    Humidity Issues

    Had a 12.5 ton York package unit replaced with a Trane 12.5 and i am having humidity issues that i have not had before. First stage puts humidity back in the building and drops the temp at the same time.Both units have a high static blower.

  2. #2
    Join Date
    Oct 2012
    Location
    Wisconsin
    Posts
    6,676
    Post Likes
    Did your installing contractor check airflow on the new unit on startup? Could be moving too much air which could cause humidity related issues.

    Depending on what model your old York was and new Trane are, there are a few things that come to mind.

    With the Trane, when you say the First Stage, do you know if the first stage opens the economizer to bring in outdoor air, or does the first stage bring on the first stage compressor?

    Other thing too depending on model its common for a 12 1/2 ton York for each stage to be 6 tons, some units stage one is (I think) 4 tons and stage two is 8 tons. So the unit will come on and run for a longer time at a lower capacity which will dehumidify better.

    On the Trane, your first stage may be a higher capacity, and the second stage a lower capacity. If there is a lower heat load on the building, the unit will come on, cool down and shut off, and may not run quite as continuous as the York may have.

  3. #3
    Join Date
    Jul 2013
    Posts
    2
    Post Likes
    Thread Starter
    Thanks for the info,first stage brings on compressor and i think the old unit first stage was smaller tonage i will check and find out. The Trane first and second stage compressor are the same tonage.

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Min opening on the economizer may be too much.

  5. #5
    Join Date
    Apr 2010
    Location
    Winnipeg,Manitoba,Canada
    Posts
    176
    Post Likes
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise, commentary, or ask questions of the OP here.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.
    Last edited by beenthere; 07-11-2013 at 08:06 PM. Reason: Non Pro * member

  6. #6
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    7,434
    Post Likes
    Quote Originally Posted by ryan79 View Post
    Does it have an economizer ?
    what are your outside air conditions ?
    Where is this unit installed ? office building or is it in a place where there is a lot of humidity ?
    This is the Ask Our Pro's or AOP forum. In order to post responses here, you must have verified qualifications and have been approved by the AOP Committee. Please see my signature line for links to register and review the AOP Forum Rules. Thank you. Your post will now be deleted. Further infractions may result in loss of posting privileges.

  7. #7
    Join Date
    Apr 2010
    Location
    Winnipeg,Manitoba,Canada
    Posts
    176
    Post Likes
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise, commentary, or ask questions of the OP here.

    You can find the rules for posting and qualifications here.

    Last edited by beenthere; 07-11-2013 at 10:13 PM. Reason: Non Pro * member

  8. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    ryan79, this is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise, commentary or ask questions of the OP here.

    You can find the rules for posting and qualifications here.

    Your post has been deleted.

  9. #9
    Join Date
    Oct 2009
    Location
    Raleigh, NC
    Posts
    1,022
    Post Likes
    I bet is is something easy like the economizer minimum setpoint being open too wide or something. I did have an issue like this with an older Carrier last month. I was scratching my head for a while, but then I figure out someone had switched the two stages. The bottom of the evap was supposed to be #1 and the top #2, but they had reversed the contactors. Stage 1 would incorrectly operate the top half of the evaporator and all that condensate would flow downward on the warm bottom half of the evap.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •