    Hmm Johnson FX20/60/70 Capacities + Integration

    Is there anyone who has extensive experience with these controllers? I was always curious to know how many controllers can be handled by each version of the FX Supervisory Controllers....although I'm sure the capacities are not based on controller count but more so on type of written programs as well as FX alarms, trends, etc. A majority of the field controllers will be controlling CW/HW/VFD-controlled AHUs and VAVs. One of the FX Supervisory Controllers will also be integrating to an existing Trane Summit System via BACnet IP (Chiller Plant, AHUs and VAVs) and possibly future Honeywell Spider Field Controllers via Lontalk.

    Thanks.

  2. #2
    Join Date
    Apr 2008
    Location
    Northeast
    Posts
    74
    Post Likes
    Thread Starter
    Quote Originally Posted by NightrainATC View Post
    Is there anyone who has extensive experience with these controllers? I was always curious to know how many controllers can be handled by each version of the FX Supervisory Controllers....although I'm sure the capacities are not based on controller count but more so on type of written programs as well as FX alarms, trends, etc. A majority of the field controllers will be controlling CW/HW/VFD-controlled AHUs and VAVs. One of the FX Supervisory Controllers will also be integrating to an existing Trane Summit System via BACnet IP (Chiller Plant, AHUs and VAVs) and possibly future Honeywell Spider Field Controllers via Lontalk.

    Thanks.
    By the way, the Johnson Field Controllers coming off of the FX Supervisory Controllers will be FEC BACnet Controllers.

    Thanks.

  3. #3
    Join Date
    Aug 2007
    Location
    Western Oregon
    Posts
    499
    Post Likes
    Generally, it's the bus that limits the number of controllers under a Jace.
    RealEyes
    Realize
    RealLies!




  4. #4
    Join Date
    Apr 2008
    Location
    Northeast
    Posts
    74
    Post Likes
    Thread Starter
    Quote Originally Posted by rad1 View Post
    Generally, it's the bus that limits the number of controllers under a Jace.
    Meaning what.....bus length or cable type? FYI...the bus cable will be 22awg, 3-conductor shielded for BACnet communication over the FC bus.

  5. #5
    Join Date
    Aug 2007
    Location
    Western Oregon
    Posts
    499
    Post Likes
    Some busses allow a fixed max. number of devices. With a Jace tho you can add a second or third network and increase the device count that way, or adding a router to your network may allow an increased count on a bus. I don't think I've ever seen or heard of an "absolute" number of controllers that a Jace could handle. You've mentioned some of the features that could add to that limit though,
    i.e., "written programs as well as FX alarms, trends, etc."
    RealEyes
    Realize
    RealLies!




  6. #6
    Join Date
    Jul 2008
    Location
    Melbourne
    Posts
    1,611
    Post Likes
    Quote Originally Posted by NightrainATC View Post
    ....the Johnson Field Controllers coming off of the FX Supervisory Controllers will be FEC BACnet Controllers.
    Is this a real job ...or a thought experiment?

    How are you gonna program the FECs?
    1 + 1 = 3 ( *** for very large values of 1)

    ...everybody wants a box of chocolates and long stemmed rose

    Be brave. You cannot get eaten by an imaginary tiger.

  7. #7
    Join Date
    Apr 2008
    Location
    Northeast
    Posts
    74
    Post Likes
    Thread Starter
    Quote Originally Posted by MatrixTransform View Post
    Is this a real job ...or a thought experiment?

    How are you gonna program the FECs?
    This is a real job. The FECs will be controlling AHUs, VAVs and Hot Water System equipment and will communicate to the FX Supervisory Controllers via BACnet MS/TP.

    I'm figuring it will be best to use FX Supervisory Controllers vs Johnson NAEs because I feel the future integration to existing 3rd party Honeywell LON Controllers will be much smoother using FX20/60/70 Controllers.

  8. #8
    Join Date
    Jul 2008
    Location
    Melbourne
    Posts
    1,611
    Post Likes
    Quote Originally Posted by NightrainATC View Post
    This is a real job.
    ...so, youre from a JCI branch ... or an ABCS?

    The FX will easily communicate to as many FEC as an NAE. What sort of unit load do FECs present on a MSTP bus? Same constraints for FX.

    we have FX60 that concurrently interfaces 5 different RS485 bus including modbus and Bacnet, SNMP, consumes RS232 strings from the fire system, and serves graphics for the site....and it still has capacity.

    How many devices do you need to communicate with
    1 + 1 = 3 ( *** for very large values of 1)

    ...everybody wants a box of chocolates and long stemmed rose

    Be brave. You cannot get eaten by an imaginary tiger.

  9. #9
    Join Date
    Apr 2008
    Location
    Northeast
    Posts
    74
    Post Likes
    Thread Starter
    Quote Originally Posted by MatrixTransform View Post
    ...so, youre from a JCI branch ... or an ABCS?

    The FX will easily communicate to as many FEC as an NAE. What sort of unit load do FECs present on a MSTP bus? Same constraints for FX.

    we have FX60 that concurrently interfaces 5 different RS485 bus including modbus and Bacnet, SNMP, consumes RS232 strings from the fire system, and serves graphics for the site....and it still has capacity.

    How many devices do you need to communicate with
    We are an ABCS but currently have access to both FX & Metasys Lines. I'm looking at around 450-500 FEC field controllers (400 of which are FEC VMA VAV Controllers and the others for AHUs and Hot Water System equipment control). I'm thinking 2 or 3 FX Supervisory Controllers would be needed....not sure if to go FX60 or FX70s.

  10. #10
    Join Date
    Mar 2009
    Location
    Several Miles from Sane
    Posts
    2,660
    Post Likes
    NightrainATC,
    Put some info in your profile please.

    While you're at it apply from pro membership. I know I would be more willing to assist in the pro forum.
    If sense were so common everyone would have it !
    You cannot protect the Stupid from themselves !
    "Experience is the ability to recognize a mistake Before you make it again!" (Stolen Quote)

  11. #11
    Join Date
    Apr 2008
    Location
    Northeast
    Posts
    74
    Post Likes
    Thread Starter
    Quote Originally Posted by CCIKelly View Post
    NightrainATC,
    Put some info in your profile please.

    While you're at it apply from pro membership. I know I would be more willing to assist in the pro forum.
    CCIKelly,

    My profile has been updated, thanks. I will look into a pro membership but if you could provide any advice in this thread, it would be appreciated.

    Thanks.

  12. #12
    Join Date
    Jan 2008
    Location
    Near Philly
    Posts
    546
    Post Likes
    I've got a site with 3200 points on a single FX60. The N2 bus is split in halve, on two different physical ports. I have the server software package doing the graphics and trending. The FX60 is maxed out. I have similar sites with 2300-2400 points and everything runs at a much lower level. So, the consumption is defiantly not linear.

  13. #13
    Join Date
    Apr 2008
    Location
    Northeast
    Posts
    74
    Post Likes
    Thread Starter
    Quote Originally Posted by mechdorn View Post
    I've got a site with 3200 points on a single FX60. The N2 bus is split in halve, on two different physical ports. I have the server software package doing the graphics and trending. The FX60 is maxed out. I have similar sites with 2300-2400 points and everything runs at a much lower level. So, the consumption is defiantly not linear.
    Mechdorn,

    Thanks. This is the type of information I was looking for. I too will be implementing a FX Server so is it safe to use 1600 pts per trunk as a max guidline?

    At this time, we are used to using NAEs which have controller count limitations. Because this is a big facility which may require 4 to 5 FX Supervisory Controllers, I'm assuming we will use the RS-485 adapter for each FX Supervisory and run (2) BACnet MS/TP trunks per FX with repeaters as needed.....is this correct?

    Lastly, I will be bringing in existing Trane pts from (2) BCUs...approx a total of 600-800 pts...over BACnet IP into the FX Server. Also future Lontalk integration to approx (15) Honeywell Spider field controllers which would require a FX LON card.

  14. #14
    Join Date
    Jan 2008
    Location
    Near Philly
    Posts
    546
    Post Likes
    I omitted the fact that all of these jobs that I'm referring to all have the extended memory license installed. With a FX60, 1600 points maybe a push without the extended memory, no problem with the extra memory and a supervisor software serving up the graphics.

  15. #15
    Join Date
    Mar 2009
    Location
    Several Miles from Sane
    Posts
    2,660
    Post Likes
    NightrainATC,
    Did you submit that Pro member app/request yet ?

    The FX-60 with extended memory should match with an NAE5500 point for point with capacity to spare if you put all your graphics on an FX-Server.

    I can't remember the figure but the limitation is "File Descriptors", I think a 60 w/o extended memor has a 2000 limit but I am not sure. You should be able to easily handle 200 devices on multiple trunks in a single 60

    Freddy-B may be able to give you more info on massive numbers of devices/points in an FX-60.

    Apply for Pro Membership !
    If sense were so common everyone would have it !
    You cannot protect the Stupid from themselves !
    "Experience is the ability to recognize a mistake Before you make it again!" (Stolen Quote)

  16. #16
    Join Date
    Apr 2008
    Location
    Northeast
    Posts
    74
    Post Likes
    Thread Starter
    Quote Originally Posted by mechdorn View Post
    I omitted the fact that all of these jobs that I'm referring to all have the extended memory license installed. With a FX60, 1600 points maybe a push without the extended memory, no problem with the extra memory and a supervisor software serving up the graphics.
    Thanks. I figured you had extended memory. I'm going with extra memory anyway to accommodate future controllers.

    Question: If I had a job without the FX server and it had (3) FX Supervisory Controllers, could the customer hit all three controllers on their network from under one controller or do they have to go into individual access points to see what's under each controller? Also with this scenario, is there anything I should no regarding the graphics?

    Thanks again!!!

  17. #17
    Join Date
    Apr 2008
    Location
    Northeast
    Posts
    74
    Post Likes
    Thread Starter
    Quote Originally Posted by CCIKelly View Post
    NightrainATC,
    Did you submit that Pro member app/request yet ?

    The FX-60 with extended memory should match with an NAE5500 point for point with capacity to spare if you put all your graphics on an FX-Server.

    I can't remember the figure but the limitation is "File Descriptors", I think a 60 w/o extended memor has a 2000 limit but I am not sure. You should be able to easily handle 200 devices on multiple trunks in a single 60

    Freddy-B may be able to give you more info on massive numbers of devices/points in an FX-60.

    Apply for Pro Membership !
    How do you apply for a Pro membership and what are the benefits? Thanks.

  18. #18
    Join Date
    Jan 2003
    Location
    USA
    Posts
    9,437
    Post Likes

  19. #19
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,302
    Post Likes
    Quote Originally Posted by NightrainATC View Post
    How do you apply for a Pro membership and what are the benefits? Thanks.
    Control folks may go Pro by simply requesting to do so, to the CFC...

    The reason is the regular Pro route is based off of things such as CFC cards and a like that several control folks obviously do not have.

    The Controls committee then votes based on ones posts to wither or not we believe they are a "Pro"

    Should this be your desire to go Pro, all I need is a request from you via this thread

    Chris

  20. #20
    Join Date
    Feb 2005
    Location
    Edmonton, AB Canada
    Posts
    1,124
    Post Likes
    Quote Originally Posted by mechdorn View Post
    I've got a site with 3200 points on a single FX60. The N2 bus is split in halve, on two different physical ports. I have the server software package doing the graphics and trending. The FX60 is maxed out. I have similar sites with 2300-2400 points and everything runs at a much lower level. So, the consumption is defiantly not linear.
    Good day Mechdorn,

    Indeed, consumption is not linear and in fact has have more to do with physics than the performance of the N2 supervisory controller. Remember that the N2 bus communicates at 9600 baud and so the maximum bandwidth (theoretical) is 960 characters per second (10 bits per character). Talking to each device on the N2 bus requires a packet size which is dependent upon the the N2 device itself (N2 device, DX devices, and VMA devices with N2 protocol having the smallest packet size in general), the number of (mapped) points in the N2 devices, the rate with which the points change, how fast the device gets off the bus, how fast the supervisory gets on and off the bus, and what priority the supervisory/user set for particular devices... all this determines how much time each field device gets attention (i.e. transferring point data to/from the supervisory) from the supervisory controller... Thus, the number of points is a guideline, but is very site specific for the reasons I previously mentioned... and so you are 100% right that consumption is not linear.

    Cheers,

    Sam

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •