Thread: nordyne tripping limit

  1. #21
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    7,473
    Post Likes
    Quote Originally Posted by craig1 View Post
    Every furnace has one since they all use the same inducer. A 60k btu will have a restrictor with a small hole, while a 120k will have one with a big hole.

    The faulty restrictors seem to be on models made in the early to mid 2000s. They were made from an opaque plastic that flakes away. The problem is most pronounced on units where the filter was not changed often enough.
    And the restrictor is part of the inducer assembly which, if changed, will remedy the issue?

  2. #22
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,249
    Post Likes
    Quote Originally Posted by hurtinhvac View Post
    And the restrictor is part of the inducer assembly which, if changed, will remedy the issue?
    No the inducer orifice is separate, and snaps into the opening in the Front Header Box. Then the inducer assembly is installed over it.

    As Crag1 said, same inducer, you just use a different orifice to control the airflow.

    See attachment (sorry, picture is a little fuzzy).
    Attached Images Attached Images
    Instead of learning the tricks of the trade, learn the trade.

  3. #23
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    7,473
    Post Likes
    Got it. Picture is fine.

    Most instructive as always, Rundawg.

    Thanks all for this thread - had no clue.

  4. #24
    Join Date
    Nov 2005
    Posts
    367
    Post Likes
    Thread Starter
    so is Inducer Orifice in blower or Header Box?

  5. #25
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    On the g26 you buy an inducer and it comes with multiple restrictor plates and based on BTU the correct color plate gets installed in the inducer, I'm sure some have them in condensate box as well?

  6. #26
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,249
    Post Likes
    Quote Originally Posted by iowa tech View Post
    so is Inducer Orifice in blower or Header Box?
    It does snap into the Inducer Motor Assembly, and not the header box on this particular unit.

    I stated it wrong on my previous post. What I was trying to say is the Orifice is between the inducer and header box.
    Instead of learning the tricks of the trade, learn the trade.

  7. #27
    Join Date
    Nov 2005
    Posts
    367
    Post Likes
    Thread Starter
    Orfice was missing

  8. #28
    Join Date
    Jul 2009
    Location
    ohio
    Posts
    100
    Post Likes
    same prob... found hooked to a 2 wire stat, replaced w/4 wire hook up, MH are particular if your used to resi. R,G,W,C
    read,learn,grow.....repeat.

  9. #29
    Join Date
    Nov 2012
    Location
    Barrie, ON
    Posts
    29
    Post Likes
    Quote Originally Posted by iowa tech View Post
    Orfice was missing
    Good stuff. Did you retrieve the old restriction plate (orifice)?

  10. #30
    Join Date
    Nov 2012
    Location
    Barrie, ON
    Posts
    29
    Post Likes
    Quote Originally Posted by barriefurnacerepair View Post
    Good stuff. Did you retrieve the old restriction plate (orifice)?
    Here's one I was working on yesterday and thought about this thread.....


  11. #31
    Join Date
    Nov 2012
    Location
    Barrie, ON
    Posts
    29
    Post Likes
    Here's one from a Lennox.....did this today.....


+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •