    Hmm Proper sizing and model question

    I have a 1100' split level house. I have had 4 differnt contractors come over. 3 out of the 4 sized it for a 2 ton unit. 1 sized it for a 11/2 ton unit. The one 11/2 unit the contractor said the coil is 2 ton or compessor is 11/2 or reversed?
    Second question is how is a Heil unit (N4H3)? And do all units come with a 10 year parts , 1 year labor?

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Some mfrs don't make a 1.5 ton coil or approve of a 2 ton coil on a 1.5 ton unit for efficiency. How are they sizing? Guessing? Measuring and calculating?

    Where are you? Is 1/2 of the first floor underground?

    The N4H3 is a builder model, very similar to Carrier's basic unit.

  3. #3
    Join Date
    May 2013
    Posts
    3
    Post Likes
    Thread Starter
    They asked square footage, windows, insulation. I live in Rochester ,NY. No part of the 1st floor is underground. Im concerned because initally the Heil contractor mentioned a 2 ton unit and now he says this 11/2 ton unit. Would a 1/12 ton unit effiently cool a 1100' house?
    The units that I were qouated on were Heil,York,Amanna,Armstrong. Who makes Heil?

  4. #4
    Join Date
    Jun 2008
    Location
    Rochester, NY
    Posts
    351
    Post Likes
    Make sure you have a load calculation done on the house. It's the only way you'll know for sure what size equipment you need.

    And Heil is made by ICP - International Comfort products

    -Mark

  5. #5
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    Rochester, NY 2.5% summer design is 88F & 77F wet bulb for 43% RH outdoors.
    An 88F outdoor air temp (OAT) doesn't carry near as high a ppm of moisture as say a 100F OAT.

    Do you have factors in your home that create increased indoor humidity loads?
    How tight do you think your home is; a high 0.8 Air Changes per Hour or 0.5 ACH?

    The only way you'll know if a 1.5-Ton will handle the load is to run a whole house load-calc

    You & your contractor can try this free online Whole House Load Calc but save your sf measurements somewhere else; then when you get everything right you'll need to print the results; as you can't save them. You'll need to use an infiltration rate between a real tight 0.4-ACH & say a 0.9-ACH, then using the cu/ft of air volume of your home & your guess of the % of ACH it will list the CFM number which you put in the make-up-air blank, so it will figure the cooling latent load, etc.

    Then you use the Expanded Cooling Data on the 1.5-Ton Model unit you are planning to buy; a "Goodman Expanded Data" (search it) is easy to access online & may get you close enough using the same conditions criteria. It shows the 1.5 with a 2-Ton indoor cooling coil.

    The 1.5-Ton A/C must be higher than the load-calc Results, by a decent margin in all 3 categories; Total Btuh, Sensible Btuh, & Latent Btuh.

    To get the sensible Btuh, look at the S/T line on the Expanded Cooling chart & multiply it by the MBh in 1000' number; subtract the sensible from the total & you get the Latent Btuh.

    Your contractor should know how to (or using other methods) do this for you... Manual S illustrates SIZING procedures; but may oversize a little bit

  6. #6
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    Actually concerning what load-calc ACH to use; you really should use 0.40 or 0.45 ACH because you need to plug the holes to get the average infiltration ACH rate down to those levels.

    Concerning sizing; you can do other things to get the heat-gain down to where the tonnage you selected will work; if you oversize you're out of options.

    Also, for those very few exceptionally hot days, with the longer continuous runtime, 79-F plus 50% RH or less in your home, you will be well within the human comfort level conditions, and have more efficient operating runtimes during the other 90% of the seasonal operating times.

    What % of the time will conditions be above the 75F indoor design & end up as high as 79F; an exceptionally few...the user has to agree with that selected design formula, or don't use it!

  7. #7
    Join Date
    Jul 2007
    Location
    Beautiful, Philadelphia, the City of Brotherly Love!
    Posts
    1,264
    Post Likes
    Quote Originally Posted by udarrell View Post
    if you oversize you're out of options.
    Not that you want to add unnecessary expense to a simple installation, but there is hope for those with mismatched or oversized condensing units. http://www.rawal.com/usrfiles/conten...s_brochure.pdf
    “You don't get paid for the hour. You get paid for the value you bring to the hour.” Jim Rohn

  8. #8
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Dang, spark, thems some credentials!

    He's in your "hood", can you help him out or line him up with someone?

    ICP/Heil is owned by Carrier. Same factories. The N4H3 is very much like the Carrier/Bryant basic units, slightly different grille.

    If all 1100 ft is above ground, the 2 ton unscientifically doesn't sound too bad. But the load calc will tell if you want to do it right.

  9. #9
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    Quote Originally Posted by AtticAce View Post
    Not that you want to add unnecessary expense to a simple installation, but there is hope for those with mismatched or oversized condensing units. http://www.rawal.com/usrfiles/conten...s_brochure.pdf
    Hey AtticACE, after seeing your response to the parts changers; you're my kind of TECH PRO!
    ---------------
    How low a tonnage do they go to with their reduction in output? Looked like they were primarily used on larger commercial applications.

    Wonder what it cost to put one on a particular sized unit?

  10. #10
    Join Date
    Jun 2008
    Location
    Rochester, NY
    Posts
    351
    Post Likes
    Quote Originally Posted by BaldLoonie View Post
    Dang, spark, thems some credentials!

    He's in your "hood", can you help him out or line him up with someone?

    ICP/Heil is owned by Carrier. Same factories. The N4H3 is very much like the Carrier/Bryant basic units, slightly different grille.

    If all 1100 ft is above ground, the 2 ton unscientifically doesn't sound too bad. But the load calc will tell if you want to do it right.
    Thanks BL!

    Drumrol,

    What I would have done is an energy audit. They should include a load calculation and will check the rest of your house for issues. They are free to have done right now in NY state.
    That way you can have a comprehensive report of your house, what can be improved on (if anything), the load calc, and learn about possible rebates/incentives for no cost.
    I work for Isaac in the commercial service dept. Here's our home energy performance page with some additional info and phone #
    http://isaachomeenergy.com/

    Hopefully I'm not overstepping my bounds by plugging the company's info.

    -Mark

  11. #11
    Join Date
    Jun 2007
    Location
    Minneapolis, MN
    Posts
    1,026
    Post Likes
    I like the 1.5ton contractor. Heating and cooling equipment should be sized properly--ACCA Manual 'J' heat loads--and left on most of the time. The only thing to improve a proper heat load is to predicate it with a proper blower door test and weather sealing.

    Most equipment is over-sized as most customers don't understand comfort. "We shut everything down when we leave for work--summer and winter--and when we come home, it better be perfect before we set down to dinner!"

    Set, forget it, be happy.

    It is not unusual to oversize the condenser coil, and could be good, if you know what your doing.

    One year labor is the standard for most mechanical trades.

  12. #12
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    In Rochester, NY, I'd have trouble imagining a typical 1100sqft residential configuration that would need more than 1.5 tons. But a load calculation is still needed to verify.

  13. #13
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Quote Originally Posted by BadgerBoiler MN View Post
    Most equipment is over-sized as most customers don't understand comfort. "We shut everything down when we leave for work--summer and winter--and when we come home, it better be perfect before we set down to dinner!"

    Set, forget it, be happy.
    .

    +1. Worse you jsut deferred all of your run time to the tiem of day where you AC system is the least effcient and has the least capacity.

    Most people would probably hate my house since it's a shrine to proper equipment sizing . It was 70F outside yesterday and I turned it down from 75 to 74F because my wife was a little warm. It took it almost 2 hours to drop it 1F. But when it was 85F and sunny earlier, it was only cycling about 50% of the time on 1st stage... as it should.

  14. #14
    Join Date
    May 2013
    Posts
    3
    Post Likes
    Thread Starter
    Thank you all for the great information and feedback. I will definetly check in to the home audit also. I have 2 more questions.
    1. Currently my return air grills are on the bottom of the walls, the contractors say I should move them up towards the ceiling. Then rotate between the two between heating and cooling??
    2. Condensate drain location. One contractor was going to pump it over to my sump pump pit, the other 3 said they would run a line to the space along the wall from the floating slab ??
    I guess I'm going to want to keep the sun out of the house if I'm trying to cool it. Shades,curtains.

  15. #15
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,329
    Post Likes
    2 ton ductless mini-split heat pump.

    < 600 Cooling Degree Days
    > 6400 Heating Degree Days

    Similar to ..

    http://www.climate-zone.com/climate/...york/syracuse/
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  16. #16
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    gravity is more reliable than a pump but out needs to have adequate slope.

    Return location isn't that critical. Supply location and register wealth make a bigger difference.

    I might argue that you want grills lower in summer. Why...because ceilings are 8+ feet tall and humans ate usually 6 or less and only 4 when sitting. Allowing Souter to strategy at the ceiling means that you have less air that needs cooling.

    All thing being equal, aesthetically a wall grill near the floor is the least noticeable

    Sent from my DROID RAZR using Tapatalk 2

  17. #17
    Join Date
    May 2013
    Posts
    1
    Post Likes
    Great information and a huge help. Thanks for everyone's efforts in helping each other. I have been quoted $13K + to change out two 2 ton units. I am thinking of going to one unit. After reading and looking at the threads on R22 vs R410A I am going with the R410A, even though it may cause a little more or quicker degradation of the system. It still should be cheaper in the end and there is the environmental factor. I do have some math under my belt and am going to enjoy trying to make the load calculation on my own first. I was surprised to find out I could over do the system size. At least that is what I think the comments on the thread are confirming. I hope my questions are fun for folks to take on. I generally get very creative when problem solving, so here they come: 1) Can someone expand on the need for accuracy regarding size of AC unit in a split system. The existing units are carrier 2 ton units. One for the up stairs and one for the down stairs. 2) Is going with a 4 ton unit a safe bet or is the load calculation still going to be a very important step? 3) Is the quoted price realistic? Thanks in advance, Jim

  18. #18
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    I generally get very creative when problem solving, so here they come: 1) Can someone expand on the need for accuracy regarding size of AC unit in a split system. The existing units are carrier 2 ton units. One for the up stairs and one for the down stairs. 2) Is going with a 4 ton unit a safe bet or is the load calculation still going to be a very important step? 3) Is the quoted price realistic? Thanks in advance, Jim
    Load calculation accuracy is important.

    Simply going to a 4 ton system is not accurate, accurate load Calc's are critically important.

    We cannot comment on quoted prices, I would get more quotes. Remove the price quote.

  19. #19
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,329
    Post Likes
    Quote Originally Posted by sunnync View Post
    Great information and a huge help. Thanks for everyone's efforts in helping each other. I have been quoted $01 to change out two 2 ton units.

    I am thinking of going to one unit. After reading and looking at the threads on R22 vs R410A I am going with the R410A, even though it may cause a little more or quicker degradation of the system.

    It still should be cheaper in the end and there is the environmental factor. I do have some math under my belt and am going to enjoy trying to make the load calculation on my own first. I was surprised to find out I could over do the system size. At least that is what I think the comments on the thread are confirming.

    I hope my questions are fun for folks to take on.

    3) Is the quoted price realistic? Thanks in advance, Jim
    Anyone thinking of R-22, is Simply not thinking or had a recent RiP Van Winkle episode.

    3) __ _ _ Hard to tell, How many ounces of gold are provided with the AHUs?

    /\ seems like No One _ Read the R U L E S. ________________
    __________ I just hate HIjacker of any form or forum.
    _______________ ______________________

    ____________________ ___________________
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •