    This is why I sometimes don't like commercial refrigeration. A Delfield under-storage refrigerated compartment wasn't cooling. After I accessed the evaporator coil, I found even though the liquid line solenoid was getting voltage, it wasn't opening. Then, I saw the expansion valve power cap looked like it was in need of replacement. Then, I saw one of the evaporator fan motors wasn't running. Then, I saw how bad the whole evaporator coil assembly looked. Once I determined I couldn't get the screws out of the back panel to remove the fan guard and the evaporator fan motor because the screws are inaccessible without pulling the whole assembly out, not to mention what a pain in the butt it's going to be to change the power cap and solenoid valve, I gave up for the day.

    I called Delfield for some guidance, the engineer confirmed that I would have to recover the refrigerant and remove the whole assembly to get the evaporator fan motor out. What? That's when I decided it was best to replace the whole assembly, including the evaporator fan motors, expansion valve, solenoid valve, evaporator coil, etc. Of course, I'm looking at close to a thousand dollars for the whole assembly.

    Attachment 263651

    The problem child

    Attachment 263661

    The fun begins

    Attachment 263671

    Expansion valve and liquid line solenoid

    Attachment 263681

    Evaporator fan motor that can't be removed

    Attachment 263691

    Leaks waiting to happen
    With your chrome heart shining in the sun, long may you run.

  2. #2
    Join Date
    May 2010
    Posts
    1,296
    Post Likes
    When it starts leaking, you get to come in and build a whole new evaporator enclosure for them. Restaurants aren't going to fix something that's not yet broken. They like squeezing the life out of their equipment for as long as possible. $1000 is about right :P

    I hate working on Delfields. I usually just tell the owner to replace the POS. :P

  3. #3
    Join Date
    Mar 2007
    Posts
    543
    Post Likes

    At least it's clean in the cooler.

    Regarding the fan motor, could you remove the evap. drain pan and get your hands under there enough to remove the lower screw for the fan mtg. bracket and flex it out to change the fan motor?

    The power head and coil sure look bad. You know if you don't change it, it's going to be a problem.

  4. #4
    Join Date
    May 2003
    Location
    Utah
    Posts
    921
    Post Likes
    Now, if there ever were a case for making the design engineer work on his creation....

  5. #5
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    For the dollars Delfield gets for these units you'd expect more consideration for serviceability.

    If I were faced with replacing that evap fan motor, I think I'd cut the motor bracket and bend it forward to get the motor out...then screw on a patch to splice it back together.

  6. #6
    Join Date
    Jul 2002
    Location
    SE Texas
    Posts
    615
    Post Likes
    Thread Starter
    Quote Originally Posted by ZeroTolerance View Post
    When it starts leaking, you get to come in and build a whole new evaporator enclosure for them. Restaurants aren't going to fix something that's not yet broken. They like squeezing the life out of their equipment for as long as possible. $1000 is about right :P

    I hate working on Delfields. I usually just tell the owner to replace the POS. :P
    Unfortunately, I work for a school district, so as much as I would like to get rid of all the Delfield equipment in our kitchens, that isn't going to happen. Someone, before I started working there, must have convinced my boss that Delfield was the equipment to buy because we have a crapload of it.

    Quote Originally Posted by 76olds View Post
    Regarding the fan motor, could you remove the evap. drain pan and get your hands under there enough to remove the lower screw for the fan mtg. bracket and flex it out to change the fan motor?

    The power head and coil sure look bad. You know if you don't change it, it's going to be a problem.
    I thought about doing that, but with all the other problems this system has, I didn't feel like tearing up my hands and arms tying to get to the screws.

    Quote Originally Posted by bunny View Post
    Now, if there ever were a case for making the design engineer work on his creation....
    There ought to be a law.

    Quote Originally Posted by icemeister View Post
    For the dollars Delfield gets for these units you'd expect more consideration for serviceability.

    If I were faced with replacing that evap fan motor, I think I'd cut the motor bracket and bend it forward to get the motor out...then screw on a patch to splice it back together.
    Yeah, you'd thing so, but having been in the trade as long as I have, I stopped expecting miracles a long time ago. Cutting the bracket would be something that I could do if it was only the motor that needed replacing.
    With your chrome heart shining in the sun, long may you run.

  7. #7
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    So do you get to climb into that box like a contortionist

  8. #8
    Join Date
    Jul 2002
    Location
    SE Texas
    Posts
    615
    Post Likes
    Thread Starter
    Quote Originally Posted by VTP99 View Post
    So do you get to climb into that box like a contortionist
    How'd you know?
    With your chrome heart shining in the sun, long may you run.

  9. #9
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Quote Originally Posted by SandShark View Post
    How'd you know?
    Been there done that accept I'm 6'-2" and I have a hard time getting my last foot in.

  10. #10
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    At least you are working in a clean kitchen. Seems like every time I get into a kitchen, I'm swimming in grease on top of it all.

  11. #11
    Join Date
    Mar 2007
    Location
    AR
    Posts
    2,489
    Post Likes
    Quote Originally Posted by chuckcrj View Post
    At least you are working in a clean kitchen. Seems like every time I get into a kitchen, I'm swimming in grease on top of it all.
    Yea i got to wallow in grease for about 3 hrs today tearing apart a pizza prep table and then thawing it out due to stopped up drain line U-trap. McCall. On the upside its been awhile since ive had to do it since i removed the stupid a$$ factory copper U and heated and bent my own pvc replacement U. Before I came up with what I think was a great idea, I was having to unplug it every couple of months.

  12. #12
    Join Date
    Jul 2002
    Location
    SE Texas
    Posts
    615
    Post Likes
    Thread Starter
    Quote Originally Posted by chuckcrj View Post
    At least you are working in a clean kitchen. Seems like every time I get into a kitchen, I'm swimming in grease on top of it all.
    Yeah, I know about grease. I used to work for Whataburger (open 24 hours a day!). The good thing about public schools is no fried foods except for the high school and the staff does a good job of keeping the fryer area spotless, which is alright by me!
    With your chrome heart shining in the sun, long may you run.

  13. #13
    Join Date
    Mar 2007
    Location
    AR
    Posts
    2,489
    Post Likes
    Ive been in a couple school kitchens. They do seem to be alot cleaner than the rathole restaurants Im usually stuck in.

  14. #14
    Join Date
    Jun 2009
    Location
    DFW, TX
    Posts
    1,719
    Post Likes
    Yeah we had a customer that had one evap fan motor out for over a year, didn't get changed until we replaced the whole evaporator ass'y, because that fan was against a wall. Sometimes though, you can just unmount the evap ass'y and there is enough play to bend it sideways enough to access the other side without cutting the refrigeration lines. I actually like those Delfield evaporator assemblies, really easy to swap out once they start leaking, which is usually 5 to 7 years in my experience.

    Seen this has happened multiple times: First tech goes out, replace t-stat. A month later, next tech goes out replace powerhead. A month later, next tech goes out, its out of refrigerant and replace the entire assembly (we rarely rebuild them, usually replace the whole assembly).

    But dang, those Delfield mullion evaporator units just work great. Great airflow, they always pull down to low 30's, and really never freeze up (assuming all fans, refrigeration, tstat etc, working properly.) They pull the box down FAST. That's what I love about them. The wrapped cold rails also work great in my experience.

    On the other hand, the 4400 series evaporator / cap tube, those style Delfields are very light duty and I am not a fan, especially on the open top design, they pretty much never hold temp properly especially in the pans; with only a single evaporator fan they just frost up continuously throughout the day and food gets warm, until it finally goes through a defrost, then it works until the first time they open a door or something, then its warm again the rest of the day. SLOOOOW to pull down, can't keep up with heavy usage or ambient > 78*f on the open top design.

  15. #15
    Join Date
    May 2009
    Location
    The Pas, Manitoba Canada
    Posts
    236
    Post Likes
    Changed out a complete prep table set up once. Has dual evaps running 2 2 door under counter cooler compartments with pans on top on each side. Also has a bread warmer and hot water pan section between the 2 cooler sections. Used a common water cooled condensing unit mounted in the middle. Spent a LOT of time fixing leaks that had to be done after closing time before being able to change all the refrigeration. Was ok for about 4 years after the retro then all the salad dressings etc. started kicking the snot out of the aluminum fins/copper again. Coated coils helped a little but the sauces and dressings must be pretty strong in this place. Makes you wonder what happens to your insides when you eat in any steak house.
    It's sure nice to engineer and install the whole system instead of the one piece at a time. Make and model number was nowhere to be found on original

  16. #16
    Join Date
    Nov 2011
    Location
    Wisconsin
    Posts
    6
    Post Likes

    I feel your pain!

    This is the exact reason I did and believe that any design engineer should be required to work in the field for 5-10 yrs before sitting in front of the computer and opening (insert your favorite design/cad program here)! Most of the design engineers I have met/talked to have no clue as to what Techs go through after the fact. I finished school for refrigeration design worked for a chiller company for 4 yrs then went into residential/commercial service work for 5 yrs before I even decided to pursue my current career in design for the company I currently am working for.

  17. #17
    Join Date
    May 2006
    Location
    Amory Mississippi
    Posts
    1,012
    Post Likes
    Quote Originally Posted by bunny View Post
    Now, if there ever were a case for making the design engineer work on his creation....
    X100

  18. #18
    Join Date
    Mar 2007
    Location
    Madison, Wisconsin
    Posts
    2,749
    Post Likes
    Randal likes to use those same style evaps. PIA if you ask me. Not near enough room in there, and I have seen several where the TEV powerhead rusts through due to sitting in water all the time.
    I r the king of the world!...or at least I get to stand on the roof and look down on the rest of yall

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •