes
    Quote Originally Posted by elvis66 View Post
    I always thought you use SH to charge with fixed orifice or distributor and SC for TXV.
    This is correct.

    Quote Originally Posted by elvis66 View Post
    But even the Sporlan instructions that come with a TXV talks about charging to SH.
    The TEV service installation instructions can be downloaded from here: http://sporlan.jandrewschoen.com/10-11.pdf

    Where does it state systems with TEVs are to be charged to superheat?

  6. #6
    Join Date
    Feb 2007
    Location
    Napa
    Posts
    111
    Post Likes
    Thread Starter
    Andy, it may not say to "charge" to SH, and I didn't read the whole thing word for word, but it doesn't say anything about SC, it only talks about SH, and that is the point I was trying to make...

  7. #7
    Join Date
    May 2008
    Location
    Jax Fl.
    Posts
    1,938
    Post Likes
    Quote Originally Posted by hands View Post
    You are right, if the system has a TXV, you charge by subcooling because the TXV will maintain whatever Superheat it is set for. It is always a good idea to check both SC and SH, but charge by SC. You can also go by discharge superheat, this works well with either fixed orface or TXV systems.
    I agree, charge with suction superheat on straight cool [only] and then verify the subcooling with a clean-as-new condenser coil. The subcooling changes as the coil ages too.

    Verify with checking Discharge superheat [apx 100 degrees].

    Charging with subcooling only works to get the highest efficiency on High SEER matched system. High SEERS must be charged to the Mfgs specs to get the highest SEER.

  8. #8
    Join Date
    Apr 2002
    Location
    Dallas, TX
    Posts
    2,659
    Post Likes
    Quote Originally Posted by elvis66 View Post
    Andy, it may not say to "charge" to SH, and I didn't read the whole thing word for word, but it doesn't say anything about SC, it only talks about SH, and that is the point I was trying to make...
    Most residential hvac OEMs will recommend their systems be charged by weight. As a result, it behooves us not to suggest something different. But I suppose we should note charging a system with a TEV and less a receiver should be done by subcooling given the absence of an OEM's charging recommendation.

  9. #9
    Join Date
    Apr 2008
    Location
    Alberta Canada
    Posts
    2,246
    Post Likes

    One Thing

    When charging a system with TEV, your super heat is basically fixed between 8 to 12 degree SH. Charge by SC and check SH to make sure evrything else is good.
    Do it right the first time.

  10. #10
    Join Date
    Sep 2008
    Location
    arlington, tx
    Posts
    225
    Post Likes
    you cant charge to the proper subcooling unless the txv is metering the desired superheat so you have to charge to both and adjust the txv as necessary

  11. #11
    Join Date
    Apr 2008
    Location
    Alberta Canada
    Posts
    2,246
    Post Likes

    Not Necessary

    Quote Originally Posted by mechanicalgsxr View Post
    you cant charge to the proper subcooling unless the txv is metering the desired superheat so you have to charge to both and adjust the txv as necessary


    Most TEVs are going to fixed positions. Less problems.
    Do it right the first time.

  12. #12
    Join Date
    Sep 2008
    Location
    arlington, tx
    Posts
    225
    Post Likes
    so are you supposed to change out the txv because you dont know how to work on it?

  13. #13
    Join Date
    Apr 2008
    Location
    Alberta Canada
    Posts
    2,246
    Post Likes

    Yah Okay

    Quote Originally Posted by mechanicalgsxr View Post
    so are you supposed to change out the txv because you dont know how to work on it?

    You have to make yourself alittle clearer.
    Do it right the first time.

  14. #14
    Join Date
    Sep 2008
    Location
    arlington, tx
    Posts
    225
    Post Likes
    you said its not necessary to know how to adjust the txv because newer models are coming out fixed i was asking if a tech should just change the device out to one of these models rather than learning how to properly adjust it


    if you just keep adding refrigerant to try and get the subcooling up without analyzing the load you can run the superheat into the low single digits and release that puff of smoke they put in the compressor

  15. #15
    Join Date
    Apr 2008
    Location
    Alberta Canada
    Posts
    2,246
    Post Likes

    Only If your an Idiot, I guess

    Quote Originally Posted by mechanicalgsxr View Post
    you said its not necessary to know how to adjust the txv because newer models are coming out fixed i was asking if a tech should just change the device out to one of these models rather than learning how to properly adjust it
    if you just keep adding refrigerant to try and get the subcooling up without analyzing the load you can run the superheat into the low single digits and release that puff of smoke they put in the compressor

    But I no i should have made myself cleared to you. Didn't you already talk about this in another post.
    Do it right the first time.

  16. #16
    Join Date
    May 2008
    Location
    Jax Fl.
    Posts
    1,938
    Post Likes
    Quote Originally Posted by mechanicalgsxr View Post
    you said its not necessary to know how to adjust the txv because newer models are coming out fixed i was asking if a tech should just change the device out to one of these models rather than learning how to properly adjust it


    if you just keep adding refrigerant to try and get the subcooling up without analyzing the load you can run the superheat into the low single digits and release that puff of smoke they put in the compressor
    How many puffs of smoke are in each new compressor?

  17. #17
    Join Date
    Sep 2008
    Location
    Cedar Rapids, IA
    Posts
    489
    Post Likes
    Quote Originally Posted by JRINJAX View Post
    How many puffs of smoke are in each new compressor?
    Reconditioned compressors have the smoke reinstalled.

  18. #18
    Join Date
    Sep 2008
    Location
    arlington, tx
    Posts
    225
    Post Likes
    Quote Originally Posted by JRINJAX View Post
    How many puffs of smoke are in each new compressor?
    only one

  19. #19
    Join Date
    Sep 2008
    Location
    arlington, tx
    Posts
    225
    Post Likes
    Quote Originally Posted by 21degrees View Post
    But I no i should have made myself cleared to you. Didn't you already talk about this in another post.
    i dunno i probably did but sorry if i misunderstood what you were saying

  20. #20
    Join Date
    Jan 2009
    Location
    Missouri, USA
    Posts
    329
    Post Likes

    When it's 30 F outside ?

    It's cold and I don't know the best way to get my charge correct, I mean I understand Superheat and subcooling should both be checked but is this going to be that acurate, In what heat mode or cooling mode ? I need to know the chart on placement best for a heat mode txv hp with a substantial vertical rise ? any help, thanks.. ...

+ Reply to Thread
Page 1 of 6 123456 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •