    Has anyone else had problems with UV lights, EAC's and the other "new" air cleaners deteriorating the hydrocarbon based components of their HVAC systems? I just had another customer show me a filter that looked like Swiss cheese after being exposed to a UV light. The UV light and the ozone will react with any plastic materials such as filters, pans, wire, mastic, flex duct, etc. I would like to know how widespread this problem is and what people are doing about it.

  2. #2
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    It is very wide spread because most UV light systems get installed in the WRONG part of the system.
    It seems that in my area, no installers have the slightest clue where they go in the system.
    Every one of them I have seen was installed in the return plenum before the filter, or in the supply plenum. UV lights do absolutely nothing good for a system in those location.

    Salesmen love adding them to systems because they are high profit margin, but talk them up as doing something that the UV light has no hope of doing. UV lights will do almost nothing to stuff that is traveling in the air because the air moves to fast to allow enough exposure time.

    The only place a UV light system can do anything positive for the system is if it is shining directly on the entering air side of the indoor coil, and is located within a foot or so of it.

  3. #3
    Join Date
    Jun 2005
    Posts
    88
    Post Likes
    Well said. One of the benefits of using some of the Photocatalytic Oxidation (PCO) designs is that you aren't trying to treat the air stream with the UV light and the design is focused on illuminating the internal coated sections of the photocatalyst. It treats the conditioned space on a longer exposure basis. Of course, some designs do actually try to condition the air stream - requiring much higher energy consumption to try and "zap" the bad stuff. Problem is that the bad stuff might not be constant in the air stream, leading to an overload of the good stuff - which can be just as bad for the occupants!
    A little vodka is ok, a liter can kill you if you drink it all at once!

  4. #4
    Join Date
    May 2005
    Location
    Lubbock Texas
    Posts
    778
    Post Likes

    Thumbs up

    Nice subject for a change and everyone is right on the money from what I have witnessed so far in a lab setting and in the field. Most HVAC manufactures have changed the formula of the plastics they use in current coil boxes in residential systems to compensate for the use of UVGI Lighting. For the old systems depending on the UV wattage the bulb produces it will break down the pans if it has a direct irradiation on the pan in 3 to 5 years.
    In the returns after at least merv 10 filtration is the place in a system that the highest kill rates can be achieved for this reason. A low out put bulb is the most common bulb on the market. Its optimum working temp is around 80 degrees so if the same bulb is put in an air stream of 55 degrees is reduces the output of the bulb by almost 40%. As what Mark said the only place to install just UVGI alone is in the coil box after improved air filtration.
    As far as filters being burned by the UVGI lighting there are benefits of illuminating the back of the filter in a controlled commercial setting for biologic protection but never in a residential unit the risks of someone being burnt by the lights are too high. This is why in our residential line we use polished aluminum shields to protect the filters and project 100% of the light to the PCOs.
    From what I have seen from field installs a 36 watt UVGI light will burn through a filter in about 3 weeks if the light is left on with no air flow. The systems I have seen with constant air flow have gone over 120 days before the holes start in the filters, like a variable speed system chiller system with VAV boxes and such.
    Field testing by us and other universities show in PCO technology the higher the temp and the higher the humidity the better the removal rate is. So yo need to keep this in mind when installing any ones PCO system.
    I am a nut with aluminum tape I tell people if in doubt cover it with foil tape. The only other technology I have really witnessed a lot of damage was in a very large (unnamed casino) they were using a very large commercial EAC System and in the beginning they said the could see some improvement in the smoke particulate then after about a year they started getting dirt clods falling out of the supplies on to the slots. What had happened was the magnetized particulate was collecting in the supplies that was making it passed the Merv 6 pleated filters they were using in the HVAC and was sticking to the supply ducting. The dirt in the supplies got so thick in a years time the air flow was rolling it in to balls and pushing it out of the supplies. They are in the process of replacing those ducts right now. It was a mess. Nothing bets good filtration humidity control and proper fresh air and sometimes thats not enough then you supplement with UVGI or UVGI with a PCO. Depends on what you want to achieve in the treated environment.

  5. #5
    Join Date
    Mar 2004
    Location
    Austin, Texas
    Posts
    2,243
    Post Likes
    genesis -

    I must be missing the most basic logic here. When I go look at your 'systems' on your web site I see what looks like UVGI lights sandwiched between two filters. How does the UVGI ever reach the coil from between the two filters? Are these units to go under a furnace? How would the UV light reach past the blower and furnace to ever see the coil?

  6. #6
    Join Date
    May 2005
    Location
    Lubbock Texas
    Posts
    778
    Post Likes
    CX the top side of a WO units is a pleated mesh screen than has the TIO2 on it. The bottom of the unit is a merv 12 4 inch filter.And one of our basic beliefs in the office is a properly maintained system is the best system in residential units. And if you have a clean evap and coil pan to start with and add our UV/PCO system the improved filtration and the combination of the UVGI and the PCO your coil box should stay clean and mold free. The last testing we did't with the Army was showing on old removel we were hitting in the range of 90% plus in a single pass at around 1800 CFM
    We are developing a system that sets on top of the coil for some one. But we are still in the testing phases of it, and still looking at proto types.

  7. #7
    Join Date
    Sep 2006
    Posts
    710
    Post Likes
    Thread Starter

    UV Attack

    Sometimes a picture is worth a thousand words. Two filters exposed to UV light for 3 months.

  8. #8
    Join Date
    Dec 2001
    Location
    Ocean Pines, MD
    Posts
    7,110
    Post Likes
    Quote Originally Posted by breathe easy View Post
    Sometimes a picture is worth a thousand words. Two filters exposed to UV light for 3 months.

    thought you said they couldn't kill anything in th airstream? looks like they killed this filter!

  9. #9
    Join Date
    Feb 2004
    Location
    Midwest
    Posts
    9,955
    Post Likes
    Quote Originally Posted by breathe easy View Post
    Sometimes a picture is worth a thousand words. Two filters exposed to UV light for 3 months.

    Thanks B.E. Immediately after seeing this, I called my brother (the one with 8 kids) and told him to get that box of Trojans away from EAC & UV equipped furnace.

  10. #10
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,346
    Post Likes

    *

    i installed 1 in my last house in miami fla.

    i put it above the a-coil in my twe 048 it worked like a

    charm it did not ruin anything from exposure,

    as previously stated if you install it properly they are

    component safe, but i dont think it treated the passing air

    it sure did keep the coil clean and no mold would grow in the drain pan!



    .

  11. #11
    Join Date
    Sep 2006
    Posts
    710
    Post Likes
    Thread Starter
    Stamas and Midhvac
    Two of the best posts I have seen. I read them an hour ago and am still laughing. (especially the Trojan alert)

    AirMech, the picture was just to illustrate the potential problems. UV lights are here to stay. I agree - great to keep the coil clean. My point is that we need to be aware of the potential negative effects on the hydrocarbon based components of the HVAC system and guard against their deterioration. For example, was that pan plastic?

  12. #12
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,346
    Post Likes

    *

    Quote Originally Posted by breathe easy View Post
    Stamas and Midhvac
    Two of the best posts I have seen. I read them an hour ago and am still laughing. (especially the Trojan alert)

    AirMech, the picture was just to illustrate the potential problems. UV lights are here to stay. I agree - great to keep the coil clean. My point is that we need to be aware of the potential negative effects on the hydrocarbon based components of the HVAC system and guard against their deterioration. For example, was that pan plastic?
    your right, i did learn something after reading these posts!



    .

  13. #13
    Join Date
    Jun 2005
    Posts
    88
    Post Likes
    Great, no mold on the coils. I guess that means that if you don't want mold in the ducts, you'll need to install UV lights througout the ducts!
    You can always do what one of our local hospitals is doing:
    Duct cleaning.
    Doesn't solve the moisture and particulate accumulation that contribute to mold growth, but sure makes some money for the HVAC contractor with the contract. Especially since the ducts will have mold later, and they can come back and do it again!
    Most UV lights have very limited effectiveness, and a short life . . .
    How are you disposing of them? You realize that they contain mercury and are considered hazardous waste, right?
    Are you shipping them back to the manufacturer for recycling?

  14. #14
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Hows this for an ineffective UV light install?
    Note that the bulb is about 2" from the end baffle, so it doesn't actually shine on any part of the coil face.


    It did a number on the humidifier, seals around the blade on a couple of zone dampers, and was eating at the duct board in the plenum.
    It only took 6 months for it to do this to the humidifier.

  15. #15
    Join Date
    Apr 2007
    Location
    Manchester, CT
    Posts
    2
    Post Likes

    UV light pics?

    Does anyone have high resolution digital pictures of accumulated mold visible to the naked eye on the coils that UV lights are meant to prevent that they can e-mail to me?



    edit

    No email addresses in post, you can place it in your profile after you post 5 times.
    Last edited by Dad; 04-15-2007 at 06:15 PM.

  16. #16
    Join Date
    Oct 2009
    Posts
    20
    Post Likes
    funman

    See some of the pics in this link.

    http://www.rgf.com/documents/AC_coil_article.pdf

    This site is pushing an "Advanced Oxidation Plasma" solution. I'm not sure of the science behind this, but they seem to make a reasonable case regarding UVC lights.
    Last edited by Beauble; 10-16-2009 at 09:08 PM. Reason: Replied before I looked at the dates on this string. It is a current issue for me.

  17. #17
    Join Date
    May 2012
    Posts
    2
    Post Likes
    here is a response from tom wilson, president of second wind. we sell his products and have had nothing but good feedback from customers. I also have one in my house installed on the cold air return and have had no problems with my aprilaire media filter deteriorating.




    Second Wind systems are instructed to be installed 36” away from non-UV materials if at all possible. Non-UV materials should be shielded to prevent degradation due to UV exposure. Aluminum duct tape does a great job, as does tinfoil! Drain pan manufacturers have fixed many of the issues by moving to UV resistant materials to prevent breakdown. Lower UV systems (again 24V systems) do not create the same damage a HO system like the 2000 model’s lamps could do. I would never advise to install a 2000 or 1000KCS next to a filter – it would melt if it was not UV-resistant like our 9000 series units.



    The return plenum is an ideal place to install a UV system as the air is moving the slowest in that part of the system, providing the best exposure time to break down the microscopic contaminants. The comment about not enough time for exposure is a statement that we love to engage because the time required to kill these contaminants that are smaller than can be seen is often achieved in the first pass (see above). Our PCO system does not have a chamber so we create the field inside the entire duct with our 18” lamps and create a massive UV bath of 72” x duct cross-section area.

  18. #18
    Join Date
    Sep 2006
    Posts
    710
    Post Likes
    Thread Starter
    So, you have confirmed exactly what this thread is about - UV lights will destroy any materials made of hydrocarbons exposed to the UV lights. This is a major problem since buyers are not informed of this potential damage or the costs involved.

  19. #19
    Join Date
    Aug 2012
    Location
    NE wisconsin
    Posts
    488
    Post Likes
    Quote Originally Posted by breathe easy View Post
    So, you have confirmed exactly what this thread is about - UV lights will destroy any materials made of hydrocarbons exposed to the UV lights. This is a major problem since buyers are not informed of this potential damage or the costs involved.
    Proper installation will result in no damage, far enough up in the return drop and you have no direct exposure to the light, put shielding in to protect non uv resistant materials or cover in foil tape. Those filte earlier in this thread must have been right next to the bulb. The company I work for installs a lot of uv lights and with proper installation and educating the customer a little we never have any problems. But I have seen them installed wrong by the other guys and it usually results in the filter deteriorating, but I've never seen them as bad as the photos posted earlier.

  20. #20
    Join Date
    Aug 2010
    Location
    SouthEast Texas Gulf
    Posts
    15
    Post Likes

    UV Lamp location is key

    Quote Originally Posted by breathe easy View Post
    Has anyone else had problems with UV lights, EAC's and the other "new" air cleaners deteriorating the hydrocarbon based components of their HVAC systems? I just had another customer show me a filter that looked like Swiss cheese after being exposed to a UV light. The UV light and the ozone will react with any plastic materials such as filters, pans, wire, mastic, flex duct, etc. I would like to know how widespread this problem is and what people are doing about it.
    The placement of the lamp (s) I believe is key. Lamps should be installed on the output side of the coil (Per Carrier pub:63UV-LA3). I sell and install UV lamps on occasion, I even have installed one in my home. I have never had a problem with plastics in the system, I believe that the new plastic pans are uv and chemical resistant. Flex duct might be a problem but I have not seen that as most of the systems I work on are metal pipe or ductboard. I use a TIF 3710 to check uv lamp operation; when installing a new bulb I mark the readings on the coil, averaging readings on both front and back side of coil. If the bulb is less than 1 year old and reading low because the bulb is dirty I clean it with alcohol, carrier sells a cleaning kit. I have seen a big difference in only 6 month of using a uv lamp on some systems. Usually the coil and pan look like new. I also recommend a good filter, like an Aprilaire, be installed at the unit. I have never seen an Aprilaire filter degraded by uv light, even when installed directly on intake of a fan coil. I always install the uv lamps between the coil and blower not the coil and filter, even so when you remove the filter you still get a dose of uv radiation but I have not seen any harm even after a year of same filter being exposed to uv.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •