    differential pressure switches

    Hello all,
    I am hoping someone can enlighten me as to the method for testing a differential pressure switch.
    I am working on an Armstrong furnace which has a differential pressure switch set at .7.
    I know how I was taught to verify differential pressures, but I am getting some funny readings at the burner box.
    Thanks

  2. #2
    Join Date
    Dec 2010
    Posts
    11
    Post Likes
    Thread Starter
    ***90% furnace
    better way to phrase question, what pressures should I be getting from the burner box with a functioning inducer, no cracks in heat exchanger, well sealed system with intake piping disconnected?
    Any help here is much appreciated. Ive got one here that has me scratching my head.

  3. #3
    Join Date
    Dec 2007
    Posts
    13,231
    Post Likes
    just dealt with a Lennox and they have all the test procedures and desired minimum for the unit in the manual.

    try contacting mfr for the info.

    if you have a dual manometer, connect it and get your reading.

    if single, connect it to each port and do the math.

    can't get too specific here.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  4. #4
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,249
    Post Likes
    Quote Originally Posted by handyandyshvac View Post
    ***90% furnace
    better way to phrase question, what pressures should I be getting from the burner box with a functioning inducer, no cracks in heat exchanger, well sealed system with intake piping disconnected?
    Any help here is much appreciated. Ive got one here that has me scratching my head.
    The pressure sensed by the switch is relative to the pressure in the burner box. In order for the furnace to operate, the larger negative must always be on the combustion air inducer side of the switch.

    You can not use one set of numbers for each manufacture.

    As pacnw mentioned, it's good to have the manufacturer data for each furnace you work on.
    Instead of learning the tricks of the trade, learn the trade.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •