    Need help working on a Residential climatrol furnace. I forgot the model #. I just installed a universal 24v gas valve and new thermocouple the other day. I got a call back today. Tenant complaint of no heat. I went to check it out again and the pilot went out. I relighted it. I checked the gas pressure and it was reading at 3.5 wc. During the 8 or 9 cycle the main burner would puff back and blow out the pilot. I can't figure out what to do the problem. A little help would be nice.

  2. #2
    Join Date
    Feb 2010
    Location
    Ontario Canada
    Posts
    1,341
    Post Likes
    You need a slow opening valve, or a step opening valve...I do not know what you call them down there.
    Never give up; Never surrender!

  3. #3
    Join Date
    Dec 2010
    Location
    Toronto
    Posts
    1,253
    Post Likes
    Are you reading 3.5" at the inlet to the valve while running? If so, you should probably have 4.5" minimum for the valve to work properly. It needs a pressure differential to operate the diaphram properly.

  4. #4
    Join Date
    Feb 2010
    Location
    Milwaukee, WI
    Posts
    62
    Post Likes
    Thread Starter
    So I have to get a slow opening valve? I'll look into it.

    Yes, I am reading 3.5 at manifold. I haven't check the inlet yet. So you are saying I might not have enough gas pressure?

  5. #5
    Join Date
    Aug 2011
    Location
    Ontario
    Posts
    386
    Post Likes
    Check heat exchanger & venting for blockage. But most likely not a slow opening valve.
    There is no bad beer, some just taste better than others.

  6. #6
    Join Date
    Dec 2010
    Location
    Toronto
    Posts
    1,253
    Post Likes
    Quote Originally Posted by xxcels View Post
    So I have to get a slow opening valve? I'll look into it.

    Yes, I am reading 3.5 at manifold. I haven't check the inlet yet. So you are saying I might not have enough gas pressure?
    I've seen it before where too low of a line pressure, which can be due to the utility meter, doesn't allow the appliance reg to work properly in the way you are describing.

  7. #7
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,439
    Post Likes
    I've always considered the minimum inlet pressure to be 7"wc.

    what's the make/model? should specify if it needs a step valve. If it doesn't you may have a flu blockage.

  8. #8
    Join Date
    Dec 2006
    Location
    Litchfield,Il
    Posts
    565
    Post Likes
    I also think you may have a flue restriction. You also have a good strong pilot right? just asking. is this propane? if so the pilot has to be clean 1st thing.
    If your not getting the results you desire then change. People change from either desperation or inspiration.

  9. #9
    Join Date
    Feb 2012
    Location
    Alabama
    Posts
    386
    Post Likes
    Quote Originally Posted by SolarMike View Post
    I've seen it before where too low of a line pressure, which can be due to the utility meter, doesn't allow the appliance reg to work properly in the way you are describing.
    +1

  10. #10
    Join Date
    Feb 2012
    Location
    Virginia
    Posts
    34
    Post Likes
    First thing of course is to be sure you have a strong enough pilot flame. Second, is there any flame blowback or rollout when the burners ignite? Third, did this happen before you replaced the gas valve?

  11. #11
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    If this is a natural draft furnace with an open hood, a blocked flue will have no effect on the burner.

    Is the pilot getting blown out, or is the pilot valve closing due to insufficient DC milivoltage?

    Make sure the pilot flame is sharp and completely engulfs the thermocouple. Measure the dc milivolts.

    If the thermocouple is just barely holding the valve open, the flame only has to flutter away from the t-couple for a couple seconds to drop out the valve.

    If it is indeed blowing it out, check for a restricted heat exchanger and if its ok install a slow opening valve.

  12. #12
    Join Date
    Feb 2010
    Location
    Milwaukee, WI
    Posts
    62
    Post Likes
    Thread Starter
    Quote Originally Posted by JPJ13 View Post
    First thing of course is to be sure you have a strong enough pilot flame. Second, is there any flame blowback or rollout when the burners ignite? Third, did this happen before you replaced the gas valve?
    There seem to but no Data plate on the unit but the cover of the manual

    M# 174-0 Series
    Gas furnace

    Yes, I checked the pilot and there is a strong pilot flame. I putted a new thermocouple there too, measuring at 25mv.

    I lowered the manifold pressure to 3.0" wc but still the problem persist

    This is a natural draft furnace and I checked the flue vent and it seem to be clear. The heat exchanger look clear to me but I will have to double check when I go back. I didn't bring my tools with me.

    I went to double check it today and I have a flame blowback when the main fired up. It will not do this all the time but 1 of 5 tries and it would blow out the pilot.

  13. #13
    Join Date
    Feb 2012
    Location
    Virginia
    Posts
    34
    Post Likes
    Burner blowback or rollout upon startup should have nothing to do with the type or style of gas valve. Typically on that style of furnace you are going to have clogged burner ports or dirty heat exchangers. Here is another thought, the times when you have flame rollout, is the blower motor already on during that ignition?

  14. #14
    Join Date
    Jul 2004
    Location
    Massachusetts
    Posts
    6,846
    Post Likes
    Okay, let's take a few seconds and reflect on what you need to establish the flame and what you've actually got.
    A.What you need:
    1. You need gas at the proper pressure (3.5 IWC in the manifold whenever the main gas valve is open.
    2. You need a solid pilot flame to ignite the gas when the main valve opens.
    3. You need good flame propagation from the pilot to the first and subsequent burners (this needs to be almost instantaneous).

    B. What you've got:
    1. Gas at 3.5 IWC in the manifold.
    2. Solid gas flame.
    3. Light-off but not smooth and sometimes the pilot blows out.

    From a comparison of what you need versus what you've got, I'd say flame propagation is your issue. Remember that water is a by-product of combustion and water creates rust. Rust not only deteriorates burners over time but also clogs the burner outlets.

    Really old burners were made of cast iron with a lot of little holes for the gas. These units lasted many decades as cast iron resists rust quite well. Newer atmospheric burners switched to stamped steel tubes with louver type gas outlets. These louver type tubes can get very easily plugged with soot and I've seen many where the louvers were damaged or missing, thus allowing too much gas to enter the flame area.

    Finally, when you advance to the fan assisted combustion, you get to the in-shot burners with their airplane like wings that are the crossover tubes. Those crossover tubes must also be kept clear of any rust and/or damage that would close them down. Cleaning crossover tubes should be part of any annual service but many techs don't even know they're present.

    In summary, I believe your issue is a result of slow flame propagation leading to periodic sudden over pressures as the unignited gas accumulates and then ignites.
    If YOU want change, YOU have to first change.

    If you are waiting for the 'other guy' to change first, just remember, you're the 'other guy's' other guy. To continue to expect real change when you keep acting the same way as always, is folly. Won't happen. Real change will only happen when a majority of the people change the way they vote!

  15. #15
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    7,434
    Post Likes

    Cool systematic approach

    Sorry but you're out of sequence. Start with measuring your inlet pressure static, just the furnace then under full house load. Compare with the mfrs requirements for minimum inlet pressure, which is usually stated at 4.5wci but may be higher so don't assume. You'll usually get about 1"wci drop from inlet to manifold through the valve. If there is an obstruction in the gas piping or a problem with the medium pressure regulator at the meter or undersized gas piping, a manometer may not always reveal it. We just had this discussion a few weeks ago. Before changing a valve, always hold your hand loosely in front of the gas pipe and open it fully for just a moment. See if you hear any gurgling or feel debris fly out and hit your hand. You'd be surprised.

    With the new valve installed, disconnect the supply tube either at the valve or where it enters the manifold before the orifices and attach a manometer. Read the true manifold pressure. Those pressure taps built into the valve can lie.

    As for the pilot, disconnect it from the valve, remove the pilot orifice and blow the tubing out. Replace the pilot orifice as needed. Attach a manometer to the pilot port and measure pressure directly to the pilot. It should be the same as the inlet pressure minus only 0.2 wci max.

    Ok, so spec. is 3.5wci manifold and that's what you're got UNDER FULL HOUSE LOAD, right? Now, work your way through the gas train. Pull each orifice, gauge, and clean as needed. Check the alignment into the venturi and mixer tube. Is each orifice fully engaged into the venturi PMI? Brush out the mixer tube or burners and especially the ports. Inspect them closely. If the venturis are adjustable, check for PMI then adjust as needed. If the ports are clogged or if they have opened up too much can both be a problem. If some ports are clogges while others are more open, you'll get uneven port loading and imbalanced gas distribution to the burners. This can cause whooshing, popping, delayed ignition and extinction popping.

    Ok, so you've established everything seems strack all the way to the heat exchanger. Inspect it for obstruction and major breaches. Finding none, what about the collector box, inducer and flue collar? Is there a draft hood or induced? If draft hood, the chimney won't affect combustion since they are not attached to each other. With an induced draft, the chimney will. Now, measure the CAZ WRT the adjoining spaces and outdoors for MUA gradient with the unit firing and air handler running.

    If you use a systematic approach ruling out system by system, the problem will reveal itself.

  16. #16
    Join Date
    Feb 2010
    Location
    On the water but near the hood
    Posts
    1,813
    Post Likes
    Poor pilot position or incorrect flame pattern matters alot to avoid roll out and snuffing of pilot so don't assume a replaced pilot is correct.

    That said, slow or stepped opening valves are what I gather is correct for your app.

  17. #17
    Join Date
    Jan 2012
    Posts
    4
    Post Likes
    I just had a problem like this one. the existing valve was slow opening but went bad somehow. after installing an 8200 series slow opening valve the problem went away. I gathered that the in rush of gas ignited to the point that there was np more oxygen i to sustain combustion.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •